  3. How to read frequency and SWP output from watermark sensor
arduinowatermarkfrequencymoisturepulse
36 Posts 4 Posters 9.4k Views 5 Watching
  • P
    P
    pierrot10
    @hard-shovel
    Hello,it's verry interresting what you shared.
    Today I left the SMX input open. No sensor no resistance. I discovered, I get the same value when the sensor is in a fully dried soil. And I did not have the sensor with me.
    Yes, I have a box that I fill up with soil of the crop where the sensors will be for the measurement.
    We only want to monitor the soil moiture from June to Septembre and the result will be display in a graph.
    Some week ago, I wrote a loop to simulate the watermark voltage. In your second table you show that KPA can be from -332 to -1300 and then immediately to a positif number. That difference make me souspicious. I am still souspicous when I look from 48Hz to 157Hz (the doc give a range of frequency from 48Hz to 13233Hz.)
    But at the final, as I understood, what is relevant is from 1220Hz to +/- 310hz (from 550Ohm to 27950). From 27950 and above, the soil is fully dry, whatever if the kPa goes to -1300 or -352. And from 550Ohm or below, the soil is fully wet.
    H 1 Reply Last reply
    • P pierrot10
      @hard-shovel
      H
      H
      hard-shovel
      @pierrot10
      Yes i think that is correct 550 Ohm to 27950 Ohms is the range for the watermark sensor.
      For the SMX module with input open no sensor should be 48Hz as you have already discovered, and if you short the input terminals out you should get 13233Hz so total range of the module is more than the sensor.
      P 1 Reply Last reply
      • H hard-shovel
        @pierrot10
        P
        P
        pierrot10
        @hard-shovel
        I think, now it's clearer for me.
        First, SMX module has a range from 48hz to 13233hz
        But the watermak sensor has a range from 550 to 27950 ohm
        As we use watermark to measure the soil mostire, wehave to consier the range of 550 to 27950 which match with 6700Hz (more or less) and 310Hz. What is below or above is not relevant for moisture measurement with Wathermark.
        Are you agree with me?
        • P pierrot10
          @hard-shovel
          H
          H
          hard-shovel
          wrote on last edited by hard-shovel
          #24
          @pierrot10
          Yes I do agree that is how i understand the operation from the data sheet.
          if your still concerned about the possibility of negative results you could add something like either of the following
          Frequency = constrain(Frequency, 48, 133233);
          or
          Resistance = constrain(Resistance, 500, 27950);
          My main concern in the long term would be the sensor connections being corroded and the sensor resistance becoming open. So error checking for higher or lower than normal values for sensor fault conditions might be worthwhile.
          • P
            P
            pierrot10
            wrote on last edited by pierrot10
            #25
            Dear hard-shovel,
            I do not know if you are still around and if you can help me a bit.
            I actually put into the soil a watermark at 20cm. I add some water to see the watermark measurement and I used your proposition (code)
            I can not understand why I have a WRm of 518 and it retrun me a 200kPa It should be 0
            Getting WM1 (SMX):
            Frequency at 15: 6896Hz WRM: 518
            WRM: 518
            WRMc: 518
            SWP: 200
            Here si the code:
            Note: sw.something. The sw is beacuse I use Seesaw Seesaw borad from Adafruit to have more DIO
            // getting the swp.
            // wm1_power_pin is pin which ppower smx
            // wm1_power_pin is the pin read the value
            // val is the return value
            get_wmsmx(wm1_power_pin, wm1_read_pin, 1000000, val, true);
            mesMesures[c_wm1][capteur_wm1_id].valeur = val; // The final SWP is store here
            Dont pain attention at 'alternative'. It's alway true and I will clean the code.
            void get_wmsmx(int powerPin, int pinRead, unsigned long timeout, int16_t &val, bool alternative)
                sw.digitalWrite(powerPin, HIGH);
                delay(1000); // Need to have the sensor "in equilibre" with the soil.
                int highInput, lowInput;             // Store high and low time of wave in microseconds
                float totalInput;                     // Temp store of total time of duration for one cycle of high and low pulse
                float frequency;                      // calculated freqency   1/total time of one cycle.
                int16_t swp;
                int percent=0;
                int32_t wrm;
                //float Tsoil=24; //temp
                highInput = pulseIn(pinRead,HIGH);
                lowInput  = pulseIn(pinRead,LOW);
                totalInput = highInput + lowInput;
                frequency = 1000000 / totalInput;
                if (highInput >0 && lowInput>0)
                  Si.sprint(F("Frequency at "),2); Si.sprint(pinRead,2); Si.sprint(F(": "),2); Si.sprint((int16_t)frequency,2); Si.sprint(F("Hz "),2);
                else
                  Si.sprint(F("frequency: "),2);
                  Si.sprintln(F("Error"),2);
                delay(500);
                sw.digitalWrite(powerPin, LOW);
                int16_t Tsoil = mesMesures[c_temperature_soil][capteur_temperature_soil_id].valeur;
                if(alternative == false)
            // That is my old code. I will remove it
                  wrm = map(frequency,48,13233,27950,550); // Must control the frequency for 440 and 27950
                  Si.sprint(F("WRM: "),2); Si.sprint(wrm,2); Si.sprintln(F(" Ohm"),2);
                  Si.sprintln(F("Calculate SWP"),2);
                  //kPa = (3.213 * kohms + 4.093) / (1 - 0.009733 * kohms - 0.01205 * Celsius)
                  swp = (int16_t)(3.213 * (wrm/1000) + 4.093) / (1 - 0.009733 * (wrm/1000) - 0.01205 * Tsoil);
                  Si.sprint(F("SWP: "),2); Si.sprint(swp,2); Si.sprint(F("kPa"),2);
                  Si.sprint(F(" for a soil temp of "),2); Si.sprintln(Tsoil,2);
                  //val = (int16_t)percent;
                  val = swp;
                else
                    resistanceCalc(frequency, wrm);
                    Si.sprintln(wrm,2);
                    kPaCalc(wrm, Tsoil, swp);
                    val = swp;
                Si.sprint(F("SWP: "),2); Si.sprintln(swp,2);
            void resistanceCalc(float frequencyInput, int32_t &wrm){
              wrm=0;
              // Convert from freqency to Resistance measurement
              // From SMX.pdf datasheet, page 6
              // 48 Hz    = 10,000,000 Ohms
              // 76 Hz    =    262,144 Ohms
              // 13233 Hz =          0 ohms
              // using lookup table held in the array  RESISTORarray
              //frequencyInput = constrain(frequencyInput,50, 13233);
              //float newVal;
              if (frequencyInput <= RESISTORarray[0]) {     // Minimum value
                wrm = RESISTORarray[0+1];
              if (frequencyInput >= RESISTORarray[74]) {     // Maximum value
                wrm = RESISTORarray[74+1];
              for (int i=0; i<74; i=i+2) {
                if ((frequencyInput >= RESISTORarray[i]) && (frequencyInput <= RESISTORarray[i+2]))
                  wrm = RESISTORarray[i+1] - ((RESISTORarray[i+1]-RESISTORarray[i+3]) * ((frequencyInput-RESISTORarray[i]) / (RESISTORarray[i+2]-RESISTORarray[i])));
                  break;
              Si.sprint(F("WRM: "),2); Si.sprintln(wrm,2);
            void kPaCalc(int32_t ResistanceInput, int16_t FTemperatureInput, int16_t &swp){
              // Convert from Resistance to SWP kPa measurement
              // From SMX.pdf datasheet, page 7
              //   550 Ohms =  0 SWP kPa
              //  6000 Ohms = 35 SWP kPa
              // 28075 Ohms =200 SWP kPa
              // using lookup table held in the array  SWPkPAarray
              // table valid for temperature of 75F, 24C
              // for increase of 1°F increase resistance by 1%.
              // ** this function accepts temperature in Fahrenheit units **
              //float newVal;
              // Adjust compensate resistance for temperature and cpnvert celculs to Fahrenheit
              // per page 8 of SMX.pdf
              swp=0;
              float ResistanceCompensated =  ResistanceInput *(1 + 0.001*((FTemperatureInput * 1.8 + 32)-75));
              Si.sprint(F("WRMc: "),2); Si.sprintln((int16_t)ResistanceCompensated,2);
                if (ResistanceCompensated <= SWPkPAarray[0]) {     // Minimum value
                swp = SWPkPAarray[0+1];
              if (ResistanceCompensated >= SWPkPAarray[74]) {     // Maximum value
                swp = SWPkPAarray[16+1];
              //for (int i=0; i<SWPkPAarray.length-2; i=i+2) {
              for (int i=0; i<16; i=i+2) {
                if ((ResistanceCompensated >= SWPkPAarray[i]) && (ResistanceCompensated <= SWPkPAarray[i+2])) {
                  swp = SWPkPAarray[i+1] - ((SWPkPAarray[i+1]-SWPkPAarray[i+3]) * ((ResistanceInput-SWPkPAarray[i]) / (SWPkPAarray[i+2]-SWPkPAarray[i])));
                  break;
              //return newVal;
            long RESISTORarray[76] = {
            // Watermark Sensor SMX interface Hz to Resistance lookup table per SMX.pdf page 6.
            48,  10000000,
            76,  262144,
            85,  196608,
            103, 131072,
            122, 98304,
            157, 65536,
            194, 49152,
            264, 32768,
            335, 24567,
            476, 16384,
            612, 12288,
            874, 8192,
            1135,  6144,
            1623,  4096,
            2071,  3072,
            2862,  2048,
            3557,  1536,
            4697,  1024,
            5596,  768,
            6932,  512,
            7878,  384,
            9104,  256,
            9882,  192,
            10802, 128,
            11312, 96,
            11893, 64,
            12200, 48,
            12526, 32,
            12708, 24,
            12871, 16,
            12962, 12,
            13047, 8,
            13092, 6,
            13139, 4,
            13162, 3,
            13186, 2,
            13209, 1,
            13233, 0,
            long SWPkPAarray[18]{
            // Watermark Sensor SMX interface Resistance to SWP kPa lookup table per SMX.pdf page 7.
            // this table is valid at temperature of 75F, 24C
             550,  0,
            1000,  9,
            1100,  10,
            2000,  15,
            6000,  35,
            9200,  55,
            12200, 75,
            15575, 100,
            28075, 200,
            Many thank!!
            • P
              P
              pierrot10
              I wonder if the problem does not come from here:
              if (ResistanceCompensated >= SWPkPAarray[74]) {}
              Should it be not 16?
              • H
                H
                hard-shovel
                yes you are correct, it should be 16.
                • P
                  P
                  pierrot10
                  #28
                  Hello Hard-shovel !
                  Are you still around?
                  I ma still doubting about my SWP value returning by my sensor and by the code to calculate it.
                  Until last week, I was used to use the great code you provide to me
                          Si.sprintln(wrm,2);
                          val = swp;
                  But I was always suspicous about the SWP value. I also bout a WATER digital reader and the values never matched.
                  All the graph/line of Station3 is calculate with a temperature of 24Celcul. As sensor is in a room where the temeparture is between 24C and 28C, a small tolerence must be "accepted" :)
                  Last week I used this to get the WRM (Watermark resistance)
                  but never use it. The result is wrong. I compared with datsheet of the Isometer and the result never matches.
                  However, your table works fine
                    wrm=0;
                    //float newVal;
                        break;
                  In order to be fixed this question, I used my LoRa node to send the wrm, swp and a second swp to my server and observe the diffrence.
                  Look at this web page (go to Station 3)
                  Station 3 (Teste)
                  Note:
                  Station 1 and 2 are two station on fields.
                  Station 3 is a node I have at home. I put a little of water on matrix of the watermark until the SWP go to 8kpa and left it dried 1,5 day until the the SWP is 200kps. one hour ago, I put the watermark sensor into water for one hour, and I am going to leave it drying under the sun and compare the graph. Today afternoon (15.9.2018), I am going to update the code of station 1 and 2 to get the SWP value with the equation of Shock
                  The red line is the WRM in Ohm and not ml/h (I have not change the unit).
                  The yellow line is the SWP return with the equation of Shock
                  and the violet line is the SWP return by
                    //float newVal;
                    swp=0;
                    if (ResistanceCompensated >= SWPkPAarray[16]) {     // Maximum value
                        break;
                    //return newVal;
                  It's interresting to see that the kPaCalc() progress as a step and stop at 100kpa and jump at 200kpa only when the wrm is 27950.
                  I used
                  constrain (wrm,550,27950)
                  so the wrm will not be display higher than 27950 even if it can go over 27950 as say the doc.
                  The equation of Shock look perfect and I controlled it with Watermark data reader. The result is similar with a tolerance of 5-10kpa.
                  From graph (See Station 3), I also compare the WRM and the SWP from the doc (see page 7) and SWP value matches.
                  I wonder why, in the array
                   550,  0,
                  1000,  9,
                  1100,  10,
                  2000,  15,
                  6000,  35,
                  9200,  55,
                  12200, 75,
                  15575, 100,
                  28075, 200,
                  you do not consider a SWP between 100kpa and 200kpa.
                  I thing it's very interresting to have value from 100kpa and 200kpa, as 100kpa is the moment when soil need to be irrigate and more we come close to 200kpa, more is dangerous.
                  In any case, your function kPaCalc2() from the code you provided to me, 3 mounth ago seems to be best.
                  Thank for all
                  Cheers
                  • P pierrot10
                    Hello Hard-shovel !
                            Si.sprintln(wrm,2);
                            val = swp;
                      wrm=0;
                      //float newVal;
                          break;
                    Station 3 (Teste)
                    Note:
                      //float newVal;
                      swp=0;
                          break;
                      //return newVal;
                    I used
                     550,  0,
                    1000,  9,
                    1100,  10,
                    2000,  15,
                    6000,  35,
                    9200,  55,
                    12200, 75,
                    15575, 100,
                    28075, 200,
                    Thank for all
                    Cheers
                    H
                    H
                    hard-shovel
                    #29
                    @pierrot10 the red violet line on the chart is showing an error in the processing as it should not jump in stages.
                    The error has appeared as you changed the original code from using float for ResistanceInput to Integer, however there was also a error in the orginal code that did not show up when using the float inputs.
                    You only need to change this line and verify results
                        //  swp = SWPkPAarray[i+1] - ((SWPkPAarray[i+1]-SWPkPAarray[i+3]) * ((ResistanceInput-SWPkPAarray[i]) / (SWPkPAarray[i+2]-SWPkPAarray[i])));
                    to use ResistanceCompensated which is in float format.
                          swp = SWPkPAarray[i+1] - ((SWPkPAarray[i+1]-SWPkPAarray[i+3]) * ((ResistanceCompensated -SWPkPAarray[i]) / (SWPkPAarray[i+2]-SWPkPAarray[i])));
                    Please test with values between 100 and 200 swp,
                    my results were
                    input Swp output
                    500Hz = 100swp
                    480hz = 105swp
                    435hz = 125swp
                    382Hz = 150swp
                    331Hz = 175swp
                    304Hz = 200swp
                    • H hard-shovel
                      my results were
                      input Swp output
                      500Hz = 100swp
                      480hz = 105swp
                      435hz = 125swp
                      382Hz = 150swp
                      331Hz = 175swp
                      304Hz = 200swp
                      P
                      P
                      pierrot10
                      #30
                      @hard-shovel said in How to read frequency and SWP output from watermark sensor:
                      the red line on the chart is showing an error in the processing as it should not jump in stages.
                      Hello, what do means by jump in stage with the red line?
                      Twice, the node could not send data but this due to a small error from me. Today, all data have been sent. Today, I left the node and the sensor outsite under the sun and I juts brang it back inside and the RWM went a little bit down. I am going to upload the code with your change, That great because right now the RWM is 88
                      • P pierrot10
                        H
                        H
                        hard-shovel
                        @pierrot10 I meant the violet line should be a smooth similar to the yellow line.
                        P 2 Replies Last reply
                        • H hard-shovel
                          P
                          P
                          pierrot10
                          @hard-shovel
                          Hello, Yes. Thank a lot to follow my topic :)
                          This morning I soaked it again the sensor into water for about 1 hour and I let it dry under the sun. It looks now really better ( See Station 3 ). I am happy with the result specially for Station 1 and 2 since yesterday 12h (UTC). Thanks a lot.
                          • H hard-shovel
                            P
                            P
                            pierrot10
                            @hard-shovel
                            Dear Hard-shovel.
                            In any case, thank a lot for your great help. Your participation helped me a lot and I would like to thank you again.
                            Now I am very happy with the result. I still keep an eye on it.
                            First I planted them in 3 different level: 15cm, 30cm and 45cm. Then I replanted them to try to observe the bulb of water: I planted them at (distance/deepth) 15cm/30cm, 15cm/60cm and 30cm/30cm from the point where drop the water. (I also make sure that all sensor have a distance of 30cm from each other to avoid interfrences). But as the ground is tilted, the drop do not fall where I expected.
                            Badly planted
                            Next step, I am going to change the position of my 3 watermark, making sure that the drop falls on the line of the sensor, as the following:
                            correct
                            When I planted them into the soil and see the difference of the result.
                            Do you have any suggestion to plant the 3 sensor?
                            In any case, tanks a lot. You helped me a lot.
                            Enjoy the end of sommer!
                            Cheers
                            • P pierrot10
                              @hard-shovel
                              Dear Hard-shovel.
                              Badly planted
                              correct
                              Cheers
                              H
                              H
                              hard-shovel
                              @pierrot10
                              Hi pierrot10 thank you for letting me know how it is working. I am glad to be of some help.
                              I have no experience of using the water sensors, I only looked at the data you posted and made a mock up of the converter module for testing.
                              My gardening is limited to two small potted plants that live on a window sill and have a capacitance sensor in each pot.
                              Best Regards
                              • P pierrot10
                                @hard-shovel
                                It's a huge, great what you wrote!!!
                                I will test it tomorrow!!! and compare the two different to calculate kpa ( kPaCalc2() and kPaCalc() )
                                :+1:
                                suhaila96
                                @pierrot10 Hi. Im very interested with your project because currently im doing a similar project. So, if u dont mind can i see how u setup the circuit because i want to compare with mine. Thank u. Hope u will reply my question^^
                                • S suhaila96
                                  P
                                  P
                                  pierrot10
                                  @suhaila96 Hello I have not seen your question since I reviewed this topics, today.
                                  What do you mean about "setup your circuit"? How did you connected you watermark sensor and to what?