I wonder what would happen for a Relay Actuator (as shown among the examples) if the communication with the controller is lost. Then the outputs may be active forever.
So, I believe an actuator like this should not be trusted to activate anything critical (heaters, pumps etc.) unless I add functionality to turn off the output in case of communication timeout. I guess I can not count on existing controllers to keep sending regular updates to the output state, so I don't know how I could even detect communcation timeout. What do you recommend?
-
I wonder what would happen for a Relay Actuator (as shown among the examples) if the communication with the controller is lost. Then the outputs may be active forever.
So, I believe an actuator like this should not be trusted to activate anything critical (heaters, pumps etc.) unless I add functionality to turn off the output in case of communication timeout. I guess I can not count on existing controllers to keep sending regular updates to the output state, so I don't know how I could even detect communcation timeout. What do you recommend?
@lassenie I agree. If the relay is controlling something critical the node should have as much as possible of:
- Turn relay off if power is lost (relay should default to shut off if it has no signal/power)
- Default relay to off when starting after power loss / reset
- Use watchdog to reset the node if the sketch hangs
- Use a timer to turn relay off after some appropriate interval if no signal is received from the controller
- Add a hardware watchdog, like discussed here
-
@lassenie I agree. If the relay is controlling something critical the node should have as much as possible of:
- Turn relay off if power is lost (relay should default to shut off if it has no signal/power)
- Default relay to off when starting after power loss / reset
- Use watchdog to reset the node if the sketch hangs
- Use a timer to turn relay off after some appropriate interval if no signal is received from the controller
- Add a hardware watchdog, like discussed here
@mfalkvidd Thank you for your valuable suggestions - they all look very relevant.
Perhaps I am overlooking something in the documentation, but I wonder if any existing controllers out there will get the node's relay outputs in the right state again after a node restart, if it always starts up in off state.
Besides that, how can I reliably detect communication in the node, such as I_HEARTBEAT/I_HEARTBEAT_RESPONSE? As far as I know, such internal messages do not arrive through the recieve(...) API function. I will need to see some incoming messages (also from existing controller implementations) - otherwise I would get timeouts.
Best regards
Lasse
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.