  3. Signing: no active verification session?
36 Posts 3 Posters 6.6k Views 2 Watching
  • T
    tomkxy
    @Anticimex Ok. I repeated the the soft signing tests: Both, gateway and node on soft signing works.
    Putting node on ATSHA204 signing while gateway is still on soft signing fails.
    Apart from that issue, the implementation seems to work and improves obviously on the timing issue I had.
    • T
      tomkxy
      So, I repeated the test again, if GW and node are on soft sign it works. If I put either GW or node on soft sign, while the other is using ATSHA204, signing fails
      To verify my setup I switched to development branch. There I could run the node on soft signing while the GW is using ATSHA204.
      AnticimexA 1 Reply Last reply
      • T tomkxy
        AnticimexA
        AnticimexA
        Anticimex
        @tomkxy Hm, ok, so with the updates from PR, soft and atsha signing are not compatible? I need to check into that.
        Out of curiosity, when you checked from development branch, was the ATSHA node using the code from the PR or was it also from development branch? Just so I know if the issue is in the soft signing implementation or both backends.
        • AnticimexA Anticimex
          tomkxy
          I ran the test with node and gateway on PR code:
          One test both on soft signing -> ok
          One test node on soft signing, GW on ATSH204 -> failed
          Then I repeated with both node and GW on development branch:
          • node soft sign, GW on ATSHA204 -> OK
          • T tomkxy
            AnticimexA
            AnticimexA
            Anticimex
            @tomkxy I think I found the problem. Mistake by me.
            Try to change the following two lines (106 & 107) in MySigningAtsha204Soft.cpp:
            memset(_signing_current_inbound_nonce, 0x00, NONCE_NUMIN_SIZE_PASSTHROUGH);
            memset(_signing_current_outbound_nonce, 0x00, NONCE_NUMIN_SIZE_PASSTHROUGH);
            to
            memset(_signing_current_inbound_nonce, 0xAA, 32);
            memset(_signing_current_outbound_nonce, 0xAA, 32);
              to
              tomkxy
              to
              I made the changes. Still not working.
              • T tomkxy
                to
                AnticimexA
                AnticimexA
                Anticimex
                @tomkxy Hm. I have rewritten the code to be easier to read. Could you please clean out the changes from my PR (restore to "pristine" development) and then reapply the PR from github?
                If possible, also include the verbose logs from both ends so that we can confirm that they agree upon which nonce to use for a message.
                • T
                  tomkxy
                  I cannot promise that I am able to do that today.
                  • T tomkxy
                    AnticimexA
                    AnticimexA
                    Anticimex
                    #28
                    @tomkxy That's ok, No big rush on this. I suspect it is just a matter of the soft and atsha backends are not in agreement on the nonce data. I have not changed the algorithms so I would not expect them to be incompatible.
                      tomkxy
                      Can I use the same pull request? I just fetched this one (https://github.com/mysensors/Arduino/pull/454)
                      OK?
                      • T tomkxy
                        OK?
                        AnticimexA
                        AnticimexA
                        Anticimex
                        @tomkxy yes, just make sure it applies cleanly. I forced pushed some updates.
                          tomkxy
                          I sent you a chat message
                          • T tomkxy
                            AnticimexA
                            AnticimexA
                            Anticimex
                            @tomkxy So I noticed. Let's iron out the details in the chat, and report here when we sort it for documentation purposes.
                            • T
                              tomkxy
                              Here are the log files. They are not in sync from the beginning. Further there re message from a node 27 which can be ignored. Best is probably to work from the end.
                              Node log
                              Starting sensor (RNNNAS, 2.0.0-beta)
                              Radio init successful.
                              Signing required
                              Skipping security for command 3 type 15
                              send: 32-32-0-0 s=255,c=3,t=15,pt=0,l=2,sg=0,st=ok:
                              Waiting for GW to send signing preferences...
                              read: 0-0-32 s=255,c=3,t=15,pt=0,l=2,sg=0:
                              Mark node 0 as one that require signed messages
                              Mark node 0 as one that do not require whitelisting
                              Skipping security for command 3 type 16
                              send: 32-32-0-0 s=255,c=3,t=16,pt=0,l=0,sg=0,st=ok:
                              Nonce requested from 0. Waiting...
                              Skipping security for command 3 type 17
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:F0E3953E5E27A57274D53B6F0B2C4098EBD0F6A84345DE7135
                              Nonce received from 0. Proceeding with signing...
                              Signing backend: ATSHA204Soft
                              Message to process: 2000560011FF322E302E302D62657461
                              Current nonce: F0E3953E5E27A57274D53B6F0B2C4098EBD0F6A84345DE7135AAAAAAAAAAAAAA
                              HMAC: DC73D1128E9B00E6E0FFA12AE46CBBD6BE0F3103FDFDE2D718A52AC530A852F9
                              Signature in message: 0173D1128E9B00E6E0FFA12AE46CBB
                              Message signed
                              Message to send has been signed
                              send: 32-32-0-0 s=255,c=0,t=17,pt=0,l=10,sg=1,st=ok:2.0.0-beta
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:E574F30C89052CFEA25ACB6D9B3B4E8CA0D462DF4770ECF72F
                              Message to process: 20000E2306FF00
                              Current nonce: E574F30C89052CFEA25ACB6D9B3B4E8CA0D462DF4770ECF72FAAAAAAAAAAAAAA
                              HMAC: 556E870FC4662534A18B29FB7A48440B7C745E15FF82EA34E806F9C372B6FDA9
                              Signature in message: 016E870FC4662534A18B29FB7A48440B7C745E15FF82EA34
                              Message signed
                              send: 32-32-0-0 s=255,c=3,t=6,pt=1,l=1,sg=1,st=ok:0
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:10C33355BD231F7BB5E53E7E39372DE1C3053161AE04D74494
                              Message to process: 20008E030BFF53656E736562656E646572204D6963726F
                              Current nonce: 10C33355BD231F7BB5E53E7E39372DE1C3053161AE04D74494AAAAAAAAAAAAAA
                              HMAC: F272ECC9E1B27FF3C089905712EDF1793D146865CE2AF9252D27FAFF953BA64F
                              Signature in message: 0172ECC9E1B27FF3
                              Message signed
                              send: 32-32-0-0 s=255,c=3,t=11,pt=0,l=17,sg=1,st=ok:Sensebender Micro
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:3B91B8117E813E6F0E12221791A78309559E5052097A420E8A
                              Message to process: 20001E030CFF312E35
                              Current nonce: 3B91B8117E813E6F0E12221791A78309559E5052097A420E8AAAAAAAAAAAAAAA
                              HMAC: 23E348148A34E8BE86788E5AA5F45F8F675089068DA52BC6C4C27D0B8DCA70C3
                              Signature in message: 01E348148A34E8BE86788E5AA5F45F8F675089068DA5
                              Message signed
                              send: 32-32-0-0 s=255,c=3,t=12,pt=0,l=3,sg=1,st=ok:1.5
                              send: 32-32-0-0 s=0,c=3,t=16,pt=0,l=0,sg=0,st=ok:
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:694B1F7903CB8A6854DAF8509AA451207AD040D71966A3453D
                              Message to process: 200006001F00
                              Current nonce: 694B1F7903CB8A6854DAF8509AA451207AD040D71966A3453DAAAAAAAAAAAAAA
                              HMAC: 6013C5AA4FDD7E2F61EAA2C3F2716BCEEFB56292BA66BC98A43517E458EF235B
                              Signature in message: 0113C5AA4FDD7E2F61EAA2C3F2716BCEEFB56292BA66BC98A4
                              Message signed
                              send: 32-32-0-0 s=0,c=0,t=31,pt=0,l=0,sg=1,st=ok:
                              Init complete, id=32, parent=0, distance=1
                              ------------- Start request time ------------
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:13F0B25E5D9A117DA1146AFA7494C90FA33FA03B128B0CE3E1
                              Message to process: 2000060301FF
                              Current nonce: 13F0B25E5D9A117DA1146AFA7494C90FA33FA03B128B0CE3E1AAAAAAAAAAAAAA
                              HMAC: 5F71BF42F9C80CC00B5319226D836566CD4F95123E96258FF8E2E3400863547E
                              Signature in message: 0171BF42F9C80CC00B5319226D836566CD4F95123E96258FF8
                              Message signed
                              send: 32-32-0-0 s=255,c=3,t=1,pt=0,l=0,sg=1,st=ok:
                              ------------- End request time ------------
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:8FBD6C07C7957826D2BAF13CDD7A82D8082180FD4F0796F6B4
                              Current nonce: 8FBD6C07C7957826D2BAF13CDD7A82D8082180FD4F0796F6B4AAAAAAAAAAAAAA
                              HMAC: 6FAC958E93696F29B508B534322FC0237EB1740405F2A7AA2A518FBF4883896D
                              Signature in message: 01AC958E93696F29B508B534322FC0237EB1740405F2A7AA2A
                              Message signed
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:6BB69A71C65A24D7077B9B2A2E65D51B3861A56CF777BBD6B6
                              Current nonce: 6BB69A71C65A24D7077B9B2A2E65D51B3861A56CF777BBD6B6AAAAAAAAAAAAAA
                              HMAC: 3E2DE76DD7349510C9CAE6F072875D7D7C380BBDD00C65339BF25898F44A180B
                              Signature in message: 012DE76DD7349510C9CAE6F072875D7D7C380BBDD00C65339B
                              Message signed
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:B7CD5773148E8916C98B5BB16265F17811F8091A560A3535EB
                              Current nonce: B7CD5773148E8916C98B5BB16265F17811F8091A560A3535EBAAAAAAAAAAAAAA
                              HMAC: 46959641C93642F85E13499948DC33F1CE3B1B0DE5D8DEC8F5D04ECBA2A28552
                              Signature in message: 01959641C93642F85E13499948DC33F1CE3B1B0DE5D8DEC8F5
                              Message signed
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:43AADEA58D5CC9AF0A58FE4A763CEE560CB751BCF31BAD7F4C
                              Current nonce: 43AADEA58D5CC9AF0A58FE4A763CEE560CB751BCF31BAD7F4CAAAAAAAAAAAAAA
                              HMAC: 1217705F14F7482ACEEC510ADD5EB2CBB329B3FA475486182644D5EC98DDB619
                              Signature in message: 0117705F14F7482ACEEC510ADD5EB2CBB329B3FA4754861826
                              Message signed
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:90E1C960135A6C130C95D8DCDA63C583905F58BC0C0AC6734C
                              Current nonce: 90E1C960135A6C130C95D8DCDA63C583905F58BC0C0AC6734CAAAAAAAAAAAAAA
                              HMAC: 5DE257A17035F53D20CE18F57BF0E0E60142F56690BB8BB9F4184632241E2015
                              Signature in message: 01E257A17035F53D20CE18F57BF0E0E60142F56690BB8BB9F4
                              Message signed
                              read: 0-0-32 s=255,c=3,t=17,pt=6,l=25,sg=0:5FB2B52B80BA2BD2B7F657B3754594C84B14811B6067EEB626
                              Current nonce: 5FB2B52B80BA2BD2B7F657B3754594C84B14811B6067EEB626AAAAAAAAAAAAAA
                              HMAC: 00AE0409E50F471F7B4154A4492D72FA382EEA40257DD408D2EB9E1B012A35EF
                              Signature in message: 01AE0409E50F471F7B4154A4492D72FA382EEA40257DD408D2
                              Message signed
                              Log file from gateway:
                              0;255;3;0;9;Starting gateway (RNNGAA, 2.0.0-beta)
                              0;255;3;0;9;MQTT connected
                              0;255;3;0;9;Skipping security for command 3 type 16
                              0;255;3;0;9;read: 32-32-0 s=255,c=3,t=16,pt=0,l=0,sg=0:
                              0;255;3;0;9;Signing backend: ATSHA204
                              0;255;3;0;9;SHA256: B44451C64C562F11BDCF41F7F3EEF39816265188B34FD45E96216B85148A12AA
                              0;255;3;0;9;Transmittng nonce
                              0;255;3;0;9;Skipping security for command 3 type 17
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:B44451C64C562F11BDCF41F7F3EEF39816265188B34FD45E96
                              0;255;3;0;9;Signature in message: 0191F99D82163BDAF73FFD91B6984D59A5F564BF45ECBBABCE
                              0;255;3;0;9;Message to process: 2000060301FF
                              0;255;3;0;9;Current nonce: B44451C64C562F11BDCF41F7F3EEF39816265188B34FD45E96AAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: EB8162E2FCAD9359B19B383A711A5E64A964A25F965162BF74BBFB4EB59836E2
                              0;255;3;0;9;Signature bad: 018162E2FCAD9359B19B383A711A5E64A964A25F965162BF74
                              0;255;3;0;9;Signature verification failed!
                              0;255;3;0;9;verify fail
                              0;255;3;0;9;read: 27-27-0 s=2,c=1,t=1,pt=7,l=5,sg=0:62.49
                              0;255;3;0;9;Sending message on topic: GW1_out/27/2/1/0/1
                              0;255;3;0;9;read: 27-27-0 s=1,c=1,t=0,pt=7,l=5,sg=0:34.11
                              0;255;3;0;9;Sending message on topic: GW1_out/27/1/1/0/0
                              0;255;3;0;9;read: 27-27-0 s=0,c=1,t=4,pt=7,l=5,sg=0:1020.15
                              0;255;3;0;9;Sending message on topic: GW1_out/27/0/1/0/4
                              0;255;3;0;9;read: 27-27-0 s=0,c=1,t=5,pt=0,l=6,sg=0:stable
                              0;255;3;0;9;Sending message on topic: GW1_out/27/0/1/0/5
                              0;255;3;0;9;read: 27-27-0 s=10,c=1,t=38,pt=7,l=5,sg=0:4.123
                              0;255;3;0;9;Sending message on topic: GW1_out/27/10/1/0/38
                              0;255;3;0;9;read: 27-27-0 s=10,c=1,t=39,pt=7,l=5,sg=0:0.000000
                              0;255;3;0;9;Sending message on topic: GW1_out/27/10/1/0/39
                              0;255;3;0;9;read: 27-27-0 s=11,c=1,t=38,pt=7,l=5,sg=0:9.978
                              0;255;3;0;9;Sending message on topic: GW1_out/27/11/1/0/38
                              0;255;3;0;9;read: 27-27-0 s=255,c=3,t=0,pt=1,l=1,sg=0:88
                              0;255;3;0;9;Sending message on topic: GW1_out/27/255/3/0/0
                              0;255;3;0;9;read: 27-27-0 s=13,c=1,t=8,pt=7,l=5,sg=0:0.40
                              0;255;3;0;9;Sending message on topic: GW1_out/27/13/1/0/8
                              0;255;3;0;9;read: 27-27-0 s=13,c=1,t=9,pt=7,l=5,sg=0:0.60
                              0;255;3;0;9;Sending message on topic: GW1_out/27/13/1/0/9
                              0;255;3;0;9;read: 27-27-0 s=12,c=1,t=10,pt=7,l=5,sg=0:328.68
                              0;255;3;0;9;Sending message on topic: GW1_out/27/12/1/0/10
                              0;255;3;0;9;read: 27-27-0 s=12,c=1,t=24,pt=7,l=5,sg=0:36.80
                              0;255;3;0;9;Sending message on topic: GW1_out/27/12/1/0/24
                              0;255;3;0;9;read: 27-27-0 s=14,c=1,t=6,pt=7,l=5,sg=0:0.00
                              0;255;3;0;9;Sending message on topic: GW1_out/27/14/1/0/6
                              0;255;3;0;9;SHA256: 9BEBE9A04F339CE85808EBF1B5E8BC7BD611CC3B5C0A638DF2A548B398BF059E
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:9BEBE9A04F339CE85808EBF1B5E8BC7BD611CC3B5C0A638DF2
                              0;255;3;0;9;Signature in message: 012C3605DF4F03AD69833FCC101EA1BF0E5750483F4E2107F6
                              0;255;3;0;9;Current nonce: 9BEBE9A04F339CE85808EBF1B5E8BC7BD611CC3B5C0A638DF2AAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: 681C6D87947BC2574D48FFCAC370BECD30789EAEB7C2BFBAD562B2ED7DCAE10F
                              0;255;3;0;9;Signature bad: 011C6D87947BC2574D48FFCAC370BECD30789EAEB7C2BFBAD5
                              0;255;3;0;9;Skipping security for command 3 type 15
                              0;255;3;0;9;read: 32-32-0 s=255,c=3,t=15,pt=0,l=2,sg=0:
                              0;255;3;0;9;Mark node 32 as one that require signed messages
                              0;255;3;0;9;Mark node 32 as one that do not require whitelisting
                              0;255;3;0;9;Informing node 32 that we require signatures
                              0;255;3;0;9;Informing node 32 that we do not require whitelisting
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=15,pt=0,l=2,sg=0,st=ok:
                              0;255;3;0;9;SHA256: F0E3953E5E27A57274D53B6F0B2C4098EBD0F6A84345DE7135D3A4AEC3E13960
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:F0E3953E5E27A57274D53B6F0B2C4098EBD0F6A84345DE7135
                              0;255;3;0;9;Signature in message: 0173D1128E9B00E6E0FFA12AE46CBB
                              0;255;3;0;9;Message to process: 2000560011FF322E302E302D62657461
                              0;255;3;0;9;Current nonce: F0E3953E5E27A57274D53B6F0B2C4098EBD0F6A84345DE7135AAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: CBC7FC088614695AD92A5A4A32CA832C6D00041CF63D1AF78F353FD6E0D9D949
                              0;255;3;0;9;Signature bad: 01C7FC088614695AD92A5A4A32CA83
                              0;255;3;0;9;SHA256: E574F30C89052CFEA25ACB6D9B3B4E8CA0D462DF4770ECF72FB75DED8D5F68BC
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:E574F30C89052CFEA25ACB6D9B3B4E8CA0D462DF4770ECF72F
                              0;255;3;0;9;Signature in message: 016E870FC4662534A18B29FB7A48440B7C745E15FF82EA34
                              0;255;3;0;9;Message to process: 20000E2306FF00
                              0;255;3;0;9;Current nonce: E574F30C89052CFEA25ACB6D9B3B4E8CA0D462DF4770ECF72FAAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: 5E2D30821345709074EB96B09CC0C7408E1291AC5C921432DD83A29919734767
                              0;255;3;0;9;Signature bad: 012D30821345709074EB96B09CC0C7408E1291AC5C921432
                              0;255;3;0;9;SHA256: 10C33355BD231F7BB5E53E7E39372DE1C3053161AE04D744948C093BFA5776C8
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:10C33355BD231F7BB5E53E7E39372DE1C3053161AE04D74494
                              0;255;3;0;9;Signature in message: 0172ECC9E1B27FF3
                              0;255;3;0;9;Message to process: 20008E030BFF53656E736562656E646572204D6963726F
                              0;255;3;0;9;Current nonce: 10C33355BD231F7BB5E53E7E39372DE1C3053161AE04D74494AAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: 82CCF6912389FCE5896B4867B82879414D80FE3FBAC1C6365E0B6303F7DADB56
                              0;255;3;0;9;Signature bad: 01CCF6912389FCE5
                              0;255;3;0;9;SHA256: 3B91B8117E813E6F0E12221791A78309559E5052097A420E8A3AB9EDED6F5D56
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:3B91B8117E813E6F0E12221791A78309559E5052097A420E8A
                              0;255;3;0;9;Signature in message: 01E348148A34E8BE86788E5AA5F45F8F675089068DA5
                              0;255;3;0;9;Message to process: 20001E030CFF312E35
                              0;255;3;0;9;Current nonce: 3B91B8117E813E6F0E12221791A78309559E5052097A420E8AAAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: ACFBD53ADA240C2FF69FF474887A750BEC719180D3A30B132AF241E94D8CF15B
                              0;255;3;0;9;Signature bad: 01FBD53ADA240C2FF69FF474887A750BEC719180D3A3
                              0;255;3;0;9;read: 32-32-0 s=0,c=3,t=16,pt=0,l=0,sg=0:
                              0;255;3;0;9;SHA256: 694B1F7903CB8A6854DAF8509AA451207AD040D71966A3453D7D5772649E35E9
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:694B1F7903CB8A6854DAF8509AA451207AD040D71966A3453D
                              0;255;3;0;9;Signature in message: 0113C5AA4FDD7E2F61EAA2C3F2716BCEEFB56292BA66BC98A4
                              0;255;3;0;9;Message to process: 200006001F00
                              0;255;3;0;9;Current nonce: 694B1F7903CB8A6854DAF8509AA451207AD040D71966A3453DAAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: 786E3B4757AA9BA51BB69546A59AC2E07B4FD696E79A72BF4DBD14530CBDFB21
                              0;255;3;0;9;Signature bad: 016E3B4757AA9BA51BB69546A59AC2E07B4FD696E79A72BF4D
                              0;255;3;0;9;SHA256: 13F0B25E5D9A117DA1146AFA7494C90FA33FA03B128B0CE3E1ED939BDD46DD66
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:13F0B25E5D9A117DA1146AFA7494C90FA33FA03B128B0CE3E1
                              0;255;3;0;9;Signature in message: 0171BF42F9C80CC00B5319226D836566CD4F95123E96258FF8
                              0;255;3;0;9;Current nonce: 13F0B25E5D9A117DA1146AFA7494C90FA33FA03B128B0CE3E1AAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: 7C9BD8227613765CC0A7D20E5C76396F6B380BB4D6A4199CDAB76C4D5CFF5C43
                              0;255;3;0;9;Signature bad: 019BD8227613765CC0A7D20E5C76396F6B380BB4D6A4199CDA
                              0;255;3;0;9;read: 27-27-0 s=13,c=1,t=8,pt=7,l=5,sg=0:0.13
                              0;255;3;0;9;read: 27-27-0 s=13,c=1,t=9,pt=7,l=5,sg=0:0.40
                              0;255;3;0;9;read: 27-27-0 s=12,c=1,t=10,pt=7,l=5,sg=0:225.00
                              0;255;3;0;9;read: 27-27-0 s=12,c=1,t=24,pt=7,l=5,sg=0:0.02
                              0;255;3;0;9;SHA256: 8FBD6C07C7957826D2BAF13CDD7A82D8082180FD4F0796F6B4E49547312D56B7
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:8FBD6C07C7957826D2BAF13CDD7A82D8082180FD4F0796F6B4
                              0;255;3;0;9;Signature in message: 01AC958E93696F29B508B534322FC0237EB1740405F2A7AA2A
                              0;255;3;0;9;Current nonce: 8FBD6C07C7957826D2BAF13CDD7A82D8082180FD4F0796F6B4AAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: 2C52B5D52BDA0030F2BC63D2CE6EB6CF7ED83AB9F35DCEA61147FB3429B03170
                              0;255;3;0;9;Signature bad: 0152B5D52BDA0030F2BC63D2CE6EB6CF7ED83AB9F35DCEA611
                              0;255;3;0;9;read: 26-26-0 s=1,c=3,t=16,pt=0,l=0,sg=0:
                              0;255;3;0;9;SHA256: 53FB5496D3358338CE2D5082FAC5D043DE6D4E0D607275D2F3908F0F1AF8CB73
                              0;255;3;0;9;send: 0-0-26-26 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:53FB5496D3358338CE2D5082FAC5D043DE6D4E0D607275D2F3
                              0;255;3;0;9;Signature in message: 012C20F0DC9CF89B84455FA90271B4823E60DF9D
                              0;255;3;0;9;Message to process: 1A002EE100014879D04101
                              0;255;3;0;9;Current nonce: 53FB5496D3358338CE2D5082FAC5D043DE6D4E0D607275D2F3AAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: 1D593C273D7167F9756DCA5CE4AF8005D7E5B8D6B95CF2C3B0C10A839E057FC3
                              0;255;3;0;9;Signature bad: 01593C273D7167F9756DCA5CE4AF8005D7E5B8D6
                              0;255;3;0;9;read: 26-26-0 s=2,c=3,t=16,pt=0,l=0,sg=0:
                              0;255;3;0;9;SHA256: 3081C0AF2996E0041CC85171727DB5F96A8201CF0BCC0D92FE3CC33C2A7B9705
                              0;255;3;0;9;send: 0-0-26-26 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:3081C0AF2996E0041CC85171727DB5F96A8201CF0BCC0D92FE
                              0;255;3;0;9;Signature in message: 01395A6873A0741CFD612BEC59D9E865888C6C29
                              0;255;3;0;9;Message to process: 1A002EE10102905B3A4201
                              0;255;3;0;9;Current nonce: 3081C0AF2996E0041CC85171727DB5F96A8201CF0BCC0D92FEAAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: 137DD0BB67606DDBF1F16854BFE720BB29C6ED1BFDD421430688DFC08F0813AF
                              0;255;3;0;9;Signature bad: 017DD0BB67606DDBF1F16854BFE720BB29C6ED1B
                              0;255;3;0;9;SHA256: 6BB69A71C65A24D7077B9B2A2E65D51B3861A56CF777BBD6B6B626B2A3942FAF
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:6BB69A71C65A24D7077B9B2A2E65D51B3861A56CF777BBD6B6
                              0;255;3;0;9;Signature in message: 012DE76DD7349510C9CAE6F072875D7D7C380BBDD00C65339B
                              0;255;3;0;9;Current nonce: 6BB69A71C65A24D7077B9B2A2E65D51B3861A56CF777BBD6B6AAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: A7FC0A4823BBE2F65EFC0F872743D808BB3DE432CCDEED33353C46B6D50736DD
                              0;255;3;0;9;Signature bad: 01FC0A4823BBE2F65EFC0F872743D808BB3DE432CCDEED3335
                              0;255;3;0;9;read: 22-22-0 s=3,c=1,t=0,pt=7,l=5,sg=0:31.0
                              0;255;3;0;9;Sending message on topic: GW1_out/22/3/1/0/0
                              0;255;3;0;9;SHA256: B7CD5773148E8916C98B5BB16265F17811F8091A560A3535EB6113A76207EE59
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:B7CD5773148E8916C98B5BB16265F17811F8091A560A3535EB
                              0;255;3;0;9;Signature in message: 01959641C93642F85E13499948DC33F1CE3B1B0DE5D8DEC8F5
                              0;255;3;0;9;Current nonce: B7CD5773148E8916C98B5BB16265F17811F8091A560A3535EBAAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: 218006AFDB5D1A909B39808D0F79E620974D2B7A291A929FD4524C0D3E5BEF9E
                              0;255;3;0;9;Signature bad: 018006AFDB5D1A909B39808D0F79E620974D2B7A291A929FD4
                              0;255;3;0;9;SHA256: 43AADEA58D5CC9AF0A58FE4A763CEE560CB751BCF31BAD7F4CCAEEC0925C60AA
                              0;255;3;0;9;send: 0-0-32-32 s=255,c=3,t=17,pt=6,l=25,sg=0,st=ok:43AADEA58D5CC9AF0A58FE4A763CEE560CB751BCF31BAD7F4C
                              0;255;3;0;9;Signature in message: 0117705F14F7482ACEEC510ADD5EB2CBB329B3FA4754861826
                              0;255;3;0;9;Current nonce: 43AADEA58D5CC9AF0A58FE4A763CEE560CB751BCF31BAD7F4CAAAAAAAAAAAAAA
                              0;255;3;0;9;HMAC: DD7AADA9C207653FF0E5184E006CCB4707837275511EC2136773AEFE80C89AB9
                              0;255;3;0;9;Signature bad: 017AADA9C207653FF0E5184E006CCB4707837275511EC21367
                              • AnticimexA
                                AnticimexA
                                Anticimex
                                I believe we sorted this through chat/github. Thanks for finding the issue and helping out with testing!
                                • T
                                  tomkxy
                                  @anticimex Thanks to your excellent working, it is working now.
                                  • AnticimexA
                                    AnticimexA
                                    Anticimex
                                    #36
                                    :+1: