  3. Domoticz
  4. Domoticz data timeout
24 Posts 5 Posters 10.3k Views 5 Watching
  • sundberg84S sundberg84
    @gbuico - it would be best to have this integrated into Domoticz. In the same time if Domoticz went down you had the same issue? Wouldnt it be the best to create a external node with an UPS that pings Domoticz and the gateway and alerts with a test/sms if it went down?
    gbuicoG
    gbuicoG
    gbuico
    @sundberg84 , in the architecture I have in mind for real operations the Raspberry with the main instance of Domoticz will be under UPS, so in my tests I'm assuming that it will be always on.
    Probably I may use a small databank between the plug and NodeMCU, so this should protect me against a normal power loss.
    Still... the protection with the databank is certainly weaker than a real UPS and this is the reason why I'm doing.
    Anyway... wherever you place a monitoring system you have only two solutions:
    1. data timeout disabled - with this setting, when the nodeMCU restarts then remains waiting for long time... may be hours.. because Domoticz doesn't answer to the initialization protocol.
    2. data timeout enabled - in this case Domoticz would surely restart the communication after the defined timeout... but would also disconnect and reconnect with the same frequency if there is no change in the sensor status.
    The second solution, at least, does not interrupts the overall functionality... but let me say it... this is a severe design error in Domoticz if this is the way it is expected to work.
    In the meanwhile... I went through all the presentation and the overall documentation of "Home Assistant" and, unless someone will dis encourage me from doing it, tonight I'll give it a try
    • gbuicoG gbuico
      @gbuico for Domoticz, I have the following cron job to restart in case Domoticz dies:
      /3  *  *   *   *     /usr/sbin/service domoticz status || /usr/sbin/service domoticz restart
      • gbuicoG
        gbuicoG
        gbuico
        Never heard of cron jobs before... you never stop learning :)
        Still, from what I understand this restart is triggered when Domoticz dies... not when a node has lost contact.
        Btw.. The Home Assistant installation is in progress on another SD card.
        If you care, the reason why it attracted me is because it seems to have full support for Piface Digital 2, RFLink and MySensors. Second, the documentation seems really well done. A small minus, 32G SD card is recommended... which is big... still I'm currently installing on a 8G card I had available in the house...
        Will let you know
        gbuicoG 1 Reply Last reply
        • K
          K
          kimot
          Sorry but I think using pure NodeMCU with Domoticz ( without other MySensors nodes connected ) like MySensors gateway is "masochistic".
          I suggest something like ESPeasy for this situation. If it supports your sensors types, you get more communication "freedom" then.
          • gbuicoG gbuico
            Will let you know
            gbuicoG
            gbuicoG
            gbuico
            wrote on last edited by gbuico
            @mfalkvidd , after a full day of work, trying to implement my configuration on Home Assistant, OpenHAB and Jeedom, I'm back here with a low tail and ready to go back to Domoticz.
            Without going in details, each of the above failed implementing either the RFLink or Piface Hardware. None of them seemed to provide a "logical" user interface like Domoticz.
            So... here I am... with one day totally lost and trying to recover.
            What I want to do now is to define a fake sensor in NodeMCU that will send a change within the data timeout.
            May I kindly ask you if you have a working sketch using the tmr function as I can't manage to compile a proper one (tmr not defined)
            Thanks in advance
            • gbuicoG gbuico
              Thanks in advance
              @gbuico I have never needed something like that, so I don't have any code.
              But I took some code from the motion sensor example and came up with this:
              // Initialize motion message
              	present(CHILD_ID, S_MOTION);
              bool tripped = false;
               tripped = !tripped;
                  wait(20000);
              Sorry for the formatting, currently using mobile.
              • gbuicoG gbuico
                @mfalkvidd , to tell you the truth I was fearing that the answer would have been this one.
                I should bettere say "these ones" because in the post you mentioned I also found confirmation to a doubt I started to have since some time.... should I continue with Domoticz or not
                As I said in my introduction I have close to 50 years of IT experience and I loved that project because you get started very quickly... but... if you are someone who likes "architectures"... it's a death.
                Plus, you may see yourself, I posted several times in the forum and I almost never received even a comment.
                I also saw in the other topic that you were close to the idea to jump to another controller... did you do it??? I gave a quick look to OpenHAB and found it far away from my mentality.. I've not tried anything else and would love to hear other experiences...
                Back to the specific issue, I was thinking to force a status update before the data timeout expires.. but I see it's not working if the status is unchanged.
                Even if it won't change anything, let me comment that to an "architecture fanatic"as I am, this behavior is just unacceptable. You may decide not to process a device event if there is no change, but you cannot say that you have not received anything from the corresponding hardware because this is just a lie.
                Whatever... even if I'm getting tired to survive with patches for the deficiencies of Domoticz, the quick and dirty solution right now seems to implement a fake sensor which changes its status with a proper frequency.
                I'm just having troubles to use the tmr.now() in my sketch because the compiler tells me "tmr" is not defined... will see how to solve.
                In the meanwhile, advices from you and whomever has experience with other controllers with a better design and a better integration with MySensors it's highly appreciated.
                P.S. Another reason why I kept going with Domoticz is that I'm using an RFLink 433 radio interface (nano shop) and I couldn't find another controller supporting this piece of hardware
                K
                K
                kimot
                tmr.now() is NodeMCU LUA function, not MySensors or Arduino.
                NodeMCU
                • K kimot
                  NodeMCU
                  gbuicoG
                  gbuicoG
                  gbuico
                  @kimot , sure, I know that tmr.now() is a NodeMCU function and I'm trying to use it in the "void loop()" sketch of my NodeMCU to send a "changed status" at regular interval.
                  Unfortunately I'm still getting compile errors as if the function has to be declared or requires an "include".
                  Back to your post above where you mention ESPEasy... I don't know this alternative, but from what I'm reading is just a sketch that you produce with a specific tool instead of using Arduino IDE software, so I cannot see how this can be better or easier compared to Mysensors since the "dumb side" seems to be in Domoticz.
                  Still since you know both, I'm sure that you have a good reason... so, may I ask you to spend a couple of words more to explain why you think this can make things simpler? Thanks a lot
                  K 1 Reply Last reply
                  • gbuicoG gbuico
                    K
                    K
                    kimot
                    wrote on last edited by kimot
                    @gbuico
                    tmr.now() is LUA function
                    NodeMCU LUA is firmware, which you load to your NodeMCU ( or other ESP2866 ) and then write your programs in LUA scripts, which stores in ESP2866.
                    MySensors is writen In Ardfuino language ( C++ ), so Arduino IDE compile your program and load it to ESP2866. And there is not tmr.now(). Use millis() instead off.
                    ESPeasy is firemware to load to ESP2866.
                    It runs on ESP2866 and you can create sensors and write simple "program" when connected to ESP webpage.
                    There are any timeouts, you can send message one per day or month, no problem.
                    You do not need compile ESPeasy itself. Use compiled file and download it to your ESP2866.
                    First you create your sensors in Domoticz as "Dummy" devices and remembers their "idx".
                    Then connect with browser to your sensor with ESPeasy running and through its webpage you can define different sensors ( sensor type, GPIO where connected, its domoticz idx , sending interval, etc )
                    For example, for DS18b20 you select pin for 1-wire bus, then you can see all sensors on this bus and select which you need. Temperature is automatically send to Domoticz.
                    Different sensor - no problem, select for example pins for i2c bus, discover this bus and then select sensor.
                    Display - select i2c address and it is done.
                    But what I really love on ESPeasy is its communication model.
                    If you cannot send some info through ESPeasy autmatically, you can write json command and send to Domotic whateverelse.
                    Need send data from Domoticz to your ESPeasy - no problem.
                    You can send commands from Domoticz with parameters and receive it in ESPeasy.
                    You can transfer everything this way.
                    No compilation, only write in your browser and hit "Apply" button.
                    I like MySensors very much, but for wi-fi connected single sensors exists easier ways.
                    But my dream is feature for MySensor ethernet gateway, when I can send to gateway something like this:
                    http://gatewayip/control?cmd=23;5;24.5
                    which means = to_node, sensor_id, value.
                    Or opposite way, send from sensor to gateway command with domoticz sensor idx, type of domoticz value (svalue or nvalue ) and value itself and gateway will send to domoticz appropriate json command.
                    • gbuicoG
                      gbuicoG
                      gbuico
                      @kimot , I have to confess that I'm still a bit lost when I have to understand which language I'm using in each environment, but this is because I keep jumping from something to something else. Your explanation was very clear and allowed me to solve the "timing problem" if a few minutes.
                      At the same time... you gave me enough reason to test ESPeasy... and to say it all I have already installed another NodeMCU on the breadboard and starting right now to play :)
                      Thanks again
                      • gbuicoG gbuico
                        Thanks again
                        K
                        K
                        kimot
                        @gbuico
                        Ok.
                        Only do not forget, that ESPeasy webpage is mainly for setting, so it is not refreshed automatically like Domoticz. You must manually refresh it when check, if sensor value changed, for example.
                        video
                        • K kimot
                          @gbuico
                          Ok.
                          video
                          gbuicoG
                          gbuicoG
                          gbuico
                          My tests with ESPeasy stopped before beginning because I realized that I need a USB to TTL converter that I don't have a t moment... Delayed...
                          This gave me time to implement the change in NodeMCU sketch which addresses and solves the original problem of this topic.
                          I'm attaching here the second part of the modified sketch omitting the WiFi part.
                          In short, I defined a fake "switch" sensor in NodeMCU and I'm sending its modified status to Domoticz every 45 seconds (data timeout in Domoticz is 1 minute).
                          Important to underline that the new "fake sensor" can remain in the list of "not used" devices in Domoticz.
                          Here is the code:
                          // Start of the sensor specific code
                          #include <pins_arduino.h>
                          #define CHILD_ID0 0
                          #define CHILD_ID1 1
                          #define CHILD_ID2 2
                          Bounce debouncer1 = Bounce();
                          Bounce debouncer2 = Bounce();
                          int oldValue1=-1;
                          int oldValue2=-1;
                          int tempo=millis();
                          int ultimo=0;
                          MyMessage msg1(CHILD_ID0, V_TRIPPED);
                          MyMessage msg2(CHILD_ID1, V_TRIPPED);
                          MyMessage msg3(CHILD_ID2, V_TRIPPED);
                            // Setup magnetic contact on D0 with pull-up
                            pinMode(D0,INPUT_PULLUP);
                            // After setting up reed switch, setup debouncer
                            debouncer1.attach(D0);
                            debouncer1.interval(5);
                            // Setup magnetic contact on D1 with pull-up
                            pinMode(D1,INPUT_PULLUP);
                            debouncer2.attach(D1);
                            debouncer2.interval(5);
                          	present(CHILD_ID0, S_DOOR);
                            present(CHILD_ID1, S_DOOR);
                            present(CHILD_ID2, S_DOOR);
                            debouncer1.update();
                            debouncer2.update();
                            // Get the update value
                            int value1 = debouncer1.read();
                            if (millis() > tempo + 45000)
                               Serial.print (millis());
                               Serial.print (ultimo);
                               tempo = millis();
                               send(msg3.set(ultimo));
                               ultimo = ultimo + 1;
                               if (ultimo > 1)
                                  ultimo = 0;
                            if (value1 != oldValue1)
                               // Send in the new value
                               send(msg1.set(value1==HIGH ? 1 : 0));
                               oldValue1 = value1;
                            if (value2 != oldValue2)
                               send(msg2.set(value2==HIGH ? 1 : 0));
                               oldValue2 = value2;
                          • gbuicoG
                            gbuicoG
                            gbuico
                            Domoticz log changed from this:
                            2018-01-05 14:19:04.819 MySensors: Gateway Ready...
                            2018-01-05 14:19:05.820 MySensors: Gateway Version: 2.1.1
                            2018-01-05 14:20:00.270 dzVents: Debug: Dumping domoticz data to /home/pi/domoticz/scripts/dzVents//domoticzData.lua
                            2018-01-05 14:20:00.293 dzVents: Debug: Event trigger type: time
                            2018-01-05 14:20:30.855 Error: MySensors1 hardware (7) nothing received for more than 1 Minute!....
                            2018-01-05 14:20:31.856 Error: Restarting: MySensors1
                            2018-01-05 14:20:32.829 MySensors: TCP/IP Worker stopped...
                            2018-01-05 14:20:33.831 MySensors: trying to connect to: 192.168.1.7:5003
                            2018-01-05 14:20:34.831 MySensors: connected to: 192.168.1.7:5003
                            2018-01-05 14:20:34.831 MySensors: Gateway Ready...
                            2018-01-05 14:20:35.832 MySensors: Gateway Version: 2.1.1
                            2018-01-05 14:21:00.379 dzVents: Debug: Dumping domoticz data to /home/pi/domoticz/scripts/dzVents//domoticzData.lua
                            2018-01-05 14:21:00.402 dzVents: Debug: Event trigger type: time
                            2018-01-05 14:22:00.486 dzVents: Debug: Dumping domoticz data to /home/pi/domoticz/scripts/dzVents//domoticzData.lua
                            2018-01-05 14:22:00.510 dzVents: Debug: Event trigger type: time
                            2018-01-05 14:22:00.846 Error: MySensors1 hardware (7) nothing received for more than 1 Minute!....
                            2018-01-05 14:22:01.847 Error: Restarting: MySensors1
                            2018-01-05 14:22:02.841 MySensors: TCP/IP Worker stopped...
                            2018-01-05 14:22:03.842 MySensors: trying to connect to: 192.168.1.7:5003
                            2018-01-05 14:22:04.843 MySensors: connected to: 192.168.1.7:5003
                            To this:
                            2018-01-05 14:55:00.413 dzVents: Debug: Dumping domoticz data to /home/pi/domoticz/scripts/dzVents//domoticzData.lua
                            2018-01-05 14:55:00.436 dzVents: Debug: Event trigger type: time
                            2018-01-05 14:55:35.108 (MySensors1) Light/Switch (Security Sensor)
                            2018-01-05 14:56:00.520 dzVents: Debug: Dumping domoticz data to /home/pi/domoticz/scripts/dzVents//domoticzData.lua
                            2018-01-05 14:56:00.543 dzVents: Debug: Event trigger type: time
                            2018-01-05 14:56:20.113 (MySensors1) Light/Switch (Security Sensor)
                            2018-01-05 14:57:00.127 dzVents: Debug: Dumping domoticz data to /home/pi/domoticz/scripts/dzVents//domoticzData.lua
                            2018-01-05 14:57:00.151 dzVents: Debug: Event trigger type: time
                            2018-01-05 14:57:05.120 (MySensors1) Light/Switch (Security Sensor)
                            2018-01-05 14:57:50.124 (MySensors1) Light/Switch (Security Sensor)
                            2018-01-05 14:58:00.235 dzVents: Debug: Dumping domoticz data to /home/pi/domoticz/scripts/dzVents//domoticzData.lua
                            2018-01-05 14:58:00.259 dzVents: Debug: Event trigger type: time
                            2018-01-05 14:58:35.129 (MySensors1) Light/Switch (Security Sensor)
                            2018-01-05 14:59:00.344 dzVents: Debug: Dumping domoticz data to /home/pi/domoticz/scripts/dzVents//domoticzData.lua
                            2018-01-05 14:59:00.367 dzVents: Debug: Event trigger type: time
                            2018-01-05 14:59:20.134 (MySensors1) Light/Switch (Security Sensor)
                            • gbuicoG gbuico
                              Here is the code:
                              #define CHILD_ID0 0
                              #define CHILD_ID1 1
                              #define CHILD_ID2 2
                              int oldValue1=-1;
                              int oldValue2=-1;
                              int tempo=millis();
                              int ultimo=0;
                                   tempo = millis();
                                   if (ultimo > 1)
                                      ultimo = 0;
                                   oldValue1 = value1;
                                   oldValue2 = value2;
                              K
                              K
                              kimot
                              @gbuico
                              "and to say it all I have already installed another NodeMCU on the breadboard and starting right now to play"
                              "My tests with ESPeasy stopped before beginning because I realized that I need a USB to TTL converter that I don't have a t moment... Delayed..."
                              NodeMCU is with USB to TTL converter onboard.
                              Or how you programme it now?
                              • P
                                P
                                pjr
                                wrote on last edited by pjr
                                I think with domoticz its might be enough to call sendHeartbeat() from your gateway every 30 seconds.
                                It should update the m_LastHeartbeatReceive of the HW and thats what mainworker uses when it defines if the HW should be "rebooted".
                                Here is a example(NOT TESTED):
                                #define HEARTBEAT_SEND_FREQUENCY 30000
                                unsigned long lastHeartBeatSend;
                                  lastHeartBeatSend  = 0;
                                  unsigned long now = millis();
                                  if(now - lastHeartBeatSend > HEARTBEAT_SEND_FREQUENCY)
                                    sendHeartbeat();
                                    lastHeartBeatSend = now;
                                See:
                                https://github.com/domoticz/domoticz/blob/8bb0420c3ba4a10bbacd6f2e2f9b40b06ff0c7ac/main/mainworker.cpp#L12864
                                https://github.com/domoticz/domoticz/blob/8bb0420c3ba4a10bbacd6f2e2f9b40b06ff0c7ac/hardware/MySensorsBase.cpp#L487
                                https://www.mysensors.org/download/sensor_api_20
                                • gbuicoG
                                  gbuicoG
                                  gbuico
                                  @kimot , right now I'm using the Arduino IDE application which allows me to upload to NodeMCU just using the USB cable.
                                  Reading the ESPeasy documentation I understand that this type of connection is not an option and you must have a USB to TTL interface.
                                  I'd be very happy to hear that I don't need it... otherwise I'm going to get one on monday...
                                  • P pjr
                                        sendHeartbeat();
                                    See:
                                    gbuicoG
                                    gbuicoG
                                    gbuico
                                    @pjr , what you are suggesting is exactly what I wanted at the beginning..... but... my understanding from the first answer I got and for this https://www.domoticz.com/forum/viewtopic.php?f=42&t=9775&sid=1fea4af7b12f84f656ca4aa825eb6115
                                    is that the sendHeartbeat() function is basically accepted but disregarded in Domoticz, meaning, would not create problems but not fixing the issues.
                                    Of course this is my understanding and would be glad to have additional opinions/tests
                                    • P
                                      P
                                      pjr
                                      #22
                                      @gbuico That thread is pretty old.
                                      The current(and most likely working) functionality is implemented here:
                                      https://github.com/domoticz/domoticz/commit/2d4e690c82b166ff8597a7deb44be17f3ad2560f#diff-a9f78798ba1bded6b56b3909b2a42848
                                      • gbuicoG
                                        gbuicoG
                                        gbuico
                                        @pjr, thanks for your update. I went to check the solution proposed in the link you attached... and let me confess... got the concept, but it's complexity is currently not something at my reach.
                                        Meaning.. as my solution is very small and working, for the time been I'll stick to it and spend my time for further function implementation.
                                        My only worry... your example was just a few lines... understandable... how did they end up with 1700 lines of code or this?
                                        Whatever.. I'l go back to it when I have some more time as I prefer an official implementation to a patch like mine...
                                        • gbuicoG gbuico
                                          K
                                          K
                                          kimot
                                          #24
                                          @gbuico
                                          USB to TTL serial is on board on NodeMCU and Wemos.
                                          Download
                                          ESPEasy mega dev.13
                                          Upload to your NodeMCU using "FlashESP8266.exe" from .zip
                                          Upload to NodeMCU
                                          Use "....._normal_4096.bin" file
                                          Power off - on !!! your NodeMCU ( reconnect USB cable )
                                          Make basic setup:
                                          With smart phone or notebook connect to your NodeMCU, which works like wifi acces point now ( name like "ESP_Easy_0" )
                                          If password required - "configesp"
                                          Type in browser address 192.168.4.1
                                          wifi setup
                                          Set your home wifi access info in config page.
                                          You will see actual IP your NodeMCU in your wifi network.
                                          Connect to this IP and make basic setup.
                                          ( you can set Fixed IP, IP of your Domoticz, etc )
                                          ESPEasy setup