  3. Issues when upgrading EnergyMeterPulseSensor from 1.5.x to 2.3.2
15 Posts 5 Posters 1.3k Views 4 Watching
  • J Offline
    J Offline
    jocke4u
    I have upgraded a few sensors and MySensors GW to 2.3.2 but when it comes to my EnergyMeterPulseSensor (which has a light sensor on top of the diod since >3 years) I face issues
    The original 1.5.x sketch looks like
    // Use this sensor to measure KWH and Watt of your house meeter
    // You need to set the correct pulsefactor of your meeter (blinks per KWH).
    // The sensor starts by fetching current KWH value from gateway.
    // Reports both KWH and Watt back to gateway.
    // Unfortunately millis() won't increment when the Arduino is in
    // sleepmode. So we cannot make this sensor sleep if we also want
    // to calculate/report watt-number.
    #define DIGITAL_INPUT_SENSOR 3  // The digital input you attached your light sensor.  (Only 2 and 3 generates interrupt!)
    #define SLEEP_MODE false        // Watt-value can only be reported when sleep mode is false.
    unsigned long SEND_FREQUENCY = 20000; // Minimum time between send (in milliseconds). We don't wnat to spam the gateway.
    double ppwh = ((double)PULSE_FACTOR)/1000; // Pulses per watt hour
    boolean pcReceived = false;
    unsigned long oldPulseCount = 0;
    unsigned long oldWatt = 0;
    double oldKwh;
    unsigned long lastSend;
    MyMessage wattMsg(CHILD_ID,V_WATT);
    MyMessage kwhMsg(CHILD_ID,V_KWH);
    MyMessage pcMsg(CHILD_ID,V_VAR1);
      gw.begin(incomingMessage);
      gw.sendSketchInfo("Energy Meter", "1.1");
      gw.present(CHILD_ID, S_POWER);
      gw.request(CHILD_ID, V_VAR1);
    //  attachInterrupt(INTERRUPT, onPulse, RISING);
      attachInterrupt(INTERRUPT, onPulse, FALLING); // JOCKE
      lastSend=millis();
      unsigned long now = millis();
      if (pcReceived && (SLEEP_MODE || sendTime)) {
    //    if (!SLEEP_MODE && watt != oldWatt) { //JOCKE: Always send
          if (watt<((unsigned long)MAX_WATT)) {
            gw.send(wattMsg.set(watt));  // Send watt value to gw
          Serial.print("Watt:");
          Serial.println(watt);
          oldWatt = watt;
        // Pulse cout has changed
    //    if (pulseCount != oldPulseCount) { // JOCKE: Always send
          gw.send(pcMsg.set(pulseCount));  // Send pulse count value to gw
          double kwh = ((double)pulseCount/((double)PULSE_FACTOR));
          oldPulseCount = pulseCount;
          if (kwh != oldKwh) {
            gw.send(kwhMsg.set(kwh, 4));  // Send kwh value to gw
            oldKwh = kwh;
        lastSend = now;
      } else if (sendTime && !pcReceived) {
        // No count received. Try requesting it again
        lastSend=now;
      if (SLEEP_MODE) {
        gw.sleep(SEND_FREQUENCY);
      if (message.type==V_VAR1) {
        pulseCount = oldPulseCount = message.getLong();
        Serial.print("Received last pulse count from gw:");
        Serial.println(pulseCount);
        pcReceived = true;
    void onPulse()
      if (!SLEEP_MODE) {
        unsigned long interval = newBlink-lastBlink;
        if (interval<10000L) { // Sometimes we get interrupt on RISING
          return;
        watt = (3600000000.0 /interval) / ppwh;
        lastBlink = newBlink;
      pulseCount++;
    The 2.3.2 upgraded sketch looks like:
    // Enable debug prints
    #define MY_RADIO_RF24
    //#define MY_RADIO_NRF5_ESB
    //#define MY_RADIO_RFM95
    #define PULSE_FACTOR 1000       // Number of blinks per kWh of your meter. Normally 1000.
    #define SLEEP_MODE false        // Watt value can only be reported when sleep mode is false.
    #define MAX_WATT 10000          // Max watt value to report. This filters outliers.
    // OLD  - #define INTERRUPT DIGITAL_INPUT_SENSOR-2 // Usually the interrupt = pin -2 (on uno/nano anyway)
    uint32_t SEND_FREQUENCY =
        20000; // Minimum time between send (in milliseconds). We don't want to spam the gateway.
    double ppwh = ((double)PULSE_FACTOR) / 1000; // Pulses per watt hour
    bool pcReceived = false;
    volatile uint32_t pulseCount = 0;
    volatile uint32_t lastBlinkmicros = 0;
    volatile uint32_t lastBlinkmillis = 0;
    volatile uint32_t watt = 0;
    uint32_t oldPulseCount = 0;
    uint32_t oldWatt = 0;
    double oldkWh;
    uint32_t lastSend;
    MyMessage wattMsg(CHILD_ID, V_WATT);
    MyMessage kWhMsg(CHILD_ID, V_KWH);
    MyMessage pcMsg(CHILD_ID, V_VAR1);
    #if defined(ARDUINO_ARCH_ESP8266) || defined(ARDUINO_ARCH_ESP32)
    #define IRQ_HANDLER_ATTR ICACHE_RAM_ATTR
    // --------OLD To investigate ----------
    //volatile unsigned long lastBlink = 0;
    void IRQ_HANDLER_ATTR onPulse()
      if (!SLEEP_MODE) {
        uint32_t newBlinkmicros = micros();
        uint32_t newBlinkmillis = millis();
        uint32_t intervalmicros = newBlinkmicros - lastBlinkmicros;
        uint32_t intervalmillis = newBlinkmillis - lastBlinkmillis;
        if (intervalmicros < 10000L && intervalmillis < 10L) { // Sometimes we get interrupt on RISING
          return;
        if (intervalmillis < 360000) { // Less than an hour since last pulse, use microseconds
          watt = (3600000000.0 / intervalmicros) / ppwh;
          watt = (3600000.0 / intervalmillis) /
                 ppwh; // more thAn an hour since last pulse, use milliseconds as micros will overflow after 70min
        lastBlinkmicros = newBlinkmicros;
        lastBlinkmillis = newBlinkmillis;
      pulseCount++;
      pinMode(DIGITAL_INPUT_SENSOR, INPUT_PULLUP);
      attachInterrupt(digitalPinToInterrupt(DIGITAL_INPUT_SENSOR), onPulse, FALLING);
      // OLD one
      ////  attachInterrupt(INTERRUPT, onPulse, RISING);
      //attachInterrupt(INTERRUPT, onPulse, FALLING); // JOCKE
      lastSend = millis();
      sendSketchInfo(F("Energy Meter"), F("2.3.2"));
      uint32_t now = millis();
          // Check that we don't get unreasonable large watt value, which
          // could happen when long wraps or false interrupt triggered
          if (watt < ((uint32_t)MAX_WATT)) {
          oldWatt = watt;
        // Pulse count value has changed
          double kWh = ((double)pulseCount / ((double)PULSE_FACTOR));
          if (kWh != oldkWh) {
            send(kWhMsg.set(kWh, 4));  // Send kWh value to gw
            oldkWh = kWh;
        lastSend = now;
        // No pulse count value received from controller. Try requesting it again.
        lastSend = now;
      if (SLEEP_MODE) {
        sleep(SEND_FREQUENCY, false);
      if (message.getType()==V_VAR1) {
        Serial.print("Received last pulse count value from gw:");
        pcReceived = true;
    It seems it get stuck on requesting V_VAR1
    From the serial monitor I get:
     __  __       ____
            |___/                      2.3.2
    16 MCO:BGN:INIT NODE,CP=RNNNA---,FQ=16,REL=255,VER=2.3.2
    26 TSM:INIT
    28 TSF:WUR:MS=0
    34 TSM:INIT:TSP OK
    36 TSF:SID:OK,ID=6
    37 TSM:FPAR
    41 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    2050 !TSM:FPAR:NO REPLY
    2052 TSM:FPAR
    2056 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    4063 !TSM:FPAR:NO REPLY
    4065 TSM:FPAR
    4069 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    6076 !TSM:FPAR:NO REPLY
    6078 TSM:FPAR
    6082 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    8089 !TSM:FPAR:FAIL
    8090 TSM:FAIL:CNT=1
    8092 TSM:FAIL:DIS
    8094 TSF:TDI:TSL
    18096 TSM:FAIL:RE-INIT
    18098 TSM:INIT
    18104 TSM:INIT:TSP OK
    18106 TSF:SID:OK,ID=6
    18108 TSM:FPAR
    18113 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    20120 !TSM:FPAR:NO REPLY
    20122 TSM:FPAR
    20126 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    22134 !TSM:FPAR:NO REPLY
    22136 TSM:FPAR
    22140 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    24148 !TSM:FPAR:NO REPLY
    24151 TSM:FPAR
    24155 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    26162 !TSM:FPAR:FAIL
    26163 TSM:FAIL:CNT=2
    26165 TSM:FAIL:DIS
    26167 TSF:TDI:TSL
    36170 TSM:FAIL:RE-INIT
    36172 TSM:INIT
    36178 TSM:INIT:TSP OK
    36180 TSF:SID:OK,ID=6
    36183 TSM:FPAR
    36188 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    38195 !TSM:FPAR:NO REPLY
    38197 TSM:FPAR
    38201 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
    38636 TSF:MSG:READ,0-0-6,s=255,c=3,t=8,pt=1,l=1,sg=0:0
    38641 TSF:MSG:FPAR OK,ID=0,D=1
    40208 TSM:FPAR:OK
    I also tried to ClearEepromConfig, only gave it a new node ID.
    Do you have any tips and tricks to get it working.
    Y 1 Reply Last reply
    • N Offline
      N Offline
      niclas
      What happens after the TSM:FPAR:OK ? It seems like the interesting stuffs happens after that part?
      • J Offline
        J Offline
        jocke4u
        Here is the full log until I closed it
         __  __       ____
                |___/                      2.3.2
        26 TSM:INIT
        28 TSF:WUR:MS=0
        34 TSM:INIT:TSP OK
        36 TSF:SID:OK,ID=6
        37 TSM:FPAR
        2052 TSM:FPAR
        4065 TSM:FPAR
        6078 TSM:FPAR
        8089 !TSM:FPAR:FAIL
        8090 TSM:FAIL:CNT=1
        8092 TSM:FAIL:DIS
        8094 TSF:TDI:TSL
        18098 TSM:INIT
        18108 TSM:FPAR
        20122 TSM:FPAR
        22136 TSM:FPAR
        24151 TSM:FPAR
        26165 TSM:FAIL:DIS
        26167 TSF:TDI:TSL
        36172 TSM:INIT
        36183 TSM:FPAR
        38197 TSM:FPAR
        40208 TSM:FPAR:OK
        40209 TSM:ID
        40211 TSM:ID:OK
        40212 TSM:UPL
        40249 !TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=NACK:1
        42257 TSM:UPL
        42294 !TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=1,st=NACK:1
        44301 TSM:UPL
        44338 !TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=2,st=NACK:1
        46345 TSM:UPL
        46382 !TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=3,st=NACK:1
        48389 !TSM:UPL:FAIL
        48390 TSM:FPAR
        48395 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=4,st=OK:
        50402 !TSM:FPAR:NO REPLY
        50404 TSM:FPAR
        50408 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        52415 !TSM:FPAR:NO REPLY
        52417 TSM:FPAR
        52421 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        54429 !TSM:FPAR:NO REPLY
        54431 TSM:FPAR
        54435 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        54663 TSF:MSG:READ,0-0-6,s=255,c=3,t=8,pt=1,l=1,sg=0:0
        54668 TSF:MSG:FPAR OK,ID=0,D=1
        56442 TSM:FPAR:OK
        56443 TSM:ID
        56445 TSM:ID:OK
        56446 TSM:UPL
        56483 !TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=NACK:1
        58492 TSM:UPL
        58529 !TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=1,st=NACK:1
        60536 TSM:UPL
        60573 !TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=2,st=NACK:1
        62580 TSM:UPL
        62617 !TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=3,st=NACK:1
        64624 !TSM:UPL:FAIL
        64625 TSM:FPAR
        64630 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=4,st=OK:
        66637 !TSM:FPAR:NO REPLY
        66639 TSM:FPAR
        66643 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        68651 !TSM:FPAR:NO REPLY
        68653 TSM:FPAR
        68657 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        70665 !TSM:FPAR:NO REPLY
        70667 TSM:FPAR
        70671 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        72678 !TSM:FPAR:FAIL
        72679 TSM:FAIL:CNT=3
        72681 TSM:FAIL:DIS
        72683 TSF:TDI:TSL
        82686 TSM:FAIL:RE-INIT
        82689 TSM:INIT
        82695 TSM:INIT:TSP OK
        82697 TSF:SID:OK,ID=6
        82699 TSM:FPAR
        82704 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        84711 !TSM:FPAR:NO REPLY
        84713 TSM:FPAR
        84717 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        86724 !TSM:FPAR:NO REPLY
        86726 TSM:FPAR
        86730 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        88737 !TSM:FPAR:NO REPLY
        88739 TSM:FPAR
        88743 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        90752 !TSM:FPAR:FAIL
        90753 TSM:FAIL:CNT=4
        90755 TSM:FAIL:DIS
        90757 TSF:TDI:TSL
        100760 TSM:FAIL:RE-INIT
        100762 TSM:INIT
        100768 TSM:INIT:TSP OK
        100771 TSF:SID:OK,ID=6
        100773 TSM:FPAR
        100777 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        102786 !TSM:FPAR:NO REPLY
        102788 TSM:FPAR
        102792 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        104800 !TSM:FPAR:NO REPLY
        104802 TSM:FPAR
        104806 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        106814 !TSM:FPAR:NO REPLY
        106816 TSM:FPAR
        106820 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        108828 !TSM:FPAR:FAIL
        108830 TSM:FAIL:CNT=5
        108832 TSM:FAIL:DIS
        108834 TSF:TDI:TSL
        118836 TSM:FAIL:RE-INIT
        118838 TSM:INIT
        118844 TSM:INIT:TSP OK
        118847 TSF:SID:OK,ID=6
        118849 TSM:FPAR
        118853 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        120861 !TSM:FPAR:NO REPLY
        120863 TSM:FPAR
        120867 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        122876 !TSM:FPAR:NO REPLY
        122878 TSM:FPAR
        122883 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        124891 !TSM:FPAR:NO REPLY
        124893 TSM:FPAR
        124897 ?TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
        126905 !TSM:FPAR:FAIL
        126907 TSM:FAIL:CNT=6
        126909 TSM:FAIL:DIS
        126911 TSF:TDI:TSL
        136913 TSM:FAIL:RE-INIT
        • N Offline
          N Offline
          niclas
          Not really sure what to make of the log. To me it looks like it isn't connecting properly with the gateway but the picture from MYSController (I have never tried the software) looks promising as it has exchanged information about sketch name, version and so on. I'm also new to MySensors so i'm not able to say what has changed from the two versions. What was the default parameters for nRF24 in 1.5? Amplification and so on.
          Hopefully someone else could be of more help...
          • J jocke4u
            double oldKwh;
              lastSend=millis();
                  oldWatt = watt;
                    oldKwh = kwh;
                lastSend = now;
                lastSend=now;
              if (SLEEP_MODE) {
                pcReceived = true;
            void onPulse()
              if (!SLEEP_MODE) {
                  return;
              pulseCount++;
            double oldkWh;
            uint32_t lastSend;
              if (!SLEEP_MODE) {
                  return;
              pulseCount++;
              // OLD one
                  oldWatt = watt;
                    oldkWh = kWh;
                lastSend = now;
                lastSend = now;
              if (SLEEP_MODE) {
                pcReceived = true;
             __  __       ____
                    |___/                      2.3.2
            26 TSM:INIT
            28 TSF:WUR:MS=0
            34 TSM:INIT:TSP OK
            36 TSF:SID:OK,ID=6
            37 TSM:FPAR
            2052 TSM:FPAR
            4065 TSM:FPAR
            6078 TSM:FPAR
            8089 !TSM:FPAR:FAIL
            8090 TSM:FAIL:CNT=1
            8092 TSM:FAIL:DIS
            8094 TSF:TDI:TSL
            18098 TSM:INIT
            18108 TSM:FPAR
            20122 TSM:FPAR
            22136 TSM:FPAR
            24151 TSM:FPAR
            26165 TSM:FAIL:DIS
            26167 TSF:TDI:TSL
            36172 TSM:INIT
            36183 TSM:FPAR
            38197 TSM:FPAR
            40208 TSM:FPAR:OK
            Y Offline
            Y Offline
            @jocke4u you changed a lot to your sketch when going from 1.5.x to 2.3.2, including e.g. the interrupt handler.
            I would advise to first convert your sketch to 2.3.2 only (following e.g. https://forum.mysensors.org/topic/4276/converting-a-sketch-from-1-5-x-to-2-0-x) and then, if that works correctly, start changing other parts of the sketch (e.g. the interrupt handling).
            You could also flash a basic sketch to test if the hardware performs correctly (I can only hope you didn't switch hardware when going to 2.3.2 :grimacing: )
            The log files you posted don't seem to match the screenshot -- there are no internal messages in the log, while the screenshot shows e.g. even the sketch name being transmitted.
            J 1 Reply Last reply
            • Y Yveaux
              J Offline
              J Offline
              jocke4u
              @Yveaux Thanks for your input.
              The hardware is unchanged ;)
              The sketch is pretty "stock" from example at the time at 1.5.4 and with 2.3.2 I went for the example as well and just secured the pins were the same etc.
              I will give your suggestion a try, just modify the pieces needed to use 2.3.2 and then leave the rest as is.
              (I wasn't sure if anything were encapsulated in 2.3.2 MySensor so that's why)
              • J jocke4u
                Y Offline
                Y Offline
                @jocke4u how about the log files don't match the screenshot?
                • J Offline
                  J Offline
                  jocke4u
                  So I followed @Yveaux good advice to port the MySensors sketch as plain as possible from 1.5.4 to 2.3.2.
                  I think the logs are in synk now also @Yveaux
                  The sketch now looks like:
                  // Node 49 Energy Sensor
                  // Measure Total Energy
                  // Sending every 20 sec
                  double oldKwh;
                    sendSketchInfo("Energy Meter", "2.3.2");
                    //begin(incomingMessage);
                    lastSend=millis();
                        oldWatt = watt;
                          oldKwh = kwh;
                      lastSend = now;
                      lastSend=now;
                    if (SLEEP_MODE) {
                  //void incomingMessage(const MyMessage &message) {
                      pcReceived = true;
                  void onPulse()
                    if (!SLEEP_MODE) {
                        return;
                    pulseCount++;
                  I cleared the Eeprom on the sensor first and when kicking the Serial Monitor in "Arduino Studio" I get the logs as follows
                   __  __       ____
                          |___/                      2.3.2
                  26 TSM:INIT
                  28 TSF:WUR:MS=0
                  34 TSM:INIT:TSP OK
                  36 TSF:SID:OK,ID=7
                  37 TSM:FPAR
                  41 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  2052 TSM:FPAR
                  2056 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  4065 TSM:FPAR
                  4069 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  6078 TSM:FPAR
                  6082 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  8089 !TSM:FPAR:FAIL
                  8090 TSM:FAIL:CNT=1
                  8092 TSM:FAIL:DIS
                  8094 TSF:TDI:TSL
                  18098 TSM:INIT
                  18106 TSF:SID:OK,ID=7
                  18108 TSM:FPAR
                  18113 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  20122 TSM:FPAR
                  20126 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  22136 TSM:FPAR
                  22140 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  24151 TSM:FPAR
                  24155 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  26165 TSM:FAIL:DIS
                  26167 TSF:TDI:TSL
                  36172 TSM:INIT
                  36180 TSF:SID:OK,ID=7
                  36183 TSM:FPAR
                  36188 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  38197 TSM:FPAR
                  38201 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  38844 TSF:MSG:READ,0-0-7,s=255,c=3,t=8,pt=1,l=1,sg=0:0
                  38849 TSF:MSG:FPAR OK,ID=0,D=1
                  40209 TSM:FPAR:OK
                  40210 TSM:ID
                  40212 TSM:ID:OK
                  40213 TSM:UPL
                  40250 !TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=NACK:1
                  42258 TSM:UPL
                  42295 !TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=1,st=NACK:1
                  44302 TSM:UPL
                  44339 !TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=2,st=NACK:1
                  46346 TSM:UPL
                  46383 !TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=3,st=NACK:1
                  48390 !TSM:UPL:FAIL
                  48391 TSM:FPAR
                  48396 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=4,st=OK:
                  50403 !TSM:FPAR:NO REPLY
                  50405 TSM:FPAR
                  50409 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  52416 !TSM:FPAR:NO REPLY
                  52418 TSM:FPAR
                  52422 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  54430 !TSM:FPAR:NO REPLY
                  54432 TSM:FPAR
                  54436 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  56444 !TSM:FPAR:FAIL
                  56445 TSM:FAIL:CNT=3
                  56448 TSM:FAIL:DIS
                  56450 TSF:TDI:TSL
                  66453 TSM:FAIL:RE-INIT
                  66455 TSM:INIT
                  66461 TSM:INIT:TSP OK
                  66463 TSF:SID:OK,ID=7
                  66465 TSM:FPAR
                  66470 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  68478 !TSM:FPAR:NO REPLY
                  68481 TSM:FPAR
                  68485 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  70492 !TSM:FPAR:NO REPLY
                  70494 TSM:FPAR
                  70498 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  72506 !TSM:FPAR:NO REPLY
                  72508 TSM:FPAR
                  72512 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  74519 !TSM:FPAR:FAIL
                  74520 TSM:FAIL:CNT=4
                  74522 TSM:FAIL:DIS
                  74524 TSF:TDI:TSL
                  84527 TSM:FAIL:RE-INIT
                  84529 TSM:INIT
                  84535 TSM:INIT:TSP OK
                  84537 TSF:SID:OK,ID=7
                  84539 TSM:FPAR
                  84544 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  86551 !TSM:FPAR:NO REPLY
                  86553 TSM:FPAR
                  86557 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  88564 !TSM:FPAR:NO REPLY
                  88566 TSM:FPAR
                  88570 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  90578 !TSM:FPAR:NO REPLY
                  90580 TSM:FPAR
                  90585 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  92592 !TSM:FPAR:FAIL
                  92593 TSM:FAIL:CNT=5
                  92595 TSM:FAIL:DIS
                  92597 TSF:TDI:TSL
                  102600 TSM:FAIL:RE-INIT
                  102602 TSM:INIT
                  102608 TSM:INIT:TSP OK
                  102611 TSF:SID:OK,ID=7
                  102614 TSM:FPAR
                  102618 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  104626 !TSM:FPAR:NO REPLY
                  104628 TSM:FPAR
                  104632 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  106640 !TSM:FPAR:NO REPLY
                  106642 TSM:FPAR
                  106646 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  108654 !TSM:FPAR:NO REPLY
                  108656 TSM:FPAR
                  108660 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  110668 !TSM:FPAR:FAIL
                  110670 TSM:FAIL:CNT=6
                  110672 TSM:FAIL:DIS
                  110674 TSF:TDI:TSL
                  120676 TSM:FAIL:RE-INIT
                  120678 TSM:INIT
                  120684 TSM:INIT:TSP OK
                  120687 TSF:SID:OK,ID=7
                  120689 TSM:FPAR
                  120693 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  122701 !TSM:FPAR:NO REPLY
                  122703 TSM:FPAR
                  122707 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  124716 !TSM:FPAR:NO REPLY
                  124718 TSM:FPAR
                  124722 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  126730 !TSM:FPAR:NO REPLY
                  126732 TSM:FPAR
                  126736 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  128744 !TSM:FPAR:FAIL
                  128746 TSM:FAIL:CNT=7
                  128748 TSM:FAIL:DIS
                  128750 TSF:TDI:TSL
                  188752 TSM:FAIL:RE-INIT
                  188754 TSM:INIT
                  188761 TSM:INIT:TSP OK
                  188764 TSF:SID:OK,ID=7
                  188766 TSM:FPAR
                  188770 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  190778 !TSM:FPAR:NO REPLY
                  190780 TSM:FPAR
                  190784 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  192792 !TSM:FPAR:NO REPLY
                  192794 TSM:FPAR
                  192798 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  194806 !TSM:FPAR:NO REPLY
                  194808 TSM:FPAR
                  194812 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  196822 !TSM:FPAR:FAIL
                  196824 TSM:FAIL:CNT=7
                  196826 TSM:FAIL:DIS
                  196828 TSF:TDI:TSL
                  256830 TSM:FAIL:RE-INIT
                  256832 TSM:INIT
                  256838 TSM:INIT:TSP OK
                  256841 TSF:SID:OK,ID=7
                  256843 TSM:FPAR
                  256847 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  258856 !TSM:FPAR:NO REPLY
                  258859 TSM:FPAR
                  258863 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  260871 !TSM:FPAR:NO REPLY
                  260873 TSM:FPAR
                  260877 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  262885 !TSM:FPAR:NO REPLY
                  262887 TSM:FPAR
                  262891 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  264899 !TSM:FPAR:FAIL
                  264901 TSM:FAIL:CNT=7
                  264903 TSM:FAIL:DIS
                  264905 TSF:TDI:TSL
                  324907 TSM:FAIL:RE-INIT
                  324909 TSM:INIT
                  324915 TSM:INIT:TSP OK
                  324918 TSF:SID:OK,ID=7
                  324920 TSM:FPAR
                  324924 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  326932 !TSM:FPAR:NO REPLY
                  326934 TSM:FPAR
                  326938 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  328946 !TSM:FPAR:NO REPLY
                  328948 TSM:FPAR
                  328952 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  330961 !TSM:FPAR:NO REPLY
                  330963 TSM:FPAR
                  330968 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  332976 !TSM:FPAR:FAIL
                  332978 TSM:FAIL:CNT=7
                  332980 TSM:FAIL:DIS
                  332982 TSF:TDI:TSL
                  392984 TSM:FAIL:RE-INIT
                  392986 TSM:INIT
                  392992 TSM:INIT:TSP OK
                  392995 TSF:SID:OK,ID=7
                  392997 TSM:FPAR
                  393001 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  395010 !TSM:FPAR:NO REPLY
                  395012 TSM:FPAR
                  395016 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  397024 !TSM:FPAR:NO REPLY
                  397026 TSM:FPAR
                  397030 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  399038 !TSM:FPAR:NO REPLY
                  399040 TSM:FPAR
                  399044 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  401052 !TSM:FPAR:FAIL
                  401054 TSM:FAIL:CNT=7
                  401056 TSM:FAIL:DIS
                  401058 TSF:TDI:TSL
                  461060 TSM:FAIL:RE-INIT
                  461062 TSM:INIT
                  461068 TSM:INIT:TSP OK
                  461071 TSF:SID:OK,ID=7
                  461073 TSM:FPAR
                  461077 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  463085 !TSM:FPAR:NO REPLY
                  463087 TSM:FPAR
                  463091 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  465099 !TSM:FPAR:NO REPLY
                  465101 TSM:FPAR
                  465105 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  467115 !TSM:FPAR:NO REPLY
                  467117 TSM:FPAR
                  467121 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  469129 !TSM:FPAR:FAIL
                  469131 TSM:FAIL:CNT=7
                  469133 TSM:FAIL:DIS
                  469135 TSF:TDI:TSL
                  529137 TSM:FAIL:RE-INIT
                  529139 TSM:INIT
                  529145 TSM:INIT:TSP OK
                  529148 TSF:SID:OK,ID=7
                  529150 TSM:FPAR
                  529155 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  531163 !TSM:FPAR:NO REPLY
                  531165 TSM:FPAR
                  531169 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  533177 !TSM:FPAR:NO REPLY
                  533179 TSM:FPAR
                  533183 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  535191 !TSM:FPAR:NO REPLY
                  535193 TSM:FPAR
                  535197 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  537205 !TSM:FPAR:FAIL
                  537207 TSM:FAIL:CNT=7
                  537209 TSM:FAIL:DIS
                  537211 TSF:TDI:TSL
                  597213 TSM:FAIL:RE-INIT
                  597215 TSM:INIT
                  597221 TSM:INIT:TSP OK
                  597224 TSF:SID:OK,ID=7
                  597226 TSM:FPAR
                  597230 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  599238 !TSM:FPAR:NO REPLY
                  599240 TSM:FPAR
                  599244 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  601252 !TSM:FPAR:NO REPLY
                  601254 TSM:FPAR
                  601259 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  603267 !TSM:FPAR:NO REPLY
                  603269 TSM:FPAR
                  603273 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  605281 !TSM:FPAR:FAIL
                  605283 TSM:FAIL:CNT=7
                  605285 TSM:FAIL:DIS
                  605287 TSF:TDI:TSL
                  665289 TSM:FAIL:RE-INIT
                  665291 TSM:INIT
                  665297 TSM:INIT:TSP OK
                  665300 TSF:SID:OK,ID=7
                  665303 TSM:FPAR
                  665307 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  667315 !TSM:FPAR:NO REPLY
                  667317 TSM:FPAR
                  667321 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  669329 !TSM:FPAR:NO REPLY
                  669331 TSM:FPAR
                  669335 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  671343 !TSM:FPAR:NO REPLY
                  671345 TSM:FPAR
                  671349 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  671833 TSF:MSG:READ,0-0-7,s=255,c=3,t=8,pt=1,l=1,sg=0:0
                  671838 TSF:MSG:FPAR OK,ID=0,D=1
                  673357 TSM:FPAR:OK
                  673358 TSM:ID
                  673360 TSM:ID:OK
                  673361 TSM:UPL
                  673399 !TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=NACK:1
                  675406 TSM:UPL
                  675443 !TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=1,st=NACK:1
                  677450 TSM:UPL
                  677487 !TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=2,st=NACK:1
                  679494 TSM:UPL
                  679531 !TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=3,st=NACK:1
                  681538 !TSM:UPL:FAIL
                  681540 TSM:FPAR
                  681544 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=4,st=OK:
                  683551 !TSM:FPAR:NO REPLY
                  683553 TSM:FPAR
                  683557 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  685566 !TSM:FPAR:NO REPLY
                  685569 TSM:FPAR
                  685573 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  687581 !TSM:FPAR:NO REPLY
                  687583 TSM:FPAR
                  687587 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  689595 !TSM:FPAR:FAIL
                  689597 TSM:FAIL:CNT=7
                  689599 TSM:FAIL:DIS
                  689601 TSF:TDI:TSL
                  749603 TSM:FAIL:RE-INIT
                  749605 TSM:INIT
                  749612 TSM:INIT:TSP OK
                  749615 TSF:SID:OK,ID=7
                  749617 TSM:FPAR
                  749621 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  751629 !TSM:FPAR:NO REPLY
                  751631 TSM:FPAR
                  751635 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  753643 !TSM:FPAR:NO REPLY
                  753645 TSM:FPAR
                  753649 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  755657 !TSM:FPAR:NO REPLY
                  755659 TSM:FPAR
                  755663 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  757672 !TSM:FPAR:FAIL
                  757675 TSM:FAIL:CNT=7
                  757677 TSM:FAIL:DIS
                  757679 TSF:TDI:TSL
                  817681 TSM:FAIL:RE-INIT
                  817683 TSM:INIT
                  817689 TSM:INIT:TSP OK
                  817692 TSF:SID:OK,ID=7
                  817694 TSM:FPAR
                  817698 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  819706 !TSM:FPAR:NO REPLY
                  819708 TSM:FPAR
                  819713 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  821721 !TSM:FPAR:NO REPLY
                  821723 TSM:FPAR
                  821727 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  823735 !TSM:FPAR:NO REPLY
                  823737 TSM:FPAR
                  823741 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                  825749 !TSM:FPAR:FAIL
                  825751 TSM:FAIL:CNT=7
                  825753 TSM:FAIL:DIS
                  825755 TSF:TDI:TSL
                  And the corresponding logs in MYSController looks like:
                  And I observe a number of C_REQ like:
                  • J Offline
                    J Offline
                    jocke4u
                    Ok, still trying to get this to work.
                    Added som more print-outs and I don't understand why none of the prints gets into the Serial Monitor.
                    Is it stuck into MySensors so the sketch isn't started correctly, or what happens?!
                    The ugly Sketch
                    // Node Total Energy Sensor
                    double oldKwh;
                      Serial.println("### Start Present");
                      Serial.println("### End Present");
                      Serial.println("### Start Setup");
                      lastSend=millis();
                      Serial.println("### End Setup");
                      Serial.println("### Loop");
                          Serial.println("");
                          Serial.print("### Sending WATTS: ");
                        oldWatt = watt;
                          Serial.println("");
                          Serial.print("### Sending kWh: ");
                          Serial.println(kwh);
                          oldKwh = kwh;
                        lastSend = now;
                        lastSend=now;
                      if (SLEEP_MODE) {
                        Serial.println("");
                        Serial.print("### Received last pulse count from gw:");
                        pcReceived = true;
                    void onPulse()
                      if (!SLEEP_MODE) {
                          return;
                      Serial.print(" . ");
                      pulseCount++;
                    The output from Serial Monitor:
                     __  __       ____
                            |___/                      2.3.2
                    26 TSM:INIT
                    28 TSF:WUR:MS=0
                    34 TSM:INIT:TSP OK
                    36 TSF:SID:OK,ID=7
                    37 TSM:FPAR
                    2052 TSM:FPAR
                    4065 TSM:FPAR
                    6078 TSM:FPAR
                    8089 !TSM:FPAR:FAIL
                    8090 TSM:FAIL:CNT=1
                    8092 TSM:FAIL:DIS
                    8094 TSF:TDI:TSL
                    18098 TSM:INIT
                    18108 TSM:FPAR
                    20122 TSM:FPAR
                    22136 TSM:FPAR
                    24151 TSM:FPAR
                    26165 TSM:FAIL:DIS
                    26167 TSF:TDI:TSL
                    36172 TSM:INIT
                    36183 TSM:FPAR
                    38197 TSM:FPAR
                    40209 !TSM:FPAR:NO REPLY
                    40211 TSM:FPAR
                    40215 ?TSF:MSG:SEND,7-7-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                    • J jocke4u
                      The ugly Sketch
                      double oldKwh;
                        lastSend=millis();
                            Serial.println("");
                          oldWatt = watt;
                            Serial.println("");
                            oldKwh = kwh;
                          lastSend = now;
                          lastSend=now;
                        if (SLEEP_MODE) {
                          Serial.println("");
                          pcReceived = true;
                      void onPulse()
                        if (!SLEEP_MODE) {
                            return;
                        pulseCount++;
                       __  __       ____
                              |___/                      2.3.2
                      26 TSM:INIT
                      28 TSF:WUR:MS=0
                      34 TSM:INIT:TSP OK
                      36 TSF:SID:OK,ID=7
                      37 TSM:FPAR
                      2052 TSM:FPAR
                      4065 TSM:FPAR
                      6078 TSM:FPAR
                      8089 !TSM:FPAR:FAIL
                      8090 TSM:FAIL:CNT=1
                      8092 TSM:FAIL:DIS
                      8094 TSF:TDI:TSL
                      18098 TSM:INIT
                      18108 TSM:FPAR
                      20122 TSM:FPAR
                      22136 TSM:FPAR
                      24151 TSM:FPAR
                      26165 TSM:FAIL:DIS
                      26167 TSF:TDI:TSL
                      36172 TSM:INIT
                      36183 TSM:FPAR
                      38197 TSM:FPAR
                      40211 TSM:FPAR
                      @jocke4u the node is unable to find a path to your gateway, so it never reaches loop()
                      Could you post the log from your gateway and the gateway sketch?
                      Do you still have your 1.x gateway running? Is it using the same channel?
                      • J Offline
                        J Offline
                        jocke4u
                        Thanks Mikael (@mfalkvidd )
                        The GW is running 2.3.2 and have not changed the channel ( I skipped the RPi approach as we discussed in another thread)
                        I hooked up my gateway to Arduino Serial Monitor and during this time I also restarted this sensor.
                        Please note that I have other sensors reporting correctly.
                        Log log shows:
                        0 MCO:BGN:INIT GW,CP=RNNGA---,FQ=16,REL=255,VER=2.3.2
                        4 TSM:INIT
                        5 TSF:WUR:MS=0
                        12 TSM:INIT:TSP OK
                        13 TSM:INIT:GW MODE
                        15 TSM:READY:ID=0,PAR=0,DIS=0
                        18 MCO:REG:NOT NEEDED
                        580 GWT:TIN:IP=192.168.1.11
                        1584 MCO:BGN:STP
                        1586 MCO:BGN:INIT OK,TSP=1
                        1588 TSM:READY:NWD REQ
                        1593 ?TSF:MSG:SEND,0-0-255-255,s=255,c=3,t=20,pt=0,l=0,sg=0,ft=0,st=OK:
                        2140 TSF:MSG:READ,7-7-0,s=255,c=3,t=21,pt=1,l=1,sg=0:0
                        14924 TSF:MSG:READ,7-7-0,s=1,c=2,t=24,pt=0,l=0,sg=0:
                        34877 TSF:MSG:READ,7-7-0,s=1,c=2,t=24,pt=0,l=0,sg=0:
                        54829 TSF:MSG:READ,7-7-0,s=1,c=2,t=24,pt=0,l=0,sg=0:
                        80115 TSF:MSG:READ,7-7-255,s=255,c=3,t=7,pt=0,l=0,sg=0:
                        80120 TSF:MSG:BC
                        80122 TSF:MSG:FPAR REQ,ID=7
                        80124 TSF:PNG:SEND,TO=0
                        80128 TSF:CKU:OK
                        80129 TSF:MSG:GWL OK
                        80392 TSF:MSG:SEND,0-0-7-7,s=255,c=3,t=8,pt=1,l=1,sg=0,ft=0,st=OK:0
                        82126 TSF:MSG:READ,7-7-0,s=255,c=3,t=24,pt=1,l=1,sg=0:1
                        82131 TSF:MSG:PINGED,ID=7,HP=1
                        82136 TSF:MSG:SEND,0-0-7-7,s=255,c=3,t=25,pt=1,l=1,sg=0,ft=0,st=OK:1
                        82149 TSF:MSG:READ,7-7-0,s=255,c=3,t=15,pt=6,l=2,sg=0:0100
                        82156 TSF:MSG:SEND,0-0-7-7,s=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=OK:0100
                        82163 TSF:MSG:READ,7-7-0,s=255,c=0,t=17,pt=0,l=5,sg=0:2.3.2
                        82171 TSF:MSG:READ,7-7-0,s=255,c=3,t=6,pt=1,l=1,sg=0:0
                        82180 GWT:TSA:ETH OK
                        82184 GWT:RFC:MSG=7;255;3;0;6;M
                        82189 TSF:MSG:SEND,0-0-7-7,s=255,c=3,t=6,pt=0,l=1,sg=0,ft=0,st=OK:M
                        82196 TSF:MSG:READ,7-7-0,s=255,c=3,t=11,pt=0,l=12,sg=0:Energy Meter
                        82205 TSF:MSG:READ,7-7-0,s=255,c=3,t=12,pt=0,l=5,sg=0:2.3.2
                        82213 TSF:MSG:READ,7-7-0,s=1,c=0,t=13,pt=0,l=0,sg=0:
                        82224 TSF:MSG:READ,7-7-0,s=255,c=3,t=26,pt=1,l=1,sg=0:2
                        82233 TSF:MSG:SEND,0-0-7-7,s=255,c=3,t=27,pt=1,l=1,sg=0,ft=0,st=OK:1
                        82241 TSF:MSG:READ,7-7-0,s=1,c=2,t=24,pt=0,l=0,sg=0:
                        102202 TSF:MSG:READ,7-7-0,s=1,c=2,t=24,pt=0,l=0,sg=0:
                        110822 TSF:MSG:READ,2-2-0,s=1,c=1,t=0,pt=7,l=5,sg=0:22.1
                        122153 TSF:MSG:READ,7-7-0,s=1,c=2,t=24,pt=0,l=0,sg=0:
                        The Sketch of GW looks like:
                         * Copyright (C) 2013-2019 Sensnology AB
                         * Full contributor list: https://github.com/mysensors/MySensors/graphs/contributors
                         * Version 1.0 - Henrik Ekblad
                         * Contribution by a-lurker and Anticimex
                         * LED purposes:
                         * - RX (green) - blink fast on radio message received. In inclusion mode will blink fast only on presentation received
                         * - ERR (red) - fast blink on error during transmission error or receive crc error
                        #define MY_GATEWAY_W5100
                        //#define MY_W5100_SPI_EN 4
                        // radio on the same spi bus.
                        #define MY_SOFTSPI
                        #ifndef MY_RF24_CE_PIN
                        #define MY_RF24_CE_PIN 5
                        #ifndef MY_RF24_CS_PIN
                        #define MY_RF24_CS_PIN 6
                        // Enable UDP communication
                        //#define MY_USE_UDP  // If using UDP you need to set MY_CONTROLLER_IP_ADDRESS or MY_CONTROLLER_URL_ADDRESS below
                        #define MY_IP_ADDRESS 192,168,1,11
                        #define MY_PORT 5003
                        //#define MY_CONTROLLER_URL_ADDRESS "my.controller.org"
                        // Note that most of the Arduino examples use  "DEAD BEEF FEED" for the MAC address.
                        // Enable inclusion mode
                        // Set blinking period
                        // Flash leds on rx/tx/err
                        #define MY_DEFAULT_ERR_LED_PIN 7  // Error led pin
                        #define MY_DEFAULT_RX_LED_PIN  8  // Receive led pin
                        #define MY_DEFAULT_TX_LED_PIN  9  // Transmit led pin
                        #if defined(MY_USE_UDP)
                        #include <EthernetUdp.h>
                        #include <Ethernet.h>
                        • mfalkviddM Offline
                          When looking in the log parser, I notice the following:
                          • At 14924, 34877, 54829, node 7 is requesting data from node 0:
                          	Received Message
                          Sender: 7
                          Last Node: 7
                          Destination: 0
                          Sensor Id: 1
                          Command: REQ
                          Message Type: V_VAR1
                          Payload Type: P_STRING
                          Payload Length: 0
                          Signing: 0
                          Payload:
                          This probably corresponds to this code in the node:
                          My guess is that the node expects this variable to be available at the controller. I don't have much experience with requesting variables so I don't have any good suggestions unfortunately.
                          • The log also shows that the FPAR requests that failed earlier work fine now:
                          Sent Message
                          Sender: 0
                          Last Node: 0
                          Next Node: 7
                          Destination: 7
                          Sensor Id: 255
                          Command: INTERNAL
                          Message Type:I_FIND_PARENT_RESPONSE
                          Payload Type: P_BYTE
                          Payload Length: 1
                          Signing: 0
                          Failed uplink counter: 0
                          Status: OK (OK=success, NACK=no radio ACK received)
                          Payload: 0
                          • J Offline
                            J Offline
                            jocke4u
                            First day of vacation and it is raining = MySensors time :)
                            I brought this power sensor with TSL237 to the office since I suspected some issues with HW. And yes it seems the TSL237 is broken so tested with a new one. The sensor seems to work fine (using a flashlight).
                            But I can't get the reply of the V_VAR1 from the GW.
                            Any idea why?
                            The Sketch:
                            double oldkWh;
                            uint32_t lastSend;
                            	if (!SLEEP_MODE) {
                            			return;
                              Serial.println("### Pulse");
                            	pulseCount++;
                            	attachInterrupt(digitalPinToInterrupt(DIGITAL_INPUT_SENSOR), onPulse, RISING);
                            	if (/*pcReceived &&*/ (SLEEP_MODE || sendTime)) {
                            			Serial.print("### Watt:");
                            			oldWatt = watt;
                            				oldkWh = kWh;
                            		lastSend = now;
                            		lastSend = now;
                            	if (SLEEP_MODE) {
                              Serial.println("### NEW Received message of type: ");
                              Serial.println(message.getType());
                              Serial.println("### Expected: ");
                              Serial.println(V_VAR1);
                            		Serial.println("");
                            		Serial.print("### Received last pulse count value from gw:");
                            		pcReceived = true;
                            Log from serial monitor:
                             __  __       ____
                                    |___/                      2.3.2
                            26 TSM:INIT
                            28 TSF:WUR:MS=0
                            34 TSM:INIT:TSP OK
                            36 TSF:SID:OK,ID=7
                            37 TSM:FPAR
                            962 TSF:MSG:READ,0-0-7,s=255,c=3,t=8,pt=1,l=1,sg=0:0
                            967 TSF:MSG:FPAR OK,ID=0,D=1
                            2050 TSM:FPAR:OK
                            2051 TSM:ID
                            2052 TSM:ID:OK
                            2054 TSM:UPL
                            2057 TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=OK:1
                            2068 TSF:MSG:READ,0-0-7,s=255,c=3,t=25,pt=1,l=1,sg=0:1
                            2073 TSF:MSG:PONG RECV,HP=1
                            2076 TSM:UPL:OK
                            2077 TSM:READY:ID=7,PAR=0,DIS=1
                            2086 TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=OK:0100
                            2094 TSF:MSG:READ,0-0-7,s=255,c=3,t=15,pt=6,l=2,sg=0:0100
                            2106 TSF:MSG:SEND,7-7-0-0,s=255,c=0,t=17,pt=0,l=5,sg=0,ft=0,st=OK:2.3.2
                            2116 TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=6,pt=1,l=1,sg=0,ft=0,st=OK:0
                            2137 TSF:MSG:READ,0-0-7,s=255,c=3,t=6,pt=0,l=1,sg=0:M
                            ### Start Present
                            2166 TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=11,pt=0,l=12,sg=0,ft=0,st=OK:Energy Meter
                            2183 TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=12,pt=0,l=5,sg=0,ft=0,st=OK:2.3.2
                            2193 TSF:MSG:SEND,7-7-0-0,s=1,c=0,t=13,pt=0,l=0,sg=0,ft=0,st=OK:
                            ### End Present
                            2199 MCO:REG:REQ
                            2238 !TSF:MSG:SEND,7-7-0-0,s=255,c=3,t=26,pt=1,l=1,sg=0,ft=0,st=NACK:2
                            2244 TSF:MSG:READ,0-0-7,s=255,c=3,t=27,pt=1,l=1,sg=0:1
                            2249 MCO:PIM:NODE REG=1
                            2252 MCO:BGN:STP
                            ### Start Setup
                            2255 TSF:MSG:SEND,7-7-0-0,s=1,c=2,t=24,pt=0,l=0,sg=0,ft=1,st=OK:
                            ### End Setup
                            2262 MCO:BGN:INIT OK,TSP=1
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            42265 TSF:MSG:SEND,7-7-0-0,s=1,c=1,t=17,pt=5,l=4,sg=0,ft=0,st=OK:2263
                            ### Watt:2263
                            42276 TSF:MSG:SEND,7-7-0-0,s=1,c=1,t=24,pt=5,l=4,sg=0,ft=0,st=OK:7
                            42290 TSF:MSG:SEND,7-7-0-0,s=1,c=1,t=18,pt=7,l=5,sg=0,ft=0,st=OK:0.0070
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            ### Pulse
                            62271 TSF:MSG:SEND,7-7-0-0,s=1,c=1,t=17,pt=5,l=4,sg=0,ft=0,st=OK:2103
                            ### Watt:2103
                            62279 TSF:MSG:SEND,7-7-0-0,s=1,c=1,t=24,pt=5,l=4,sg=0,ft=0,st=OK:19
                            62290 TSF:MSG:SEND,7-7-0-0,s=1,c=1,t=18,pt=7,l=5,sg=0,ft=0,st=OK:0.0190
                            Screenshot from MYSController
                            • S Offline
                              Sasquatch
                              wrote on last edited by Sasquatch
                              V_Var1 is variable(your total pulses) stored in the controller - HomeAssistant, Domoticz etc....
                              Assuming you have controller shut down you have to send that value from MYSController.
                              This request will be fulfilled by controller after you configure it to use node's 7 child 1
                              • S Sasquatch
                                J Offline
                                J Offline
                                jocke4u
                                @Sasquatch Thanks, it was a connection issue with HomeAssistant to MySensors GW.
                                Now it is time to clean up the sketch and put it to operation again.
                                Also thanks you other guys that have been helpful @mfalkvidd @Yveaux @niclas
                                12.0k
