Water pressure sensors?

Scheduled Pinned Locked Moved Hardware
41 Posts 12 Posters 7.8k Views 11 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • gohanG gohan

    What are you trying to measure?

    mfalkviddM Offline
    mfalkviddM Offline
    mfalkvidd
    Mod
    wrote on last edited by
    #3

    @gohan the pressure of water/sewage

    dbemowskD 1 Reply Last reply
    0
    • gohanG Offline
      gohanG Offline
      gohan
      Mod
      wrote on last edited by
      #4

      pressure of sewage? I am missing the point....

      1 Reply Last reply
      0
      • mfalkviddM mfalkvidd

        @gohan the pressure of water/sewage

        dbemowskD Offline
        dbemowskD Offline
        dbemowsk
        wrote on last edited by
        #5

        @mfalkvidd wouldn't you want flow rate and not pressure? I am assuming this is to calculate water usage, which sewer usage is typically based off your water usage. Maybe my assumption is wrong.

        Vera Plus running UI7 with MySensors, Sonoffs and 1-Wire devices
        Visit my website for more Bits, Bytes and Ramblings from me: http://dan.bemowski.info/

        mfalkviddM 1 Reply Last reply
        0
        • dbemowskD dbemowsk

          @mfalkvidd wouldn't you want flow rate and not pressure? I am assuming this is to calculate water usage, which sewer usage is typically based off your water usage. Maybe my assumption is wrong.

          mfalkviddM Offline
          mfalkviddM Offline
          mfalkvidd
          Mod
          wrote on last edited by
          #6

          @dbemowsk in this application, flow rate is often zero, so flow rate is of little interest.

          1 Reply Last reply
          0
          • gohanG Offline
            gohanG Offline
            gohan
            Mod
            wrote on last edited by
            #7

            I wasn't aware sewage had pressure

            mfalkviddM 1 Reply Last reply
            0
            • gohanG gohan

              I wasn't aware sewage had pressure

              mfalkviddM Offline
              mfalkviddM Offline
              mfalkvidd
              Mod
              wrote on last edited by mfalkvidd
              #8

              @gohan if something is blocking the sewage's way to its final destination, pressure will build up pretty quickly.
              alt text

              1 Reply Last reply
              0
              • gohanG Offline
                gohanG Offline
                gohan
                Mod
                wrote on last edited by
                #9

                for something like that, by the time you get notification it is already too late :D

                mfalkviddM 1 Reply Last reply
                0
                • gohanG gohan

                  for something like that, by the time you get notification it is already too late :D

                  mfalkviddM Offline
                  mfalkviddM Offline
                  mfalkvidd
                  Mod
                  wrote on last edited by
                  #10

                  @gohan that's where you are wrong.
                  "In many countries there are obligations to measure and report SSO occurrence using real-time telemetry to warn the public, bathers and shellfishery operators."

                  From https://en.wikipedia.org/wiki/Sanitary_sewer_overflow

                  Now that we've completely derailed this thread, could we get back on topic?

                  1 Reply Last reply
                  0
                  • gohanG Offline
                    gohanG Offline
                    gohan
                    Mod
                    wrote on last edited by
                    #11

                    If you could derive a small pipe from the main sewage line, you could could then have a transducer at the end to measure pressure without requiring it to go submerged.

                    https://www.aliexpress.com/item/5V-G1-4-0-0-5-MPa-Hydraulic-Pressure-Sensor-for-Non-Corrosive-Water-Oil-Gas/32822204051.html

                    mfalkviddM 1 Reply Last reply
                    0
                    • gohanG gohan

                      If you could derive a small pipe from the main sewage line, you could could then have a transducer at the end to measure pressure without requiring it to go submerged.

                      https://www.aliexpress.com/item/5V-G1-4-0-0-5-MPa-Hydraulic-Pressure-Sensor-for-Non-Corrosive-Water-Oil-Gas/32822204051.html

                      mfalkviddM Offline
                      mfalkviddM Offline
                      mfalkvidd
                      Mod
                      wrote on last edited by
                      #12

                      @gohan thanks. Yes, that's a solution that could work. (technically, the "inside" part of the sensor would still be submerged which probably is necessary)

                      zboblamontZ 1 Reply Last reply
                      0
                      • gohanG Offline
                        gohanG Offline
                        gohan
                        Mod
                        wrote on last edited by
                        #13

                        of course the sensor is built to be in contact with water, so that is fine

                        1 Reply Last reply
                        0
                        • mfalkviddM mfalkvidd

                          @gohan thanks. Yes, that's a solution that could work. (technically, the "inside" part of the sensor would still be submerged which probably is necessary)

                          zboblamontZ Offline
                          zboblamontZ Offline
                          zboblamont
                          wrote on last edited by zboblamont
                          #14

                          @mfalkvidd Not so.... You can install a sensor on a sealed stack (vertical pipe) as @gohan suggested, sealed to the crown of the sewer or drain (a Tee or saddle fitting), the air pressure from the relative hydraulic head will create air pressure which can be correlated to hydraulic head. Whereas the sensor may get moisture in the air it will never be actually submerged, which you generally do not want in sewage anyway due to grease etc and various objects which customers do deposit...
                          Another option is ultrasonics in a vertical pipe venting to atmosphere thereby contact free.. Whether you could get a decent interpretation in a tube from a DYP-ME007Y or similar I do not know, but commercial systems use just such an arrangement....

                          mfalkviddM 1 Reply Last reply
                          0
                          • zboblamontZ zboblamont

                            @mfalkvidd Not so.... You can install a sensor on a sealed stack (vertical pipe) as @gohan suggested, sealed to the crown of the sewer or drain (a Tee or saddle fitting), the air pressure from the relative hydraulic head will create air pressure which can be correlated to hydraulic head. Whereas the sensor may get moisture in the air it will never be actually submerged, which you generally do not want in sewage anyway due to grease etc and various objects which customers do deposit...
                            Another option is ultrasonics in a vertical pipe venting to atmosphere thereby contact free.. Whether you could get a decent interpretation in a tube from a DYP-ME007Y or similar I do not know, but commercial systems use just such an arrangement....

                            mfalkviddM Offline
                            mfalkviddM Offline
                            mfalkvidd
                            Mod
                            wrote on last edited by
                            #15

                            Thanks for the input @zboblamont
                            I can't mount a 10m vertical pipe on top of the sewage pipe, so I don't think ultrasound is a viable alternative unfortunately.

                            zboblamontZ 1 Reply Last reply
                            0
                            • mfalkviddM Offline
                              mfalkviddM Offline
                              mfalkvidd
                              Mod
                              wrote on last edited by
                              #16

                              I might have found what I am looking for
                              https://eu.mouser.com/new/measurement-specialties/te-ms5837-30ba/ is inexpensive, small and handles 0-30bar.

                              1 Reply Last reply
                              0
                              • gohanG Offline
                                gohanG Offline
                                gohan
                                Mod
                                wrote on last edited by
                                #17

                                But it is missing the entire enclosure, it is the bare sensor. The one I posted was ready to be bolted into place

                                mfalkviddM 1 Reply Last reply
                                0
                                • mfalkviddM mfalkvidd

                                  Thanks for the input @zboblamont
                                  I can't mount a 10m vertical pipe on top of the sewage pipe, so I don't think ultrasound is a viable alternative unfortunately.

                                  zboblamontZ Offline
                                  zboblamontZ Offline
                                  zboblamont
                                  wrote on last edited by zboblamont
                                  #18

                                  @mfalkvidd 10m? Wow, that is one very large hydraulic head you're measuring if it's a storm overflow or similar... Oslo's trunk sewer system? A sealed pressure transducer would be your best bet at that head, holding it in a fixed position and running the cable will be a challenge...
                                  Oops, just read your follow up...

                                  1 Reply Last reply
                                  0
                                  • gohanG gohan

                                    But it is missing the entire enclosure, it is the bare sensor. The one I posted was ready to be bolted into place

                                    mfalkviddM Offline
                                    mfalkviddM Offline
                                    mfalkvidd
                                    Mod
                                    wrote on last edited by
                                    #19

                                    @gohan yes, I do need a whole solution. But I'm hoping to find something more compact.

                                    gohanG zboblamontZ alexsh1A 4 Replies Last reply
                                    0
                                    • mfalkviddM mfalkvidd

                                      @gohan yes, I do need a whole solution. But I'm hoping to find something more compact.

                                      gohanG Offline
                                      gohanG Offline
                                      gohan
                                      Mod
                                      wrote on last edited by
                                      #20

                                      @mfalkvidd you are a difficult customer 😁

                                      1 Reply Last reply
                                      1
                                      • mfalkviddM mfalkvidd

                                        @gohan yes, I do need a whole solution. But I'm hoping to find something more compact.

                                        zboblamontZ Offline
                                        zboblamontZ Offline
                                        zboblamont
                                        wrote on last edited by
                                        #21

                                        @mfalkvidd Perhaps if you expand on the objective and location it might help narrow down options.
                                        eg - Is this a pressurised pipe below the surface which may be tapped into or a deep well vented to atmosphere? Does the site have power or is this a remote location?

                                        If the intent is a submerged logger type device occasionally retrieved and downloaded at the surface, an adaption of the cavepearlproject.org format might suit.
                                        If this is to report to the surface in real time from a vented chamber surcharging to 10m, cabling brings a host of problems, not least low voltage operation... Typical commercial devices for such applications are sealed pressure probes operating at over 9v with a 4-20mA output, and pricetags north of 400 euro...
                                        A rigid pipe with a transducer sealed and mounted on the top will work when the pipe is purged (compressor/foot pump), the static air pressure thereafter relates directly to depth of hydraulic submergence..

                                        B 1 Reply Last reply
                                        0
                                        • zboblamontZ zboblamont

                                          @mfalkvidd Perhaps if you expand on the objective and location it might help narrow down options.
                                          eg - Is this a pressurised pipe below the surface which may be tapped into or a deep well vented to atmosphere? Does the site have power or is this a remote location?

                                          If the intent is a submerged logger type device occasionally retrieved and downloaded at the surface, an adaption of the cavepearlproject.org format might suit.
                                          If this is to report to the surface in real time from a vented chamber surcharging to 10m, cabling brings a host of problems, not least low voltage operation... Typical commercial devices for such applications are sealed pressure probes operating at over 9v with a 4-20mA output, and pricetags north of 400 euro...
                                          A rigid pipe with a transducer sealed and mounted on the top will work when the pipe is purged (compressor/foot pump), the static air pressure thereafter relates directly to depth of hydraulic submergence..

                                          B Offline
                                          B Offline
                                          boozz
                                          wrote on last edited by
                                          #22

                                          @mfalkvidd

                                          Have a look at freescale sensors. i.e. MXP-type sensors. You could ask for samples (they will provide up to 5 pcs. for free). Cost around $15 pcs. normally.

                                          You'd mount such a sensor on top of a riser (air-tight) and when the (sewage) water rises, the air-pocket is compressed proportionally. This is how I measure the ground-water level at my location and it helps me to keep my basement free of water. Works flawlessly!

                                          BR,

                                          Boozz1_1525272320306_IMG_E7592.JPG 0_1525272320306_IMG_E7591.JPG

                                          1 Reply Last reply
                                          1
                                          Reply
                                          • Reply as topic
                                          Log in to reply
                                          • Oldest to Newest
                                          • Newest to Oldest
                                          • Most Votes


                                          15

                                          Online

                                          11.7k

                                          Users

                                          11.2k

                                          Topics

                                          113.1k

                                          Posts


                                          Copyright 2025 TBD   |   Forum Guidelines   |   Privacy Policy   |   Terms of Service
                                          • Login

                                          • Don't have an account? Register

                                          • Login or register to search.
                                          • First post
                                            Last post
                                          0
                                          • MySensors
                                          • OpenHardware.io
                                          • Categories
                                          • Recent
                                          • Tags
                                          • Popular