  3. Software signing suddenly stop working
28 Posts 3 Posters 6.8k Views 4 Watching
  • AnticimexA Anticimex
    @sineverba
    1. I am not sure. I assume you run the 2.2.0-rc.1 version on all nodes and gw? The documentation you read is for that branch (development branch).
    2. The verifying node is the node that verifies the signatures. That is, the node that require signatures. It can be both ends if both require signatures (node and GW)
    3. No, I meant "someone" could sniff. The library itself does not offer sniffing APIs.
    sineverba
    @Anticimex No, I'm running the 2.1.1 on all nodes and gw.
    In this moment I did re-enable the signature and signing software section on the gateway (but not in nodes, no nodes have signing enabled). All works. I can confirm.
    For the 2 (whitelisting) I did enable only on the node that require signature, i.e. the relay node. Not in gw, not in no others nodes.
    For the 3, maybe I was not clear. I did mean if I did have the possibility, on receive function, as following pseudo code:
    if (message.getSenderSerial() == 0X01,0XAA, 0XBB) {
        Serial.println("We did receive this message from our gateway... we can proceed");
    • S sineverba
      AnticimexA
      AnticimexA
      Anticimex
      • S sineverba
        AnticimexA
        AnticimexA
        Anticimex
        @sineverba your config seem correct.
          sineverba
          wrote on last edited by sineverba
          A small update.
          1 - I did delete the library and re-downloaded from Github
          2 - I did clear the EEPROM of gateway
          3 - I did clear the EEPROM of a new Atmega328 (for relay / actuactor)
          4 - I did reinstall the Gateway sketch and the sketch for the relay heater, with signing.
          ..... it works......
          Yes, too many changes all together..... And fortunately I did receive today the PCBs for it, so in next days I will solder it on a firm base and not on breadboard.....
          After 30 min, no working anymore...... :( :( Fake alarm.... maybe some trouble with breadboard, maybe oxyde.... I will test in some day on PCB.
          AnticimexA 1 Reply Last reply
          • S sineverba
            A small update.
            AnticimexA
            AnticimexA
            Anticimex
            @sineverba uhm, if you cleared the eeprom, you have erased your personalization data. So now you run without a signing key. So your signatures are worthless.
            You also still run 2.1.1 because that would not work on 2.2.0,iy has checks for such things.
            You will need to redo personalization if you erase the eeprom.
            S 1 Reply Last reply
              sineverba
              @Anticimex I did forget a step. I did reinstall the personalization also, but after 20/30 mins, all stop works.
              I could try also the 2.2.0rc. Do I need every node and gw on same release or can I mix nodes and gw between 2.1.1 and 2.2.0 ?
              • S sineverba
                AnticimexA
                AnticimexA
                Anticimex
                @sineverba ok, I strongly suggest you instead just post your logs (or read them yourself). If you get NACKs, you can reflash and re-personalize all you want. Signing will never work as long as you get NACKs. You have to fix that problem by either tuning your rf settings, checking your rf environment or power supplies.
                • brendanlB
                  brendanlB
                  brendanl
                  Well I've just got mine working again. I'm putting it down to the birds not just crossing, but circulating for the last couple of weeks!
                  After the work last night, I moved my Gateway into the same room as my node on the breadboard in order to swap radios and it instantly became more responsive (much less NACKs & much less randomness on signed communication). I continued swapping radios etc to at least demonstrate consistency/working radios, but the location improvement alone was a Big Clue!
                  I have a NRF24L with the external aerial on the gateway, so was always expecting it to continue performing well regardless of what was around it. In my case though it was sitting above a metal 19" network patch panel & right next to a running laptop. Inside the patch panel as well as numerous runs of Cat6, is a 24port switch and a 8 port POE switch. Fair enough, plenty of interference potential, but I don't recall changing any of that recently (for it to just drop out).
                  Anyway, whether it's a combination of things, wriggling some wires, resetting some radios in their sockets etc or just now positioning the Gateway further from all the metal, we're back in business.
                  I agree, nothing wrong with the software, but perhaps somewhat sensitive on the environmental factors.
                  Thanks guys and good luck with the remainder of yours @sineverba
                    sineverba
                    @Anticimex
                    I'm looking and investigating for this issue.
                    My network of sensors is located at channel 125, by the way I did notice new troubles when Wifi of ADSL is under heavy load.
                    I did use two different scanner, and this is the output.
                    And other scanner
                    I don't know if my choice to move the radio to channel 125 is ok. In effect, on the node with relay/actuactor, I have also the traffic light. When wifi is under heavy load, I can see the red led blinking. No red when no wifi is used.
                    On another website (http://arduino-info.wikispaces.com/Nrf24L01-2.4GHz-HowTo) I did read the hint to move the radios to channel 108.
                    What do you think about?
                    • S sineverba
                      @Anticimex
                      And other scanner
                      AnticimexA
                      AnticimexA
                      Anticimex
                      @sineverba I'd suggest that if you can analyze the traffic, pick a channel with low "competing" traffic. Wifi and nrf work in the same band, so it would also to some extent depend on your (and your surroundings) use of various wifi channels. It's difficult to give any recommendations. Just try various and see which have the fewest failed transmissions.
                        sineverba
                        #27
                        @Anticimex
                        I'm investigating on this issue.
                        1. I'm on channel 125 (last one, the more free channel on my house).
                        2. I have a node on a custom printed pcb with atmega328@8MHZ and an Amplified Antenna. This node is feeded via a LM11173v3 from a 5V 2A samsung charger. This node also has a 100uF near the VCC/GND of antenna.
                        3. I have a PI2 + Arduino UNO (genuine!) with an amplified antenna with socket module. The amplified antenna is feeded via the socket module from 5V of PI.
                        4. I did clear the EEPROM of Gateway, reloaded the personalization sketch and the Gateway Sketch.
                        5. I did load the range finder sketch test from @Boots33 located here: https://forum.mysensors.org/topic/4567/repeater-node-problems/17
                        RESULT WITHOUT THE SIGNING ENABLED:
                        0 MCO:BGN:INIT NODE,C⸮=RNNNA--,VER=2.1.1
                        4 TSM:INIT
                        4 TSF:WUR:MS=0
                        12 TSM:INIT:TSP OK
                        14 TSF:SID:OK,ID=6
                        16 TSM:FPAR
                        51 TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                        712 TSF:MSG:READ,0-0-6,s=255,c=3,t=8,pt=1,l=1,sg=0:0
                        718 TSF:MSG:FPAR OK,ID=0,D=1
                        2060 TSM:FPAR:OK
                        2060 TSM:ID
                        2062 TSM:ID:OK
                        2064 TSM:UPL
                        2068 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=OK:1
                        2084 TSF:MSG:READ,0-0-6,s=255,c=3,t=25,pt=1,l=1,sg=0:1
                        2088 TSF:MSG:PONG RECV,HP=1
                        2093 TSM:UPL:OK
                        2095 TSM:READY:ID=6,PAR=0,DIS=1
                        2099 TSF:MSG:SEND,6-6-0-0,⸮=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=OK:0100
                        2107 Waiting for GW to send signing preferences...
                        2138 TSF:MSG:READ,0-0-6,s=255,c=3,t=15,pt=6,l=2,sg=0:0100
                        2144 Received signing presentation, but signing is not supported (message ignored)
                        2154 TSF:MSG:SEND,6-6-0-0,s=255,c=0,t=17,pt=0,l=5,sg=0,ft=0,st=OK:2.1.1
                        2164 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=6,pt=1,l=1,sg=0,ft=0,st=OK:0
                        2185 TSF:MSG:READ,0-0-6,s=255,c=3,t=6,pt=0,l=1,sg=0:M
                        2195 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=11,pt=0,l=12,sg=0,ft=0,st=OK:Range Finder
                        2207 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=12,pt=0,l=3,sg=0,ft=0,st=OK:1.0
                        2217 TSF:MSG:SEND,6-6-0-0,s=0,c=0,t=16,pt=0,l=0,sg=0,ft=0,st=OK:
                        2224 MCO:REG:REQ
                        2230 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=26,⸮t=1,l=1,sg=0,ft=0,st=OK:2
                        2244 TSF:MSG:READ,0-0-6,s=255,c=3,t=27,pt=1,l=1,sg=0:1
                        2248 MCO:PIM:NODE REG=1
                        2252 MCO:BGN:INIT OK,TSP=1
                        2256 TSF:MSG:SEND,6-6-0-0,s=0,c=1,t=23,pt=2,l=2,sg=0,ft=0,st=OK:0
                        3266 TSF:MSG:SEND,6-6-0-0,s=0,c=1,t=23,pt=2,l=2,sg=0,ft=0,st=OK:1
                        And it goes to "infinity" to 20 and restart. NO missing 1 send in about 30 minutes.. Very happy with this.
                        After, I did enable the Signing Personalization:
                         * rangeTester
                        #define MY_SIGNING_SOFT
                        #define MY_SIGNING_NODE_WHITELISTING {{.nodeId = GATEWAY_ADDRESS,.serial = {0x3B,0xF4,0xDD,0xDF,0x1E,0x97,0xB1,0xFB,0xEC}}}
                        #define MY_RF24_CHANNEL 125
                        #define CHILD_ID_LIGHT 0
                        unsigned long WAIT_TIME = 1000; //  time between reads (in milliseconds)
                        void presentation()  {
                          sendSketchInfo("Range Finder", "1.0");
                         for (int i=0; i<20; i++) {
                           send(msg.set(i));
                           Serial.println(i);
                           wait(WAIT_TIME);
                        It is a disaster... This is the LOG:
                        ⸮0 MCO:BGN:INIT NODE,CP=RNNNAS-,VER=2.1.1
                        4 TSM:INIT
                        4 TSF:WUR:MS=0
                        12 TSM:INIT:TSP OK
                        14 TSF:SID:OK,ID=6
                        16 TSM:FPAR
                        59 TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                        1032 TSF:MSG:READ,0-0-6,s=255,c=3,t=8,pt=1,l=1,sg=0:0
                        1038 Skipping security for command 3 type 8
                        1042 TSF:MSG:FPAR OK,ID=0,D=1
                        2068 TSM:FPAR:OK
                        2068 TSM:ID
                        2070 TSM:ID:OK
                        2072 TSM:UPL
                        2074 Skipping security for command 3 type 24
                        2080 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=OK:1
                        2097 TSF:MSG:READ,0-0-6,s=255,c=3,t=25,pt=1,l=1,sg=0:1
                        2103 Skipping security for command 3 type 25
                        2107 TSF:MSG:PONG RECV,HP=1
                        2109 TSM:UPL:OK
                        2111 TSM:READY:ID=6,PAR=0,DIS=1
                        2115 Signing required
                        2117 Whitelisting required
                        2119 Skipping security for command 3 type 15
                        2127 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=OK:0103
                        2134 Waiting for GW to send signing preferences...
                        2162 TSF:MSG:READ,0-0-6,s=255,c=3,t=15,pt=6,l=2,sg=0:0101
                        2168 Skipping security for command 3 type 15
                        2172 Mark node 0 as one that require signed messages
                        2179 Mark node 0 as one that do not require whitelisting
                        2185 Skipping security for command 3 type 16
                        2191 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=16,pt=0,l=0,sg=0,ft=0,st=OK:
                        2197 Nonce requested from 0. Waiting...
                        7202 Timeout waiting for nonce!
                        7204 !TSF:MSG:SIGN FAIL
                        7206 Skipping security for command 3 type 16
                        7213 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=16,pt=0,l=0,sg=0,ft=1,st=OK:
                        7221 Nonce requested from 0. Waiting...
                        12226 Timeout waiting for nonce!
                        12228 !TSF:MSG:SIGN FAIL
                        14231 Skipping security for command 3 type 16
                        14239 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=16,pt=0,l=0,sg=0,ft=1,st=OK:
                        14245 Nonce requested from 0. Waiting...
                        14282 TSF:MSG:READ,0-0-6,s=255,c=3,t=17,pt=6,l=25,sg=0:CDD8E3A6EF6862ABE47C625626385D9C43B17DF5EED6C19A8C
                        14295 Skipping security for command 3 type 17
                        14299 Nonce received from 0.
                        14303 Proceeding with signing...
                        Message to process: 060066030BFF52616E67652046696E646572
                        Current nonce: CDD8E3A6EF6862ABE47C625626385D9C43B17DF5EED6C19A8CAAAAAAAAAAAAAA
                        HMAC: 2FBD5D7E220EB6B33DDC59893EE33081AB9C3A6069BA1DBB0DBC9C52B354AE9D
                        Signature in message: 01BD5D7E220EB6B33DDC59893E
                        14477 Message ⸮igned
                        14485 Message to send has been signed
                        14491 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=11,pt=0,l=12,sg=1,ft=0,st=OK:Range Finder
                        14499 Skipping security for command 3 type 16
                        14510 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=16,pt=0,l=0,sg=1,ft=0,st=OK:
                        14518 Nonce requested from 0. Waiting...
                        19523 Timeout waiting for nonce!
                        19525 !TSF:MSG:SIGN FAIL
                        19529 Skipping security for command 3 type 16
                        19535 TSF:MSG:SEND,6-6-0-0,s=0,c=3,t=16,pt=0,l=0,sg=1,ft=1,st=OK:
                        19544 Nonce requested from 0. Waiting...
                        24549 Timeout waiting for nonce!
                        24551 !TSF:MSG:SIGN FAIL
                        24553 MCO:REG:REQ
                        24555 Skipping security for command 3 type 26
                        24563 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=26,pt=1,l=1,sg=1,ft=1,st=OK:2
                        24592 TSF:MSG:READ,0-0-6,s=255,c=3,t=16,pt=0,l=0,sg=1:
                        24598 Skipping security for command 3 type 16
                        SHA256: C88B09B24FEE7C0C5CA06C1C70DB958B075D545BCED7A42C4E00000000000000
                        24633 Skipping security for command 3 type 17
                        24647 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=17,pt=6,l=25,sg=1,ft=0,st=OK:C88B09B24FEE7C0C5CA06C1C70DB958B075D545BCED7A42C4E
                        24659 Transmitted nonce
                        24788 TSF:MSG:READ,0-0-6,s=255,c=3,t=27,pt=1,l=1,sg=1:1
                        Signature in message: 01C615639AAE6055592C7394379A9FD7A448D9BAAE6D8057
                        Message to process: 00060E231BFF01
                        Current nonce: C88B09B24FEE7C0C5CA06C1C70DB958B075D545BCED7A42C4EAAAAAAAAAAAAAA
                        HMAC: 955CF8A12B90E36B4D42B321FFD79586AFEED8566A0162025D1DD3A826393EDD
                        SHA256: 80C615639AAE6055592C7394379A9FD7A448D9BAAE6D80572ADFBC1FA45A61E3
                        24993 MCO:PIM:NODE REG=1
                        24999 MCO:BGN:INIT OK,TSP=1
                        25004 Skipping security for command 3 type 16
                        25012 TSF:MSG:SEND,6-6-0-0,s=0,c=3,t=16,pt=0,l=0,sg=1,ft=0,st=OK:
                        25018 Nonce requested from 0. Waiting...
                        25083 TSF:MSG:READ,0-0-6,s=255,c=3,t=17,pt=6,l=25,sg=1:098D99FFD443EF2C0D37320ACE0BC0E4B57FFAF6A5705FC2EC
                        25096 Skipping security for command 3 type 17
                        25100 Nonce received from 0.
                        25102 Proceeding with signing...
                        Message to process: 0600164117000000
                        Current nonce: 098D99FFD443EF2C0D37320ACE0BC0E4B57FFAF6A5705FC2ECAAAAAAAAAAAAAA
                        HMAC: A7147AC2A73D5C389A437078A9F2D022528FED7B2431DA3226B05C3C616039B7
                        Signature in message: 01147AC2A73D5C389A437078A9F2D022528FED7B2431DA
                        25278 Message signed
                        25284 Message to send has been signed
                        25292 TSF:MSG:SEND,6-6-0-0,s=0,c=1,t=23,pt=2,l=2,sg=1,ft=0,st=OK:0
                        26298 Skipping security for command 3 type 16
                        26316 TSF:MSG:SEND,6-6-0-0,s=0,c=3,t=16,pt=0,l=0,sg=1,ft=0,st=OK:
                        26322 Nonce requested from 0. Waiting...
                        26378 TSF:MSG:READ,0-0-6,s=255,c=3,t=17,pt=6,l=25,sg=1:79101C63451593B1924BD221797435507AB7AC59C55558D365
                        26388 Skipping security for command 3 type 17
                        26394 Nonce received from 0.
                        26396 Proceeding with signing...
                        Message to process: 0600164117000100
                        Current nonce: 79101C63451593B1924BD221797435507AB7AC59C55558D365AAAAAAAAAAAAAA
                        HMAC: 11D124CC8BA9369358F58569ACBC78ABE57B21C64FA46FCA9E4DCEAEF4042933
                        Signature in message: 01D124CC8BA9369358F58569ACBC78ABE57B21C64FA46F
                        26570 Message signed
                        26578 Message to send has been signed
                        26589 TSF:MSG:SEND,6-6-0-0,s=0,c=1,t=23,pt=2,l=2,sg=1,ft=0,st=OK:1
                        27596 Skipping security for command 3 type 16
                        27602 TSF:MSG:SEND,6-6-0-0,s=0,c=3,t=16,pt=0,l=0,sg=1,ft=0,st=OK:
                        27611 Nonce requested from 0. Waiting...
                        32616 Timeout waiting for nonce!
                        32618 !TSF:MSG:SIGN FAIL
                        33622 Skipping security for command 3 type 16
                        33632 TSF:MSG:SEND,6-6-0-0,s=0,c=3,t=16,pt=0,l=0,sg=1,ft=1,st=OK:
                        33638 Nonce requested from 0. Waiting...
                        38643 Timeout waiting for nonce!
                        38645 !TSF:MSG:SIGN FAIL
                        39649 Skipping security for command 3 type 16
                        39659 TSF:MSG:SEND,6-6-0-0,s=0,c=3,t=16,pt=0,l=0,sg=1,ft=1,st=OK:
                        39665 Nonce requested from 0. Waiting...
                        Sometimes it signs, often no. Could be that ACK // timeout for nonce is too fast?
                        =================== UPDATE ?======================================
                        I did just swap from this radio
                        To this << edited >> radio.... with plastic and aluminium to shield it...
                        I would say victory.... now nonce is coming istantly.....
                        ================= NEW UPDATE ============================
                        I did swap the radio from node and gateway. Gateway with black and node with shielded. No issue, no issue. Probabily the shielded doesn't like Arduino or simply doesn't love the jumpers and works like a charme with a pcb.... don't know, in aliexpress they have so many positive feedback.....
                        • S sineverba
                          @Anticimex
                          4 TSM:INIT
                          4 TSF:WUR:MS=0
                          12 TSM:INIT:TSP OK
                          14 TSF:SID:OK,ID=6
                          16 TSM:FPAR
                          2060 TSM:FPAR:OK
                          2060 TSM:ID
                          2062 TSM:ID:OK
                          2064 TSM:UPL
                          2093 TSM:UPL:OK
                          2224 MCO:REG:REQ
                           * rangeTester
                             send(msg.set(i));
                             Serial.println(i);
                             wait(WAIT_TIME);
                          4 TSM:INIT
                          4 TSF:WUR:MS=0
                          12 TSM:INIT:TSP OK
                          14 TSF:SID:OK,ID=6
                          16 TSM:FPAR
                          2068 TSM:FPAR:OK
                          2068 TSM:ID
                          2070 TSM:ID:OK
                          2072 TSM:UPL
                          2109 TSM:UPL:OK
                          24553 MCO:REG:REQ
                          AnticimexA
                          AnticimexA
                          Anticimex
                          @sineverba great that you got it working. Yes, signing require a solid radio link. It is not so much a matter of "signing is not working" but rather "radio is not working".