  2. Bug Reports
  3. Strange value being sent from controller using mixed temp/relay node
multiple sensormqtterror
42 Posts 6 Posters 22.9k Views 3 Watching
  • G
    G
    Gambituk
    wrote on last edited by Gambituk
    Hello, I am getting strange values being sent from this controller sketch from @gadu (many thanks again) and this node sketch from @pgo
    It almost works.. i am going via mosquitto install on the same raspberry as openhab, and it does turn on and off the relay while sending temp values from the same node. The problem i am having is that it is not reliable, it doesn't always turn on and off, and i have found that the following is being sent from the mqtt gateway sketch:
    0;0;3;0;9;send: 0-0-21-21 s=0,c=1,t=0,pt=0,l=5,st=ok:19.7r
    0;0;3;0;9;read: 21-21-0 s=1,c=1,t=0,pt=7,l=5:5.4
    publish: MyMQTT/21/1/V_TEMP 5.4
    0;0;3;0;9;send: 0-0-21-21 s=1,c=1,t=0,pt=0,l=5,st=fail:5.47r
    0;0;3;0;9;send: 0-0-24-24 s=2,c=1,t=2,pt=0,l=4,st=ok:147r
    0;0;3;0;9;send: 0-0-24-24 s=2,c=1,t=2,pt=0,l=4,st=ok:047r
    0;0;3;0;9;read: 21-21-0 s=0,c=1,t=0,pt=7,l=5:19.8
    publish: MyMQTT/21/0/V_TEMP 19.8
    0;0;3;0;9;send: 0-0-21-21 s=0,c=1,t=0,pt=0,l=5,st=ok:19.8r
    0;0;3;0;9;send: 0-0-24-24 s=2,c=1,t=2,pt=0,l=4,st=ok:1.8r
    0;0;3;0;9;send: 0-0-24-24 s=2,c=1,t=2,pt=0,l=4,st=ok:0.8r
    0;0;3;0;9;read: 21-21-0 s=1,c=1,t=0,pt=7,l=5:5.6
    publish: MyMQTT/21/1/V_TEMP 5.6
    0;0;3;0;9;send: 0-0-21-21 s=1,c=1,t=0,pt=0,l=5,st=fail:5.68r
    0;0;3;0;9;read: 21-21-0 s=1,c=1,t=0,pt=7,l=5:5.5
    so.. node 21 is just sending temp values, node 24 is the mixed temp/relay..
    As you may notice the 1 and zero code for the relay is getting mixed with the last received temp values, which seems to be ok if the last temp read is more than 10degrees resulting in a 1.xx value sent or a 0.xx value sent, which is accepted as a 1 or 0, but when it receives a value below 10 then it converts it to something like 047 or 147 which doesn't trigger the relay correctly! Please any help or guidance to understand where the 1 or 0 message is coming from?
    I imagine its what is being sent from the gateway sketch that is mixing the payload, but i cannot see how to reformulate what is sent to send only a 1 or 0 when sending to the relay...... ??
    MyMQTT/24/0/V_TEMP 23.9
    MyMQTT/21/1/V_TEMP 5.1
    MyMQTT/24/2/V_LIGHT 1
    MyMQTT/24/2/V_LIGHT 0
    =Sample of mqtt messages showing 24 node with v_temp and V_light on node 24 and v_temp on node 21
    • G
      G
      Gambituk
      For ease of access here is the mqtt gateway sketch with the intro comments removed for pasting here,
      #include "MyMQTTClient.h"
      #include "PubSubClient.h"
          #include <Ethernet.h>
           * To configure MQTTClientGateway.ino to use an ENC28J60 based board include
           * 'UIPEthernet.h' (SPI.h required for MySensors anyway). The UIPEthernet-library can be downloaded
          //#include <UIPEthernet.h>
           * To execute MQTTClientGateway.ino on Yun uncomment Bridge.h and YunClient.h.
           * Do not include Ethernet.h or SPI.h in this case.
           * On Yun there's no need to configure local_ip and mac in the sketch
           * as this is configured on the linux-side of Yun.
          //#include <Bridge.h>
          //#include <YunClient.h>
          // * Use this for IBOARD modded to use standard MISO/MOSI/SCK, see note *1 above!
           #define RADIO_CE_PIN        3			// radio chip enable
           #define RADIO_SPI_SS_PIN    8			// radio SPI serial select
           #define RADIO_ERROR_LED_PIN A2  		// Error led pin
           #define RADIO_RX_LED_PIN    A1  		// Receive led pin
           #define RADIO_TX_LED_PIN    A0  		// the PCB, on board LED*/
          // * Use this for default configured pro mini / nano etc :
          #define RADIO_CE_PIN        7		// radio chip enable
          #define RADIO_ERROR_LED_PIN 5		// Error led pin
          #define RADIO_RX_LED_PIN    6		// Receive led pin
          #define RADIO_TX_LED_PIN    9		// the PCB, on board LED*/
          //replace with ip of server you want to connect to, comment out if using 'remote_host'
          uint8_t remote_ip[] =
            { 192, 168, 0, 7 };
          //replace with hostname of server you want to connect to, comment out if using 'remote_ip'
          //char* remote_ip = "server.local";
          //replace with the port that your server is listening on
          #define remote_port 1883
          //replace with arduinos ip-address. Comment out if Ethernet-startup should use dhcp. Is ignored on Yun
          uint8_t local_ip[] = {192,168,0,10};
          //replace with ethernet shield mac. It's mandatory every device is assigned a unique mac. Is ignored on Yun
          uint8_t mac[] =
            { 0x90, 0xA2, 0xDA, 0x0D, 0x07, 0x02 };
          #if defined remote_ip && defined remote_host
          #error "cannot define both remote_ip and remote_host at the same time!"
          #ifdef _YUN_CLIENT_H_
          YunClient ethClient;
          #else
          EthernetClient ethClient;
          void
          processMQTTMessages(char* topic, byte* payload, unsigned int length);
          PubSubClient client(remote_ip, remote_port, processMQTTMessages, ethClient);
          MyMQTTClient gw(client,RADIO_CE_PIN, RADIO_SPI_SS_PIN);
          void
          setup()
            Ethernet.begin(mac, local_ip);
            delay(1000);   // Wait for Ethernet to get configured.
            gw.begin(RF24_PA_LEVEL_GW, RF24_CHANNEL, RF24_DATARATE,
            RADIO_RX_LED_PIN, RADIO_TX_LED_PIN, RADIO_ERROR_LED_PIN);
          void
          loop()
            if (!client.connected())
                client.connect("mysensor");
                client.subscribe("MyMQTT/#");
            client.loop();
            gw.processRadioMessage();
          void
            gw.processMQTTMessage(topic, payload, length);
      • G
        G
        Gambituk
        and here is the modified relay/temp sketch
        // Running DS temperature sensor(s) and relay(s) on one mysensor arduino node
            // Combines Onewire and Relay code
            // 2014-10-14 Pego: Tested and Running on Uno/Clone and MQTT gateway
            // Example sketch showing how to send in OneWire temperature readings
            // Example sketch showing how to control physical relays.
            // This example will remember relay state even after power failure.
            #include <OneWire.h>presen
            #define RELAY_1  4  // Arduino Digital I/O pin number for first relay (second on pin+1 etc)
            unsigned long SLEEP_TIME = 30000; // Sleep time between reads (in milliseconds) 30000 orig
            OneWire oneWire(ONE_WIRE_BUS);
            int numSensors=0;
            boolean metric = true;
            MyMessage msg(0,V_TEMP);
              // Startup OneWire
              sensors.begin();
              //gw.begin();
              gw.sendSketchInfo("Temp and Relays", "1.0");
                 gw.present(i, V_TEMP);
              // Fetch relay status
                gw.present(sensor, S_LIGHT);
                pinMode(pin, OUTPUT);
                digitalWrite(pin, gw.loadState(sensor)?RELAY_ON:RELAY_OFF);
              gw.process();
                // Only send data if temperature has changed more then 1 degC and no error
                if (int(lastTemperature[i]) != int(temperature) && temperature != -127.00) { //added integer
              //gw.sleep(SLEEP_TIME); //no sleep for relays!!!!
              if (message.type==V_LIGHT) {
                 // Change relay state
                 // Store state in eeprom
                 // Write some debug info
                 Serial.print(message.sensor);
        T 1 Reply Last reply
        • G
          G
          Gambituk
          I guess this probably should have been in troubleshooting :S
          • gaduG
            gaduG
            gadu
            Just guessing here, have you different child id's on the temp and relay?
            • G
              G
              Gambituk
              No it seems like they are given the same child id's. Ok, so maybe i'l look at how to force a different child id for each sensor/actuator
              • BulldogLowellB
                BulldogLowellB
                BulldogLowell
                the combining of the extensible sketches make it harder than needs to be.
                How many sensors are you connecting of each type?
                • G
                  G
                  Gambituk
                  Hi, i have 3 temp sensors and 2 relays, I am just looking at how to make this work but am not making much progress. Cant figure out how to assign the child id's. Any help would be appreciated.
                  • G
                    G
                    Gambituk
                    was thinking of presenting the temps sensors first, and adding something like && i>NUMBER_OF_RELAYS to start assigining child id's above the range of relays? Will test and report back
                    • G
                      G
                      Gambituk
                      I tried to modify the temp child presentation like this..... but it seemed to have no effect
                      int offsetforrelays=5;   //(at start of sketch)
                      // and this further down in the presentation for temp sensors
                       for (int i=0; i<(numSensors+offsetforrelays) && i<(MAX_ATTACHED_DS18B20+offsetforrelays) && i>offsetforrelays; i++) {
                      but so far it hasn't assigned any different id's to the temp sensors. Anyone got any pointers?
                      • G Gambituk
                        BulldogLowellB
                        BulldogLowellB
                        BulldogLowell
                        do you still have this typo in your code?
                        • G
                          G
                          Gambituk
                          no, i took it out (without effect) about an hour ago
                          • G Gambituk
                            BulldogLowellB
                            BulldogLowellB
                            BulldogLowell
                            @Gambituk
                            try something like this:
                            #define NUMBER_OF_TEMP_SENSORS 3
                              sensors.begin();
                              for (int i=0; i < NUMBER_OF_TEMP_SENSORS ; i++)
                                gw.present(i, V_TEMP); // creates 0, 1 and 2
                              for (int sensor=1, pin=RELAY_1 ; sensor <= NUMBER_OF_RELAYS ; sensor++ , pin++)
                                gw.present(NUMBER_OF_TEMP_SENSORS + sensor, S_LIGHT); // should create 3 and 4
                            you will also have to sort out the sensor numbers in the callback
                            • G
                              G
                              Gambituk
                              0;0;3;0;9;read: 25-25-0 s=0,c=0,t=0,pt=0,l=5:1.4.1
                              0;0;3;0;9;read: 25-25-0 s=1,c=0,t=0,pt=0,l=5:1.4.1
                              0;0;3;0;9;read: 25-25-0 s=2,c=0,t=0,pt=0,l=5:1.4.1
                              0;0;3;0;9;read: 25-25-0 s=4,c=0,t=3,pt=0,l=5:1.4.1
                              0;0;3;0;9;read: 25-25-0 s=5,c=0,t=3,pt=0,l=5:1.4.1
                              So far it seems to create 0,1,2,4,5 but i think that's not going to be a problem, just working my way through to figure what else i need to change for the callback? (and what a callback is :D )
                              Thanks for the help so far!
                              • BulldogLowellB
                                BulldogLowellB
                                BulldogLowell
                                the call back function:
                                incomingMessage()
                                look to get this right:
                                so that the command matches the sensor numbers...
                                G 1 Reply Last reply
                                  incomingMessage()
                                  G
                                  G
                                  Gambituk
                                  @BulldogLowell
                                  For the earlier part, should this be "for (int sensor=0" to get 3 and 4?
                                  I get 4 and 5 ... But either way, i dont suppose it matters that there is a gap of 1 in the sensor child id's.
                                  1. I change the callback to this:
                                    digitalWrite(message.sensor - 4 + RELAY_1, message.getBool() ? RELAY_ON : RELAY_OFF);
                                  and that works.... i can send a message and it activates the relay.. :D
                                  1. BUT.... :(
                                     repeater started, id 25
                                     send: 25-25-0-0 s=255,c=0,t=18,pt=0,l=5,st=ok:1.4.1
                                     send: 25-25-0-0 s=255,c=3,t=6,pt=1,l=1,st=ok:0
                                     read: 0-0-25 s=255,c=3,t=6,pt=0,l=1:M
                                     send: 25-25-0-0 s=255,c=3,t=11,pt=0,l=15,st=ok:Temp and Relays
                                     send: 25-25-0-0 s=255,c=3,t=12,pt=0,l=3,st=ok:1.0
                                     send: 25-25-0-0 s=0,c=0,t=0,pt=0,l=5,st=ok:1.4.1
                                     send: 25-25-0-0 s=1,c=0,t=0,pt=0,l=5,st=ok:1.4.1
                                     send: 25-25-0-0 s=2,c=0,t=0,pt=0,l=5,st=ok:1.4.1
                                     send: 25-25-0-0 s=4,c=0,t=3,pt=0,l=5,st=ok:1.4.1
                                     send: 25-25-0-0 s=5,c=0,t=3,pt=0,l=5,st=ok:1.4.1
                                     send: 25-25-0-0 s=0,c=1,t=0,pt=7,l=5,st=ok:19.1
                                  Here i am sending a message with 1 and then 0 to relay id4 and then the same to relay id5 -It works, but i still have the 1.3 and 0.3 values
                                      read: 0-0-25 s=5,c=1,t=2,pt=0,l=4:1.3r
                                      Incoming change for sensor:5
                                      Incoming change for sensor:5, New status: 1
                                      read: 0-0-25 s=5,c=1,t=2,pt=0,l=4:0.3r
                                      Incoming change for sensor:5, New status: 0
                                  And then it starts going even crazier, only seeing the status as 1 and received command is nothing like boolean so it see's 0's and 1's as only 1's
                                      read: 0-0-25 s=4,c=1,t=2,pt=0,l=4:1.3r
                                      Incoming change for sensor:4
                                      Incoming change for sensor:4, New status: 1
                                      read: 0-0-25 s=4,c=1,t=2,pt=0,l=4:0.3r
                                      read: 0-0-25 s=5,c=1,t=2,pt=0,l=4:003r
                                      read: 0-0-25 s=5,c=1,t=2,pt=0,l=4:013r
                                      read: 0-0-25 s=4,c=1,t=2,pt=0,l=4:113r
                                      read: 0-0-25 s=4,c=1,t=2,pt=0,l=4:013r
                                  1. So i am thinking it is still a problem with what is sent from gateway somehow... :(
                                  Any ideas
                                  • G Gambituk
                                    @BulldogLowell
                                    1. BUT.... :(
                                    Any ideas
                                    BulldogLowellB
                                    BulldogLowellB
                                    BulldogLowell
                                    @Gambituk
                                    would you mind posting your latest (sorta working) code?
                                    • G
                                      G
                                      Gambituk
                                          #define ONE_WIRE_BUS 3 // Pin where dallas sensor is connected
                                          //int numSensors = 0;
                                          MyMessage msg(0, V_TEMP);
                                          //int offsetforrelays = 5;
                                            // Startup OneWire
                                            sensors.begin();
                                            gw.begin(incomingMessage, AUTO, true);        // Startup and initialize MySensors library. Set callback for incoming messages.
                                            gw.sendSketchInfo("Temp and Relays", "1.0");   // Send the sketch version information to the gateway and Controller
                                            for (int i = 0; i < NUMBER_OF_TEMP_SENSORS ; i++)
                                            for (int sensor = 1, pin = RELAY_1 ; sensor <= NUMBER_OF_RELAYS ; sensor++ , pin++)
                                              //   loop from sensor1/pin4 to sensor2/pin5 (numofrelays=2)
                                              digitalWrite(pin, gw.loadState(sensor) ? RELAY_ON : RELAY_OFF);
                                            gw.process();
                                            for (int i = 0; i < NUMBER_OF_TEMP_SENSORS && i < MAX_ATTACHED_DS18B20; i++) {
                                              float temperature = static_cast<float>(static_cast<int>((gw.getConfig().isMetric ? sensors.getTempCByIndex(i) : sensors.getTempFByIndex(i)) * 10.)) / 10.;
                                                gw.send(msg.setSensor(i).set(temperature, 1));
                                                lastTemperature[i] = temperature;
                                              Serial.println(message.sensor);
                                      • G
                                        G
                                        Gambituk
                                        @BulldogLowell I just tried uploading a standard vanilla relay node, and i get the same garbled data instead of 1 and 0 (should have tried this at the start, but i am happy with what i have learned in the last 12 hours.) So it seems almost certain that it is an issue with the @gadu version of the mqtt gateway.. which is unaltered from the above post. #2 above
                                        • gaduG
                                          gaduG
                                          gadu
                                          Interesting findings, if you find any solution for this in the MQTT gateway I would really appreciate if you post it. I'm about to start implementing relays as well.
                                          (it's actually not my version, I think @ntruchsess is the one who created it) ;)