Skip to content
  • MySensors
  • OpenHardware.io
  • Categories
  • Recent
  • Tags
  • Popular
Skins
  • Light
  • Brite
  • Cerulean
  • Cosmo
  • Flatly
  • Journal
  • Litera
  • Lumen
  • Lux
  • Materia
  • Minty
  • Morph
  • Pulse
  • Sandstone
  • Simplex
  • Sketchy
  • Spacelab
  • United
  • Yeti
  • Zephyr
  • Dark
  • Cyborg
  • Darkly
  • Quartz
  • Slate
  • Solar
  • Superhero
  • Vapor

  • Default (No Skin)
  • No Skin
Collapse
Brand Logo
  1. Home
  2. Hardware
  3. Safe In-Wall AC to DC Transformers??

Safe In-Wall AC to DC Transformers??

Scheduled Pinned Locked Moved Hardware
431 Posts 71 Posters 457.6k Views 69 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • B Offline
    B Offline
    Bertb
    wrote on last edited by
    #114

    Wait Mike, there is more ...
    I sacrificed a device to the altar of success and opened it.
    That was not very difficult. After scratching away some gum stuff the following was revealed.
    I will try to remove the rest of the gum with acetone. I will also do some heat and burn tests.

    This is quite funny to do :-)

    IMG_20150728_214007.jpg IMG_20150728_214057.jpg IMG_20150728_214105.jpg IMG_20150728_214436.jpg

    1 Reply Last reply
    1
    • B Offline
      B Offline
      Bertb
      wrote on last edited by
      #115

      And I found the AP8012 chip inside. It has the following features:
      _1286955514_oj99d4.pdf

      YveauxY Moshe LivneM 3 Replies Last reply
      0
      • B Bertb

        And I found the AP8012 chip inside. It has the following features:
        _1286955514_oj99d4.pdf

        YveauxY Offline
        YveauxY Offline
        Yveaux
        Mod
        wrote on last edited by
        #116

        @Bertb Thanks Bert! Good digging!

        http://yveaux.blogspot.nl

        1 Reply Last reply
        0
        • B Bertb

          And I found the AP8012 chip inside. It has the following features:
          _1286955514_oj99d4.pdf

          Moshe LivneM Offline
          Moshe LivneM Offline
          Moshe Livne
          Hero Member
          wrote on last edited by
          #117

          @Bertb thanks! Good detective work! It seems the chip provide all the protections needed. That is very encouraging

          1 Reply Last reply
          0
          • scalzS Offline
            scalzS Offline
            scalz
            Hardware Contributor
            wrote on last edited by
            #118

            Thank you very much. I agree with you ap8012 seems to be a good chip. As we can see, it is difficult to make it smaller if we want all securities...and for the price including shipping I think they will sell lot of these things!

            1 Reply Last reply
            0
            • B Bertb

              And I found the AP8012 chip inside. It has the following features:
              _1286955514_oj99d4.pdf

              Moshe LivneM Offline
              Moshe LivneM Offline
              Moshe Livne
              Hero Member
              wrote on last edited by
              #119

              @Bertb it is hard to see from the photos, are the capacitors rated for 105c?

              1 Reply Last reply
              0
              • B Offline
                B Offline
                Bertb
                wrote on last edited by
                #120

                @Moshe. Yes they are. I did not yet dug into that, but is that good news?
                IMG_20150729_124755.jpg IMG_20150729_124953.jpg IMG_20150729_125107.jpg IMG_20150729_125455.jpg

                Moshe LivneM 1 Reply Last reply
                1
                • B Offline
                  B Offline
                  Bertb
                  wrote on last edited by Bertb
                  #121

                  Observe the air gaps.

                  I also tried to incinerate the gum stuff that is inside the module with a cigaret lighter.
                  After a couple of seconds it starts to glow, then, after some 10 seconds, the material starts to burn. But this stops within some 20 seconds ofter removal of the lighter.
                  I made a film, but it is too large to upload.

                  I am not an expert on AC-DC converters, but I am quite impressed by the layout of the design.
                  The only thing that worries me is that I do not see how the OVP is created. On the other hand, this can be easily solved by adding a fuse and a ovp zener in the primary circuit.

                  IMG_20150729_131014.jpg

                  1 Reply Last reply
                  0
                  • B Bertb

                    @Moshe. Yes they are. I did not yet dug into that, but is that good news?
                    IMG_20150729_124755.jpg IMG_20150729_124953.jpg IMG_20150729_125107.jpg IMG_20150729_125455.jpg

                    Moshe LivneM Offline
                    Moshe LivneM Offline
                    Moshe Livne
                    Hero Member
                    wrote on last edited by
                    #122

                    @Bertb yes,although to be expected. Did you see the comparison mentioned a bit earlier in this thread? That is the first thing he checked

                    1 Reply Last reply
                    0
                    • scalzS Offline
                      scalzS Offline
                      scalz
                      Hardware Contributor
                      wrote on last edited by
                      #123

                      In the datasheet we can see it is implemented in the chip (in the block diagram) and how it works is explained at page 7. If VCC not well built, the chip would not work well I think.

                      1 Reply Last reply
                      0
                      • B Offline
                        B Offline
                        Bertb
                        wrote on last edited by
                        #124

                        I do not totally agree with this. When I take a look at the example circuit and read the ovp text, I can only conclude that the output is protected, because the circuit seizes to work when VCC rises to high. Whatever happens to the input circuit, I don't know. Therefore I prefer a fuse and and a varistor.

                        Have a look at the tutorial link text

                        petewillP 1 Reply Last reply
                        1
                        • B Bertb

                          I do not totally agree with this. When I take a look at the example circuit and read the ovp text, I can only conclude that the output is protected, because the circuit seizes to work when VCC rises to high. Whatever happens to the input circuit, I don't know. Therefore I prefer a fuse and and a varistor.

                          Have a look at the tutorial link text

                          petewillP Offline
                          petewillP Offline
                          petewill
                          Admin
                          wrote on last edited by
                          #125

                          @Bertb thank you for your testing!!! Although I don't know much about hardware I am gathering by the posts here that it is mostly good news!

                          So, now for the big question... If I were to add an external fuse like pictured here does everyone agree this is safe to put in a wall?

                          And, a follow up question if the answer is yes. Are there any basic tests we can do at home to verify the performance should be the same as what was tested here?

                          My "How To" home automation video channel: https://www.youtube.com/channel/UCq_Evyh5PQALx4m4CQuxqkA

                          1 Reply Last reply
                          0
                          • rvendrameR Offline
                            rvendrameR Offline
                            rvendrame
                            Hero Member
                            wrote on last edited by
                            #126

                            @Bertb, thanks a lot. I guess you mention to put a varistor/fuse right at output of this device, for example a 7K 14V varistor in parallel, and a 500mA fuse in series?

                            And what about the fire burn test --- Perhaps is there a method to measure it (and compare to some standard?).

                            Home Assistant / Vera Plus UI7
                            ESP8266 GW + mySensors 2.3.2
                            Alexa / Google Home

                            1 Reply Last reply
                            0
                            • scalzS Offline
                              scalzS Offline
                              scalz
                              Hardware Contributor
                              wrote on last edited by
                              #127

                              I agree with you about varistor. it is a good idea.

                              1 Reply Last reply
                              0
                              • B Offline
                                B Offline
                                Bertb
                                wrote on last edited by Bertb
                                #128

                                I did not finish the automated power tester, but I put an HLK with a DS18B20 temp sensor in a closed flush box(is that the English word for the box in the wall, used for domestic wiring?).
                                A simple resistor acts as a load and draws a 800 mA from the power supply. That is 33% more than the max continuous value. Voltage across the leads is 4.96. That is 5.08 without load. Not too bad. At 600 mA (100% load) the voltage is also 5.00.
                                The Dallas says that the surface temperature at the HLK is 48.19 c ( F: 118.74).
                                Also do not forget to mount adequate capacitors to reduce ripple.

                                @petewill and @rvendrame ... Every country has directives regarding flammability. I cannot say which one is valid. I have seen some testing in the past. They put a burner under the device under test and waited to see what happened after removal of the source. In general (without any warranty whatsoever) when there are no flames or when they extinguish autonomic is good. If there is no hot material dripping from the DUT, that is also good. The test I carried out is described above. No dripping en self extinguishing. So I am satisfied.
                                Sorry, I cannot be more specific. I do not have the knowledge.

                                @rvendrame: yes the fuse in series in the mains live wire en the varistor in parallel with the primary side of the HLK.
                                With respect to the varistor ... see the sheet below:
                                Take a value that is well above the normal AC tension of your mains power, but below the max input voltage of the HLK. so in Netherlands 250 volts will do.

                                link text

                                Moshe LivneM 1 Reply Last reply
                                1
                                • B Offline
                                  B Offline
                                  Bertb
                                  wrote on last edited by
                                  #129

                                  Now for the million dollar question ... would I mount a HLK in a flush box?
                                  Well ... when equipped with varistor and fuse and with the load on the safe side ...
                                  Yes, I would.

                                  1 Reply Last reply
                                  0
                                  • rvendrameR Offline
                                    rvendrameR Offline
                                    rvendrame
                                    Hero Member
                                    wrote on last edited by
                                    #130

                                    @Bertb, thanks again. I got a bit confused, do you mean put the varistor + fuse into the PSU input (AC Mains)? I was more thinking in over voltage protection on output. So a low-volt varistor together with a fuse/ptc, both on the 5V output.

                                    My concern is having something wrong into the PSU-PWM control, and somehow the AC mains leaking to the low-volt side, cause arduino+friends burn/flaming. But I'm a hobbyist, so maybe I'm guessing wrong here.

                                    Maybe to be on safest side --- varistor + fuse/ptc on both AC mains and 5V rails?

                                    Home Assistant / Vera Plus UI7
                                    ESP8266 GW + mySensors 2.3.2
                                    Alexa / Google Home

                                    1 Reply Last reply
                                    0
                                    • B Offline
                                      B Offline
                                      Bertb
                                      wrote on last edited by Bertb
                                      #131

                                      My initial safety is always toward the biggest danger ... mains in this case.
                                      For the secondary part a simple semiconductor fuse and a zener (transzorb) will do.

                                      1 Reply Last reply
                                      0
                                      • B Bertb

                                        I did not finish the automated power tester, but I put an HLK with a DS18B20 temp sensor in a closed flush box(is that the English word for the box in the wall, used for domestic wiring?).
                                        A simple resistor acts as a load and draws a 800 mA from the power supply. That is 33% more than the max continuous value. Voltage across the leads is 4.96. That is 5.08 without load. Not too bad. At 600 mA (100% load) the voltage is also 5.00.
                                        The Dallas says that the surface temperature at the HLK is 48.19 c ( F: 118.74).
                                        Also do not forget to mount adequate capacitors to reduce ripple.

                                        @petewill and @rvendrame ... Every country has directives regarding flammability. I cannot say which one is valid. I have seen some testing in the past. They put a burner under the device under test and waited to see what happened after removal of the source. In general (without any warranty whatsoever) when there are no flames or when they extinguish autonomic is good. If there is no hot material dripping from the DUT, that is also good. The test I carried out is described above. No dripping en self extinguishing. So I am satisfied.
                                        Sorry, I cannot be more specific. I do not have the knowledge.

                                        @rvendrame: yes the fuse in series in the mains live wire en the varistor in parallel with the primary side of the HLK.
                                        With respect to the varistor ... see the sheet below:
                                        Take a value that is well above the normal AC tension of your mains power, but below the max input voltage of the HLK. so in Netherlands 250 volts will do.

                                        link text

                                        Moshe LivneM Offline
                                        Moshe LivneM Offline
                                        Moshe Livne
                                        Hero Member
                                        wrote on last edited by
                                        #132

                                        @Bertb that is actually a very good surface temp for overload from what I saw in the other tests. Very promising.

                                        1 Reply Last reply
                                        0
                                        • B Offline
                                          B Offline
                                          Bertb
                                          wrote on last edited by
                                          #133

                                          At 535 mA, the temperature stabilizes at 39.81c /F 103.66

                                          1 Reply Last reply
                                          0
                                          Reply
                                          • Reply as topic
                                          Log in to reply
                                          • Oldest to Newest
                                          • Newest to Oldest
                                          • Most Votes


                                          16

                                          Online

                                          11.7k

                                          Users

                                          11.2k

                                          Topics

                                          113.0k

                                          Posts


                                          Copyright 2019 TBD   |   Forum Guidelines   |   Privacy Policy   |   Terms of Service
                                          • Login

                                          • Don't have an account? Register

                                          • Login or register to search.
                                          • First post
                                            Last post
                                          0
                                          • MySensors
                                          • OpenHardware.io
                                          • Categories
                                          • Recent
                                          • Tags
                                          • Popular