    Cliff Karlsson
    I have built the pulse power meter using the code on this page and it is working great, but when I look at the domoticz log it looks like the sensor is flooding the controller with values.
    General/kWh (Elförbrukning)
    2015-10-21 06:54:52.664 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:54:52.708 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:54:52.903 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:54:52.947 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:54:52.993 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:07.057 Hardware Monitor: Fetching data (System sensors)
    2015-10-21 06:55:12.648 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:12.694 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:12.738 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:12.933 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:12.977 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:13.023 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:32.680 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:32.725 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:32.768 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:32.964 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:33.008 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:33.053 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:37.196 Hardware Monitor: Fetching data (System sensors)
    2015-10-21 06:55:52.710 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:52.756 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:52.801 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:52.995 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:53.039 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:55:53.085 (Mysensors.org) General/kWh (Elförbrukning)
    2015-10-21 06:56:07.427 Hardware Monitor: Fetching data (System sensors)
    What is the cause of this problem?
    Y 1 Reply Last reply
    • S Offline
      Strange. I have the same setup and it works. What did you set the sleep time to in the sketch ? I'm changed to 15 minutes.
        Y Offline
        Y Offline
        What sensor are you using to count the pulses? The signal might need denouncing...
          Cliff Karlsson
          I am using the same sensor as in the build example, the biggest sensor.
          • S Offline
            And the code is unchanged from the website?
              Cliff Karlsson
              Damn, I removed the sensor and re-uploaded the original sketch and now I get the same error as I struggled with for several days. I get no values from the sensor and it is reported 3 times after every power-cycle.
              2015-10-21 18:06:21.225 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:06:51.365 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:07:21.504 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:07:51.643 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:08:15.844 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:08:15.889 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:08:15.935 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:08:15.984 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:08:16.028 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:08:16.071 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:08:21.782 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:08:51.250 Incoming connection from: 192.168.0.24
              2015-10-21 18:08:52.000 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:09:22.271 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:09:52.490 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:10:22.632 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:10:52.787 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:11:22.930 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:11:34.322 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:11:34.366 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:11:34.411 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:11:34.460 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:11:34.504 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:11:34.547 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:11:53.069 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:12:23.208 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:12:47.029 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:12:47.073 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:12:47.119 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:12:47.168 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:12:47.212 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:12:47.255 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:12:53.347 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:13:23.486 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:13:53.628 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:14:23.768 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:14:53.908 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:15:24.049 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:15:54.187 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:16:15.120 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:16:15.164 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:16:15.209 MySensors: Node: 7, Sketch Name: Energy Meter
              2015-10-21 18:16:15.258 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:16:15.302 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:16:15.345 MySensors: Node: 7, Sketch Version: 1.0
              2015-10-21 18:16:24.331 Hardware Monitor: Fetching data (System sensors)
              2015-10-21 18:16:54.475 Hardware Monitor: Fetching data (System sensors)
              And this is the code, I have only added the RFM69 stuff:
               * Version 1.0 - Henrik EKblad
               * This sketch provides an example how to implement a distance sensor using HC-SR04
               * Use this sensor to measure KWH and Watt of your house meeter
               * You need to set the correct pulsefactor of your meeter (blinks per KWH).
               * The sensor starts by fetching current KWH value from gateway.
               * Reports both KWH and Watt back to gateway.
               * Unfortunately millis() won't increment when the Arduino is in
               * sleepmode. So we cannot make this sensor sleep if we also want
               * to calculate/report watt-number.
               * http://www.mysensors.org/build/pulse_power
              #include <MyTransportRFM69.h>
              #define DIGITAL_INPUT_SENSOR 3  // The digital input you attached your light sensor.  (Only 2 and 3 generates interrupt!)
              #define SLEEP_MODE false        // Watt-value can only be reported when sleep mode is false.
              unsigned long SEND_FREQUENCY = 30000; // Minimum time between send (in milliseconds). We don't wnat to spam the gateway.
              MyTransportRFM69 transport(RFM69_FREQUENCY, RFM69_NETWORKID, RF69_SPI_CS, RF69_IRQ_PIN, false, RF69_IRQ_NUM);
              MySensor gw(transport);
              double ppwh = ((double)PULSE_FACTOR)/1000; // Pulses per watt hour
              boolean pcReceived = false;
              unsigned long oldPulseCount = 0;
              unsigned long oldWatt = 0;
              double oldKwh;
              unsigned long lastSend;
              MyMessage wattMsg(CHILD_ID,V_WATT);
              MyMessage kwhMsg(CHILD_ID,V_KWH);
              MyMessage pcMsg(CHILD_ID,V_VAR1);
                gw.begin(incomingMessage);
                gw.sendSketchInfo("Energy Meter", "1.0");
                gw.present(CHILD_ID, S_POWER);
                gw.request(CHILD_ID, V_VAR1);
                attachInterrupt(INTERRUPT, onPulse, RISING);
                lastSend=millis();
                unsigned long now = millis();
                if (pcReceived && (SLEEP_MODE || sendTime)) {
                  if (!SLEEP_MODE && watt != oldWatt) {
                    if (watt<((unsigned long)MAX_WATT)) {
                      gw.send(wattMsg.set(watt));  // Send watt value to gw
                    Serial.print("Watt:");
                    Serial.println(watt);
                    oldWatt = watt;
                  // Pulse cout has changed
                  if (pulseCount != oldPulseCount) {
                    gw.send(pcMsg.set(pulseCount));  // Send pulse count value to gw
                    double kwh = ((double)pulseCount/((double)PULSE_FACTOR));
                    oldPulseCount = pulseCount;
                    if (kwh != oldKwh) {
                      gw.send(kwhMsg.set(kwh, 4));  // Send kwh value to gw
                      oldKwh = kwh;
                  lastSend = now;
                } else if (sendTime && !pcReceived) {
                  // No count received. Try requesting it again
                  lastSend=now;
                if (SLEEP_MODE) {
                  gw.sleep(SEND_FREQUENCY);
                if (message.type==V_VAR1) {
                  pulseCount = oldPulseCount = message.getLong();
                  Serial.print("Received last pulse count from gw:");
                  Serial.println(pulseCount);
                  pcReceived = true;
              void onPulse()
                if (!SLEEP_MODE) {
                  unsigned long interval = newBlink-lastBlink;
                  if (interval<10000L) { // Sometimes we get interrupt on RISING
                    return;
                  watt = (3600000000.0 /interval) / ppwh;
                  lastBlink = newBlink;
                pulseCount++;
              • S Offline
                I cant see anything strange with the code - but i dont know that RFM69 stuff... the code should not send presentation three times, so can it be something with your radio?
                  Cliff Karlsson
                  Ahhh, got it to work again finally. I straightened the curled RFM69 antenna in desperation and moved it around in the room where I have the meeter. Could it be interference as I got alot of cables and electric stuff around the sensor and also a big ass thick pipe that is placed right next to the sensor and is located between the sensor and gateway?
                  Now I get this instead:
                  2015-10-21 18:53:05.095 MySensors: Node: 7, Sketch Name: Energy Meter
                  2015-10-21 18:53:05.108 MySensors: Node: 7, Sketch Version: 1.0
                  2015-10-21 18:53:05.723 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:53:35.192 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:53:35.221 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:53:35.944 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:54:05.239 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:54:05.267 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:54:06.085 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:54:35.284 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:54:35.313 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:54:36.228 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:55:05.330 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:55:05.362 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:55:06.378 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:55:35.375 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:55:35.403 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:55:36.519 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:56:05.435 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:56:06.658 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:56:35.466 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:56:35.494 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:56:36.797 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:57:05.526 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:57:06.938 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:57:35.557 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:57:35.585 (Mysensors.org) General/kWh (Meter)
                  2015-10-21 18:57:37.079 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:58:05.618 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 18:58:07.220 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:58:35.648 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 18:58:35.676 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 18:58:37.364 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:59:05.694 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 18:59:05.722 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 18:59:07.504 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 18:59:35.739 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 18:59:35.767 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 18:59:37.646 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 19:00:05.784 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 19:00:05.812 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 19:00:07.787 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 19:00:35.830 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 19:00:35.858 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 19:00:37.927 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 19:01:05.875 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 19:01:05.903 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 19:01:08.163 Hardware Monitor: Fetching data (System sensors)
                  2015-10-21 19:01:35.934 (Mysensors.org) General/kWh (Elmätare)
                  2015-10-21 19:01:38.305 Hardware Monitor: Fetching data (System sensors)
                  The most of the time the sensor sends twice every time, could it still be the pipe or other things that bounches the signal? Or would the pipe not affect the radio in that way.
                    Y Offline
                    Y Offline
                    And by 'biggest sensor' you mean the 'LM393 Light Sensor' ?
                    I use a comparable sensor (same pcb) with a LDR and had to debounce its readings or multiple pulses were detected on each blink.
                    Anyway, from the sketch I see sensor values should only be sent every 30 seconds, so that can't cause you gateway-spamming issue.
                    The sketch will try to receive the old absolute counter value on startup, so it can continue counting where it left off:
                    IKf it doesn't get an answer, it will retry forever:
                        lastSend=now;
                    Could it be that that mechanism is bugging you?
                    You could also connect to the sensor's serial port an see what it has to tell you.