Generic pressure sensors -SOLVED
-
Didn't find exactly what I was looking for in a forum search...
Bought two of these (Chinese?) pressure transducers and 1/2" adapters with the intent of monitoring pressure (initially at 2 points) in the pumped water supply which has various headlosses in the line.
These are listed as 5v supply, 0.5-4.5 output for 0-0.5MPa, 20mA consumption, beyond that only claims the response is "perfectly" linear.
![20200705_082815[1].jpg](/assets/uploads/files/1593927807370-20200705_082815-1-resized.jpg)
The Node is 3.3v, 5v is available on-board from an external PSU, but the voltage output will have to be scaled down to suit the ADC pin, even more so if aiming for Vref 1.1.
Normally a high value resistance ladder would suffice, but concerned over effect on response (presumably a variable resistance device), checked output resistance to ground, at atmospheric ca 6.7 Mohm, purportedly corresponding to 0.5v.It occurred to me that if it IS a variable resistance it should also function the same at 3v, so any here able to offer any insights, experience, or tips ?
-
Didn't find exactly what I was looking for in a forum search...
Bought two of these (Chinese?) pressure transducers and 1/2" adapters with the intent of monitoring pressure (initially at 2 points) in the pumped water supply which has various headlosses in the line.
These are listed as 5v supply, 0.5-4.5 output for 0-0.5MPa, 20mA consumption, beyond that only claims the response is "perfectly" linear.
![20200705_082815[1].jpg](/assets/uploads/files/1593927807370-20200705_082815-1-resized.jpg)
The Node is 3.3v, 5v is available on-board from an external PSU, but the voltage output will have to be scaled down to suit the ADC pin, even more so if aiming for Vref 1.1.
Normally a high value resistance ladder would suffice, but concerned over effect on response (presumably a variable resistance device), checked output resistance to ground, at atmospheric ca 6.7 Mohm, purportedly corresponding to 0.5v.It occurred to me that if it IS a variable resistance it should also function the same at 3v, so any here able to offer any insights, experience, or tips ?
-
@zboblamont can't you just try it? Nothing will break when powered below 5v, but you would have to apply the pressure somehow
@Yveaux Yes, but was hoping someone had already gone through similar experiments, and could advise what did/didn't work ;)
Your post prompted a reminder there is a 1/2" valved drain cock for the water meter/PRV in the bathroom... This would simplify testing without having to make plumbing alterations for the final locations :) -
As a postscript to my own question should someone be looking at similar later, in practice the sensors were found to work perfectly well at 3v3.
Described as 5v working, 0.5-4.5v signal range, the effect is pro-rata at 3v3 in terms of voltage but the ADC output is identical for VCC scaling - viz, ZERO pressure is 10% of 1024 the range is 80%
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.