  3. Help! feedback S_COVER status
9 Posts 2 Posters 1.4k Views 2 Watching
  • G
    G
    giva
    what is the correct way to send the commands ,...V_UP V_DOWN V_STOP ..., to controller (vera) ? Indicating the status Open ... closed etc
    MyMessage msg_S_COVER_U(CHILD_PORTAO_INT, V_UP);
    send(msg_S_COVER_U.set(V_UP)); ?
    send(msg_S_COVER_U.set("Up")); ?
    send(msg_S_COVER_U.set(Up)); ?
    send(msg_S_COVER_U.set(UP)); ?
    send(msg_S_COVER_U.set(1)); ?
    I ask this because my home app (homebridge-vera) do not update status . then i look for solution
    enum CoverState {
    STOP,
    UP, // Window covering. Up.
    DOWN, // Window covering. Down.
    static int coverState = STOP;
    MyMessage msgUP(CHILD_ID_COVER, V_UP);
    MyMessage msgDown(CHILD_ID_COVER, V_DOWN);
    MyMessage msgStop(CHILD_ID_COVER, V_STOP);
    MyMessage msgPercentage(CHILD_ID_COVER, V_PERCENTAGE);
    void sendState() {
    // Send current state and status to gateway.
    send(msgUP.set(coverState == UP));
    send(msgDown.set(coverState == DOWN));
    send(msgStop.set(coverState == STOP));
    send(msgPercentage.set(currentShutterLevel));
    skywatchS 1 Reply Last reply
    • G giva
      enum CoverState {
      STOP,
      void sendState() {
      skywatchS
      skywatchS
      skywatch
      @giva I think it should be the other way around.
      When I tried this I used V_UP,V_DOWN and V_STOP from the controller to the blind to tell it which way to move or to stop moving.
      I only sent V_PERCENTAGE back to the controller so that the controller knew where the blind was (allows to tell it to go to xx% of travel allowing any position to be set).
      G 1 Reply Last reply
      • skywatchS skywatch
        G
        G
        giva
        wrote on last edited by giva
        @skywatch Yes, you're right. however it only informs the opening percentage. I need to inform the iphone application the state (open close) so that the icon is in the correct position. What happens is that when I ask to open (by the crab) it opens as long as it is (the icon) in the closed position. and so as to close. only closes if icon is in open position!!
        G skywatchS 2 Replies Last reply
        • G giva
          G
          G
          giva
          @giva by the crab. Sorry Siri
          • G giva
            skywatchS
            skywatchS
            skywatch
            @giva said in Help! feedback S_COVER status:
            Then there is a problem in your code somewhere. I can't help as you didn't post the full code.
            I am not sure what 'the crab' is, but if I understand that you simply want the status of the cover to update in the controller as it opens/closes then again this is something you need to add to the code.
            How are you getting the percentage open/closed in the first place?
            • G
              G
              giva
              Sorry about my bad English
              • G
                G
                giva
                I wrote wrong. means "Siri" apple
                In Portuguese Siri is crab rsrs
                • G
                  G
                  giva
                  • G
                    G
                    giva
                    #define MY_GATEWAY_ESP8266
                    #define MY_NODE_ID                   9
                    #define MY_BAUD_RATE                 9600
                    #define MY_WIFI_SSID                 "xxxxx"
                    #define MY_WIFI_PASSWORD             "xxxxxxxxxxx"
                    #define MY_HOSTNAME                  "PortInt48"
                    #define SKETCH_NAME                  "PortInt48"
                    #define SKETCH_VERSION               "2.4"
                    #define SKETCH_NAME_PORT             "Portão Interno"
                    #define SKETCH_NAME_SENS_PORT_O      "Sensor Portão Aberto"
                    #define SKETCH_NAME_SENS_PORT_C      "Sensor Portão Fechado"
                    #define SKETCH_NAME_INFO             "Estado do Portão"
                    //#define SKETCH_NAME_BOTAO            "Botão Portão Ext"
                    #define MY_IP_ADDRESS                10,0,1,48
                    #define MY_IP_GATEWAY_ADDRESS        10,0,1,1
                    #define MY_IP_SUBNET_ADDRESS         255,255,255,0
                    #define MY_PORT                      5003
                    #define MY_GATEWAY_MAX_CLIENTS       3
                    //#define MY_INCLUSION_MODE_DURATION   60
                    //#define MY_INCLUSION_MODE_BUTTON_PIN 5 // D1
                    #ifndef UNIT_TEST
                    #include <Arduino.h>
                    #include <ESP8266WiFi.h>
                    #include <ArduinoOTA.h>
                    #include <NewPing.h>
                    #define CHILD_PORTAO_INT        1
                    #define CHILD_ID_SENSOR_A       2
                    #define CHILD_ID_SENSOR_TA      3
                    #define CHILD_ID_TEXT           4
                    #define RELE_PIN               13   //d7
                    #define ECHO_PIN               14   //d5
                    #define TRIGGER_PIN            12   //d6
                    #define CLOSED                  0
                    #define OPEN                    1
                    #define CLOSING                 2
                    #define OPENING                 3
                    #define MAX_DISTANCE            160
                    #define RELE_OFF                1
                    #define RELE_ON                 0
                    int reverso                    = 3000;
                    int lastDist                   = 0;
                    int AverageDist                = 0;
                    int cState                     = 0;
                    int lState                     = 0;
                    int lLimit                     = 0;
                    int Distx                      = 0;
                    int lDistx                     = 0;
                    int incomingBlindData          = 0;
                    int distmin                    = 13;
                    int distmax                    = 80;
                    int Level_FECHADO              = 2;
                    int Level_ABERTO               = 2;
                    int Level_CONTROLE             = 23 ;
                    int lastState                  = 0;
                    int lastposition               = 0;
                    int aberto                     = 0;
                    int abertototal                = 0;
                    boolean metric                 = true;
                    boolean obstruction            = false;
                    const char *currentState[]     = { "Fechado", "Aberto", "Fechando", "Abrindo" };
                    static int status              = 0; // 0=cover is down, 1=cover is up
                    static bool initial_state_sent = false;
                    unsigned long lastsend         = 0;
                    unsigned long lastsendx        = 0;
                    enum State {STOP, UP, DOWN,};
                    static int State               = STOP;
                    NewPing sonar(TRIGGER_PIN, ECHO_PIN, MAX_DISTANCE);
                    MyMessage msg_Porcent(CHILD_PORTAO_INT, V_PERCENTAGE);
                    MyMessage msg_S_COVER_D(CHILD_PORTAO_INT, V_DOWN);
                    MyMessage msg_S_COVER_S(CHILD_PORTAO_INT, V_STOP);
                    MyMessage msg_Aberto(CHILD_ID_SENSOR_A, V_TRIPPED);
                    MyMessage msg_Aberto_Total(CHILD_ID_SENSOR_TA, V_TRIPPED);
                    MyMessage msg_Text(CHILD_ID_TEXT, V_TEXT);
                      sendSketchInfo(SKETCH_NAME, SKETCH_VERSION); // Send the sketch version information to the gateway and Controller
                      present(CHILD_PORTAO_INT, S_COVER, SKETCH_NAME_PORT); // Register all sensors to gw (they will be created as child devices)
                      present(CHILD_ID_SENSOR_A, S_DOOR, SKETCH_NAME_SENS_PORT_O);
                      present(CHILD_ID_SENSOR_TA, S_DOOR, SKETCH_NAME_SENS_PORT_C);
                      present(CHILD_ID_TEXT, S_INFO, SKETCH_NAME_INFO );
                      pinMode(RELE_PIN, OUTPUT);
                      digitalWrite(RELE_PIN, RELE_OFF);
                      //-------------------OTA----------------
                      ArduinoOTA.setHostname(MY_HOSTNAME);
                      ArduinoOTA.onStart([]() {
                        Serial.println("ArduinoOTA start");
                      ArduinoOTA.onEnd([]() {
                        Serial.println("\nArduinoOTA end");
                      ArduinoOTA.onProgress([](unsigned int progress, unsigned int total) {
                        Serial.printf("OTA Progress: %u%%\r", (progress / (total / 100)));
                      ArduinoOTA.onError([](ota_error_t error) {
                        Serial.printf("Error[%u]: ", error);
                        if (error == OTA_AUTH_ERROR) {
                          Serial.println("Auth Failed");
                        } else if (error == OTA_BEGIN_ERROR) {
                          Serial.println("Begin Failed");
                        } else if (error == OTA_CONNECT_ERROR) {
                          Serial.println("Connect Failed");
                        } else if (error == OTA_RECEIVE_ERROR) {
                          Serial.println("Receive Failed");
                        } else if (error == OTA_END_ERROR) {
                          Serial.println("End Failed");
                      ArduinoOTA.begin();
                      ArduinoOTA.handle();
                      calcDistx();
                      getState();
                      if (initial_state_sent == false) {
                        sendState();
                        initial_state_sent = true;
                      if (millis() - lastsendx >= 20000) {
                        sendState();
                        lastsendx = millis();
                      if (lState != cState) {
                        if ( (cState == OPEN) || (cState == CLOSED) ) {
                          if (cState == OPEN) {
                            status = 1;
                            State = UP;
                            aberto = 1;
                            abertototal = 1;
                          else if (cState == CLOSED) {
                            status = 0;
                            State = DOWN;
                            aberto = 0;
                            abertototal = 0;
                        if (cState == CLOSING) {
                          status = 0;
                          State = STOP;
                          aberto = 1;
                          abertototal = 0;
                        else if (cState == OPENING) {
                          status = 0;
                          State = STOP;
                          aberto = 1;
                          abertototal = 0;
                          //send(msg_Porcent.set(Distx));
                        lState = cState;
                        sendState();
                      if ( digitalRead( RELE_PIN ) == 1) {
                        relayOff();
                    void relayOff() {
                      digitalWrite(RELE_PIN, RELE_OFF );
                    void getState() {
                      if (Distx >= distmax) {
                        cState = OPEN;
                      } else if (Distx <= distmin) {
                        cState = CLOSED;
                      } else if ((Distx < distmax) && (Distx > distmin)) {
                        if (lState == OPEN) {
                          cState = CLOSING;
                          cState = OPENING;
                      if (message.isAck()) {
                        return;
                      incomingBlindData = atoi(message.data);
                      if (message.sensor == CHILD_PORTAO_INT) {
                        calcDistx();
                        if ((message.type == V_UP ) && (cState == OPENING)) {
                          m_up();
                          wait(reverso);
                          m_up();
                          wait(reverso);
                          m_up();
                        else if ((message.type == V_UP ) && (cState == CLOSING)) {
                          m_up();
                        else if ((message.type == V_UP ) && (cState == CLOSED)) {
                          m_up();
                        else if ((message.type == V_UP ) && (cState == OPEN)) {
                        else if ((message.type == V_DOWN) && (cState == OPEN)) {
                          m_up();
                        else if ((message.type == V_DOWN) && (cState == CLOSED)) {
                        else if ((message.type == V_DOWN) && (cState == CLOSING)) {
                          m_up();
                          wait(reverso);
                          m_up();
                          wait(reverso);
                          m_up();
                        else if ((message.type == V_DOWN) && (cState == OPENING)) {
                          m_up();
                          wait(reverso);
                          m_up();
                        else if (message.type == V_STOP ) {
                          m_up();
                        else if ((incomingBlindData == 100) && (cState != OPEN)) {
                          lastposition = 100;
                          m_up();
                        else if ((incomingBlindData == 0) && (cState != CLOSED)) {
                          lastposition = 0;
                          m_up();
                         else if ((incomingBlindData > 0) && (incomingBlindData  < 100)) {
                            if ((cState == CLOSING) && (incomingBlindData > Distx))  {
                              m_up();
                              while (Distx >= incomingBlindData) {
                                calcDistx();
                              m_up();
                            else if ((cState == OPENING) && (incomingBlindData < Distx))  {
                              m_up();
                              while (Distx <= incomingBlindData) {
                                calcDistx();
                              m_up();
                            else if ((cState == OPENING) && (incomingBlindData > Distx))  {
                              m_up();
                              wait(reverso);
                              m_up();
                              wait(reverso);
                             // m_up();
                                calcDistx();
                              m_up();
                            else if ((cState == CLOSING) && (incomingBlindData < Distx))  {
                              m_up();
                              wait(reverso);
                              m_up();
                              wait(reverso);
                              //m_up();
                                calcDistx();
                              m_up();
                            else if ((cState == OPEN) && (incomingBlindData < Distx))  {
                              m_up();
                                calcDistx();
                              m_up();
                            else if ((cState == CLOSED) && (incomingBlindData > Distx))  {
                              m_up();
                                calcDistx();
                              m_up();
                        lastposition = incomingBlindData;
                        sendState(); // Update Vera with status of blinds (up/down)
                    void m_up() {
                      digitalWrite(RELE_PIN, RELE_ON); // Change relay state
                      wait(500);
                      exit;
                    void calcDistx() {
                      for (int i = 0; i < 10; ++i) {
                        AverageDist += metric ? sonar.ping_cm() : sonar.ping_in();;
                        wait(10);
                      AverageDist /= 10;
                      int dist = AverageDist;
                      // Serial.println("Ping: ");
                      Serial.print(dist); // Convert ping time to distance in cm and print result (0 = outside set distance range)
                      // Serial.println(metric ? " cm" : " in");
                      if (dist != lastDist) {
                        lastDist = dist;
                        int Disty = map(lastDist, distmin, distmax, 0, 100);
                        Distx = constrain(Disty, 0, 100);
                        //  Serial.print("Ping CONERTIDO: ");
                        // Serial.print(Distx); // Convert ping time to distance in cm and print result (0 = outside set distance range)
                    void sendState() {
                      send( msg_Text.set( currentState[cState] ) );
                      send(msg_S_COVER_U.set(State == UP));
                      send(msg_S_COVER_D.set(State == DOWN));
                      send(msg_S_COVER_S.set(State == STOP));
                      send(msg_Aberto.set(aberto));
                      send(msg_Aberto_Total.set(abertototal));
                    12.5k
