Whole house power monitoring.

Scheduled Pinned Locked Moved Hardware
hardware sensor power
44 Posts 11 Posters 8.2k Views 11 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • gohanG gohan

    @zboblamont just for clarification, what do you mean by "direct reading "?

    zboblamontZ Offline
    zboblamontZ Offline
    zboblamont
    wrote on last edited by
    #26

    @gohan Sorry for any confusion, I meant in-line meters, where there is direct reading of voltage, current, pf, etc....

    gohanG 1 Reply Last reply
    0
    • zboblamontZ zboblamont

      @gohan Sorry for any confusion, I meant in-line meters, where there is direct reading of voltage, current, pf, etc....

      gohanG Offline
      gohanG Offline
      gohan
      Mod
      wrote on last edited by
      #27

      @zboblamont have you found any worth mentioning?

      zboblamontZ 1 Reply Last reply
      0
      • gohanG gohan

        @zboblamont have you found any worth mentioning?

        zboblamontZ Offline
        zboblamontZ Offline
        zboblamont
        wrote on last edited by
        #28

        @gohan I guess you meant in-line meters? Not specific device recommendations, but more a methodology, none of which is new.

        The supply here is about 65A, so perhaps not euro-typical, in the UK it would be a standard 100A supply even though full load current would rarely top 50A unless you were simultaneously loading supply with some hefty coincidental peak demand, and electricity ain't cheap particularly in the UK.

        If you were measuring each major circuit separately, a 45A meter could easily cover all sockets, another could cover all lighting, each with a kWh pulse output, all you need is space for 2 standard DIN units, or 3 if you had a high load such as an instant shower or cooker. These will comfortably measure kWh to a high degree of accuracy, pulsing out according to choice of model, probably 30 euro each.

        Where expanding the consumer box or adding to it is not physically possible, that is where I view CTs as solution to achieve the objective, but it remains a compromise.

        1 Reply Last reply
        0
        • gohanG Offline
          gohanG Offline
          gohan
          Mod
          wrote on last edited by
          #29

          I am using a couple of sonoff pow to measure kitchen and washing machine as they are the most power hungry devices. I am also using a pulse counter on the electric company meter but I figured it is not really working well in reporting instant power readings, while the pulse counter is counting fine but power calculation by domoticz is too slow and I can't use it to switch off the big loads in case of overload ( over here we have 3000W maximum allowed and if you exceed that for few minutes the main switch will cut the power and I was planning to avoid those situations with the help of the sonoffs pow)

          raptorjrR 1 Reply Last reply
          0
          • gohanG gohan

            I am using a couple of sonoff pow to measure kitchen and washing machine as they are the most power hungry devices. I am also using a pulse counter on the electric company meter but I figured it is not really working well in reporting instant power readings, while the pulse counter is counting fine but power calculation by domoticz is too slow and I can't use it to switch off the big loads in case of overload ( over here we have 3000W maximum allowed and if you exceed that for few minutes the main switch will cut the power and I was planning to avoid those situations with the help of the sonoffs pow)

            raptorjrR Offline
            raptorjrR Offline
            raptorjr
            wrote on last edited by
            #30

            @gohan Just curious, where do you live with those restrictions?

            gohanG 1 Reply Last reply
            1
            • raptorjrR raptorjr

              @gohan Just curious, where do you live with those restrictions?

              gohanG Offline
              gohanG Offline
              gohan
              Mod
              wrote on last edited by
              #31

              @raptorjr Italy, that is the most common contract for homes, but there are other contracts with 4500w or more and you get charged with an higher fixed monthly fee for the extra power availability even if you actually use it once a month

              1 Reply Last reply
              0
              • gohanG gohan

                @kimot yeah, 5 minutes intervals are not the best for that kind of statistics; you'd probably better look at influxDB for more accurate statistics

                K Offline
                K Offline
                kimot
                wrote on last edited by
                #32

                @gohan
                5 min interval is not big problem for me.
                Problem is, that this last 5 min interval in each hour is completely lost.
                They do not add it to next hour.
                Next hour is calculated from hh:mm:00 again.
                So first interval hh:00:00 to hh:mm:04.
                InfluxDB is good, but I want all at one web ( domoticz ).
                I try calculate power consumption myself through some Domoticz script.

                1 Reply Last reply
                0
                • S shabba

                  Hi,
                  I see some commercial offering that count meter ticks but are there any clamp style current meters that people have used to measure power usage in a house?

                  Thanks!

                  T Offline
                  T Offline
                  terryrow
                  wrote on last edited by
                  #33

                  @shabba I have used a clamp meter and arduino uno to monitor power levels, disadvantages are that you need to full wave rectify, provide load resistor and smoothing. Measurement becomes a bit of guesswork as to how many volts o/p in a Kwh.
                  Here in Britain, meters have a LED that flashes 1000 times per Kw. I have used a digital light sensor input into arduino uno digital input and then measured the time between flashes in msecs to give accurate readings. I use have used both methods to monitor solar panel output, then turn on Leaf BEV car when sufficient free power is available and off again when clouds arrive. Next step is to o/p readings to a Nextion for both solar and grid power readings with adjustment of turn on thresholds to optimise summer and winter useage.

                  gohanG zboblamontZ 2 Replies Last reply
                  1
                  • T terryrow

                    @shabba I have used a clamp meter and arduino uno to monitor power levels, disadvantages are that you need to full wave rectify, provide load resistor and smoothing. Measurement becomes a bit of guesswork as to how many volts o/p in a Kwh.
                    Here in Britain, meters have a LED that flashes 1000 times per Kw. I have used a digital light sensor input into arduino uno digital input and then measured the time between flashes in msecs to give accurate readings. I use have used both methods to monitor solar panel output, then turn on Leaf BEV car when sufficient free power is available and off again when clouds arrive. Next step is to o/p readings to a Nextion for both solar and grid power readings with adjustment of turn on thresholds to optimise summer and winter useage.

                    gohanG Offline
                    gohanG Offline
                    gohan
                    Mod
                    wrote on last edited by
                    #34

                    @terryrow do you mind sharing your pulse meter code?

                    T 1 Reply Last reply
                    0
                    • T terryrow

                      @shabba I have used a clamp meter and arduino uno to monitor power levels, disadvantages are that you need to full wave rectify, provide load resistor and smoothing. Measurement becomes a bit of guesswork as to how many volts o/p in a Kwh.
                      Here in Britain, meters have a LED that flashes 1000 times per Kw. I have used a digital light sensor input into arduino uno digital input and then measured the time between flashes in msecs to give accurate readings. I use have used both methods to monitor solar panel output, then turn on Leaf BEV car when sufficient free power is available and off again when clouds arrive. Next step is to o/p readings to a Nextion for both solar and grid power readings with adjustment of turn on thresholds to optimise summer and winter useage.

                      zboblamontZ Offline
                      zboblamontZ Offline
                      zboblamont
                      wrote on last edited by
                      #35

                      @terryrow Out of curiosity, was there no output pulse connection on the meter, or is it a sealed 'smart' meter from the supplier?
                      Wh pulses appear to be rare on supplier provided meter which piqued my curiosity, they are generally kWh pulses...

                      T 1 Reply Last reply
                      0
                      • gohanG Offline
                        gohanG Offline
                        gohan
                        Mod
                        wrote on last edited by gohan
                        #36

                        Our utility company meters have a flashing led that flashes 1000 times for every Kwh, so 1 flash is a wh

                        zboblamontZ 1 Reply Last reply
                        0
                        • gohanG gohan

                          Our utility company meters have a flashing led that flashes 1000 times for every Kwh, so 1 flash is a wh

                          zboblamontZ Offline
                          zboblamontZ Offline
                          zboblamont
                          wrote on last edited by zboblamont
                          #37

                          @gohan said in Whole house power monitoring.:

                          Our utility company meters have a flashing led that flashes 1000 times for every Kwh, so 1 flash is a wh

                          Fair comment for Italy, but I do not recall similar for the UK, although I must confess I had little interest with respect to monitoring systems at the time.

                          In Romania they have the habit of placing smart meters with pulse flashers in rather large acrylic bubbles (a la Klockner Moeller) out on the main road, which not only renders optical detection difficult, put potentially removeable by every passing drunk.... Hence placing a padlock on the isolator access to dissuade the same folks from switching off the entire house from the main road...
                          ;)

                          1 Reply Last reply
                          0
                          • zboblamontZ zboblamont

                            @terryrow Out of curiosity, was there no output pulse connection on the meter, or is it a sealed 'smart' meter from the supplier?
                            Wh pulses appear to be rare on supplier provided meter which piqued my curiosity, they are generally kWh pulses...

                            T Offline
                            T Offline
                            terryrow
                            wrote on last edited by
                            #38

                            @zboblamont I cannot see any sockets for a digital o/p. Neither is a smart meter, but both are only 2 years old. The grid meter has an additional green led when power is going out of the house.

                            zboblamontZ 1 Reply Last reply
                            0
                            • gohanG gohan

                              @terryrow do you mind sharing your pulse meter code?

                              T Offline
                              T Offline
                              terryrow
                              wrote on last edited by
                              #39

                              @gohan Sorry I have been so long, some things, apparently, are more important than playing on my laptop. I managed to lose the "saved" copy when looking at Nextion mods. I have recovered/repaired and tidied the code but I need your help as to how to share with you.

                              gohanG 1 Reply Last reply
                              0
                              • T terryrow

                                @zboblamont I cannot see any sockets for a digital o/p. Neither is a smart meter, but both are only 2 years old. The grid meter has an additional green led when power is going out of the house.

                                zboblamontZ Offline
                                zboblamontZ Offline
                                zboblamont
                                wrote on last edited by
                                #40

                                @terryrow Sorry, perhaps I am misunderstanding your scenario in thinking it may be similar to my own.
                                I cannot access the supplier's meter or optically couple safely as explained above, but I can shut down power to the house, which allowed fitting of a DIN mounted meter in the consumer box. This has both external flashing LED and 2 connections for pulse measurement via clamp screws.

                                If the house meter is less than two years old, it will be digital, and these USUALLY have a connector for external pulse.
                                If you can physically access the meter, google the make and meter type for info, perhaps you have a model with similar pulse connection available. Hence my query...

                                1 Reply Last reply
                                0
                                • T terryrow

                                  @gohan Sorry I have been so long, some things, apparently, are more important than playing on my laptop. I managed to lose the "saved" copy when looking at Nextion mods. I have recovered/repaired and tidied the code but I need your help as to how to share with you.

                                  gohanG Offline
                                  gohanG Offline
                                  gohan
                                  Mod
                                  wrote on last edited by
                                  #41

                                  @terryrow just use pastebin and send the link :-)

                                  1 Reply Last reply
                                  0
                                  • T Offline
                                    T Offline
                                    terryrow
                                    wrote on last edited by
                                    #42

                                    Hello Gohan, unable to find the paste bin or any help section. I need more precise guidance please.

                                    1 Reply Last reply
                                    0
                                    • gohanG Offline
                                      gohanG Offline
                                      gohan
                                      Mod
                                      wrote on last edited by
                                      #43

                                      pastebin.com

                                      T 1 Reply Last reply
                                      0
                                      • gohanG gohan

                                        pastebin.com

                                        T Offline
                                        T Offline
                                        terryrow
                                        wrote on last edited by
                                        #44

                                        @gohan Thanks, eventually worked it out. https://pastebin.com/D0Cc8TSG should do it for you. writing to the Nextion is creating difficulties.

                                        1 Reply Last reply
                                        1
                                        Reply
                                        • Reply as topic
                                        Log in to reply
                                        • Oldest to Newest
                                        • Newest to Oldest
                                        • Most Votes


                                        14

                                        Online

                                        11.7k

                                        Users

                                        11.2k

                                        Topics

                                        113.1k

                                        Posts


                                        Copyright 2025 TBD   |   Forum Guidelines   |   Privacy Policy   |   Terms of Service
                                        • Login

                                        • Don't have an account? Register

                                        • Login or register to search.
                                        • First post
                                          Last post
                                        0
                                        • MySensors
                                        • OpenHardware.io
                                        • Categories
                                        • Recent
                                        • Tags
                                        • Popular