  3. MQTT Gateway: Add a confirmation/acknowledgement to the publish topic upon setting via subscribe topic.
11 Posts 4 Posters 3.2k Views 4 Watching
  • B Offline
    B Offline
    Brian Morris
    Essentially right now, if i turn on a light/fan/binary/etc. over MQTT by using my in topic, it does what it is supposed to. But there is no output on the out topic to confirm to the Home Automation controller, (Home Assistant in this case), that the state was changed. I have to use optimistic mode, which does not help me if i want to know if the equipment is on/off. So after receive of a change via MQTT, send a update of the current status on the out topic.
    • B Brian Morris
      Welcome to the MySensors community @Brian-Morris. Can't you just send a reply after switching the output? See https://www.mysensors.org/download/sensor_api_20#sending-data
      B 1 Reply Last reply
        B Offline
        B Offline
        Brian Morris
        wrote on last edited by Brian Morris
        @mfalkvidd I did not think of that That should definitely work. I will give it a shot. Thanks!
        Also for the record, I was thinking of a feature request globally. MySensors already does the acknowledgements in its own protocol, could be cool to do it with MQTT as well.
        • B Brian Morris
          @Brian-Morris a global feature could be nice. To my knowledge, the current protocol does not support sending ack to a controller but maybe it can be added.
          • mfalkviddM Offline
            btw, it looks like the dimmable led example already does what you're requesting: https://www.mysensors.org/build/dimmer
            • B Offline
              B Offline
              Brian Morris
              @mfalkvidd that did not seem to work. It causes a loop where it sends the state back and forth, changing the value and switch state. This topic could be moved to troubleshooting if someone can do so as well.
                if (message.isAck()) {
                   // Change relay state
                   state = message.getBool();
                   // Store state in eeprom
                   saveState(CHILD_ID, state);
                   send(msg.set(state?false:true), true);
                   if (state == true){
                     colorSet(strip.Color(0, 255, 0));  // Green
                     colorSet(strip.Color(255, 255, 255));  // White
              Y 1 Reply Last reply
              • B Brian Morris
                     if (state == true){
                Y Offline
                Y Offline
                @Brian-Morris you can probably fix the looping by changing the second if in an else if.
                Now the ack message can/will trigger a new message...
                • B Offline
                  B Offline
                  Brian Morris
                  Changed to the following. Still no change. Still loops.
                    } else if (message.type == V_LIGHT) {
                       if (state == true){
                  • B Brian Morris
                         if (state == true){
                    @Brian-Morris I think
                    should be moved to inside the else if.
                    If that doesn't help, could you please post a debug log from the node and the gateway, with your complete sketch? Easier to get all the cards on the table :)
                    • B Offline
                      B Offline
                      Brian Morris
                      with it here, I attempt to turn on the switch by sending a payload of "1" to turn on the switch via MQTT. The gateway receives it, sends it to the node, where the node reverses it, sends it back 0. I can press the button many times over, stays 0/off.
                           send(msg.set(state?false:true));
                           if (state == true){
                      Node DEBUG
                      0 MCO:BGN:INIT REPEATER,CP=RNNRA--,VER=2.1.1
                      4 TSM:INIT
                      4 TSF:WUR:MS=0
                      12 TSM:INIT:TSP OK
                      14 TSM:INIT:STATID=80
                      16 TSF:SID:OK,ID=80
                      18 TSM:FPAR
                      55 TSF:MSG:SEND,80-80-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                      557 TSF:MSG:READ,0-0-80,s=255,c=3,t=8,pt=1,l=1,sg=0:0
                      563 TSF:MSG:FPAR OK,ID=0,D=1
                      2062 TSM:FPAR:OK
                      2062 TSM:ID
                      2064 TSM:ID:OK
                      2066 TSM:UPL
                      2070 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=OK:1
                      2076 TSF:MSG:READ,0-0-80,s=255,c=3,t=25,pt=1,l=1,sg=0:1
                      2082 TSF:MSG:PONG RECV,HP=1
                      2086 TSM:UPL:OK
                      2088 TSM:READY:ID=80,PAR=0,DIS=1
                      2127 !TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=NACK:0100
                      4136 TSF:MSG:SEND,80-80-0-0,s=255,c=0,t=18,pt=0,l=5,sg=0,ft=1,st=OK:2.1.1
                      4147 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=6,pt=1,l=1,sg=0,ft=0,st=OK:0
                      6158 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=11,pt=0,l=22,sg=0,ft=0,st=OK:Living Room Fan Switch
                      6170 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=12,pt=0,l=3,sg=0,ft=0,st=OK:1.5
                      6178 TSF:MSG:SEND,80-80-0-0,s=1,c=0,t=3,pt=0,l=0,sg=0,ft=0,st=OK:
                      6187 MCO:REG:REQ
                      6191 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=26,pt=1,l=1,sg=0,ft=0,st=OK:2
                      6197 TSF:MSG:READ,0-0-80,s=255,c=3,t=27,pt=1,l=1,sg=0:1
                      6203 MCO:PIM:NODE REG=1
                      6207 MCO:BGN:STP
                      8660 MCO:BGN:INIT OK,TSP=1
                      170743 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=0,l=1,sg=0:1
                      170752 TSF:MSG:SEND,80-80-0-0,s=1,c=1,t=2,pt=1,l=1,sg=0,ft=0,st=OK:0
                      Incoming change for sensor:1, New status: 1
                      173297 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=0,l=1,sg=0:1
                      173305 TSF:MSG:SEND,80-80-0-0,s=1,c=1,t=2,pt=1,l=1,sg=0,ft=0,st=OK:0
                      294385 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=1,l=1,sg=0:0
                      294391 TSF:MSG:ACK
                      GW
                      0;255;3;0;9;MCO:BGN:STP
                      IP: 10.200.62.10
                      0;255;3;0;9;MQTT connected
                      0;255;3;0;9;Sending message on topic: /mysgw1-out/0/255/0/0/18
                      0;255;3;0;9;Sending message on topic: /mysgw1-out/0/255/3/0/11
                      0;255;3;0;9;Sending message on topic: /mysgw1-out/0/255/3/0/12
                      0;255;3;0;9;Sending message on topic: /mysgw1-out/0/10/0/0/3
                      pm open,type:2 0
                      0;255;3;0;9;Message arrived on topic: /mysgw1-in/80/1/1/0/2
                      0;255;3;0;9;TSF:MSG:SEND,0-0-80-80,s=1,c=1,t=2,pt=0,l=1,sg=0,ft=0,st=OK:1
                      0;255;3;0;9;TSF:MSG:READ,80-80-0,s=1,c=1,t=2,pt=1,l=1,sg=0:0
                      0;255;3;0;9;Sending message on topic: /mysgw1-out/80/1/1/0/2
                      Incoming change for sensor:1, New status: 0
                      0;255;3;0;9;TSF:MSG:ACK REQ
                      0;255;3;0;9;TSF:MSG:SEND,0-0-80-80,s=1,c=1,t=2,pt=1,l=1,sg=0,ft=0,st=OK:0
                      moving it to here, the physical switch stays at 1 no matter how many times you click. Controller to MQTT works and the switch works, but still no response back to the controller.
                           if (state == true){
                      Node
                      4 TSM:INIT
                      4 TSF:WUR:MS=0
                      12 TSM:INIT:TSP OK
                      16 TSF:SID:OK,ID=80
                      18 TSM:FPAR
                      704 TSF:MSG:READ,0-0-80,s=255,c=3,t=8,pt=1,l=1,sg=0:0
                      708 TSF:MSG:FPAR OK,ID=0,D=1
                      2062 TSM:FPAR:OK
                      2062 TSM:ID
                      2064 TSM:ID:OK
                      2066 TSM:UPL
                      2084 TSF:MSG:READ,0-0-80,s=255,c=3,t=25,pt=1,l=1,sg=0:1
                      2091 TSF:MSG:PONG RECV,HP=1
                      2093 TSM:UPL:OK
                      2095 TSM:READY:ID=80,PAR=0,DIS=1
                      2101 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=OK:0100
                      2109 TSF:MSG:READ,0-0-80,s=255,c=3,t=15,pt=6,l=2,sg=0:0100
                      2117 TSF:MSG:SEND,80-80-0-0,s=255,c=0,t=18,pt=0,l=5,sg=0,ft=0,st=OK:2.1.1
                      2129 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=6,pt=1,l=1,sg=0,ft=0,st=OK:0
                      4141 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=11,pt=0,l=22,sg=0,ft=0,st=OK:Living Room Fan Switch
                      4153 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=12,pt=0,l=3,sg=0,ft=0,st=OK:1.5
                      4161 TSF:MSG:SEND,80-80-0-0,s=1,c=0,t=3,pt=0,l=0,sg=0,ft=0,st=OK:
                      4169 MCO:REG:REQ
                      4173 TSF:MSG:SEND,80-80-0-0,s=255,c=3,t=26,pt=1,l=1,sg=0,ft=0,st=OK:2
                      4239 TSF:MSG:READ,0-0-80,s=255,c=3,t=27,pt=1,l=1,sg=0:1
                      4245 MCO:PIM:NODE REG=1
                      4247 MCO:BGN:STP
                      6701 MCO:BGN:INIT OK,TSP=1
                      ▒&L▒TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=0,l=1,sg=0:1
                      M▒TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=0,l=1,sg=0:▒2▒Ɂ▒▒▒ͽ▒▒brU▒▒.]X▒us: 1
                      54794 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=1,l=1,sg=0:1
                      54800 TSF:MSG:ACK
                      54806 TSF:MSG:SEND,80-80-0-0,s=1,c=1,t=2,pt=1,l=1,sg=0,ft=0,st=OK:1
                      96909 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=0,l=1,sg=0:0
                      99350 TSF:MSG:SEND,80-80-0-0,s=1,c=1,t=2,pt=1,l=1,sg=0,ft=0,st=OK:1
                      99360 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=1,l=1,sg=0:1
                      99366 TSF:MSG:ACK
                      99371 TSF:MSG:SEND,80-80-0-0,s=1,c=1,t=2,pt=1,l=1,sg=0,ft=0,st=OK:1
                      101445 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=1,l=1,sg=0:1
                      101451 TSF:MSG:ACK
                      101455 TSF:MSG:SEND,80-80-0-0,s=1,c=1,t=2,pt=1,l=1,sg=0,ft=0,st=OK:1
                      113451 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=0,l=1,sg=0:0
                      118966 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=0,l=1,sg=0:1
                      121210 TSF:MSG:READ,0-0-80,s=1,c=1,t=2,pt=0,l=1,sg=0:0
                      GW
                      IP: 10.200.62.10
                      pm open,type:2 0
                      0;255;3;0;9;TSF:MSG:SEND,0-0-80-80,s=1,c=1,t=2,pt=0,l=1,sg=0,ft=0,st=OK:0
                      0;255;3;0;9;TSF:MSG:READ,80-80-0,s=1,c=1,t=2,pt=1,l=1,sg=0:1
                      0;255;3;0;9;TSF:MSG:SEND,0-0-80-80,s=1,c=1,t=2,pt=1,l=1,sg=0,ft=0,st=OK:1
                      Whole code
                      #define MY_NODE_ID 80
                      #define MY_REPEATER_FEATURE
                      #include <Arduino.h>
                      #include <Adafruit_NeoPixel.h>
                      #include <Ticker.h>
                      #define RELAY_PIN  2  // Arduino Digital I/O pin number for relay
                      #define BUTTON_PIN  3  // Arduino Digital I/O pin number for button
                      #define RGB_CHILD_ID 2   // Id of the sensor child
                      #define RELAY_ON 1
                      #define RELAY_OFF 0
                      #define NUMPIXELS 1
                      #define PIXELPIN 4
                      #define BRIGHTNESS 10
                      Adafruit_NeoPixel strip = Adafruit_NeoPixel(NUMPIXELS, PIXELPIN, NEO_GRB + NEO_KHZ800);
                      long RGB_values[3] = {0,0,0};
                      Bounce debouncer = Bounce();
                      int oldValue=0;
                      bool state;
                        // Setup the button
                        pinMode(BUTTON_PIN,INPUT);
                        // Activate internal pull-up
                        debouncer.attach(BUTTON_PIN);
                        debouncer.interval(5);
                        pinMode(RELAY_PIN, OUTPUT);
                        state = loadState(CHILD_ID);
                        strip.begin();
                        strip.setBrightness(BRIGHTNESS);
                        strip.show(); // Update the strip, to start they are all 'off'
                        startupSequence();
                      void presentation()  {
                        sendSketchInfo("Living Room Fan Switch", "1.5");
                        present(CHILD_ID, S_LIGHT);
                        //present(RGB_CHILD_ID, S_RGB_LIGHT);
                      *  Example on how to asynchronously check for new messages from gw
                        debouncer.update();
                        // Get the update value
                        int value = debouncer.read();
                        if (value != oldValue && value==0) {
                            send(msg.set(state?false:true), true); // Send new state and request ack back
                            if (value == true){
                        oldValue = value;
                           if (state == true){
                      void startupSequence(){
                        colorSet(strip.Color(255, 0, 0));  // Red
                        delay(350);
                        colorSet(strip.Color(255, 255, 0));  // Yellow
                        delay(350);
                        delay(350);
                        colorSet(strip.Color(0, 0, 0));  // Black
                        delay(350);
                        delay(350);
                        delay(350);
                        delay(350);
                      void colorSet(uint32_t color)
                          for (int i = 0; i < strip.numPixels(); i++)
                              strip.setPixelColor(i, color);
                          strip.show();
                      • B Brian Morris
                             if (state == true){
                        Node DEBUG
                        4 TSM:INIT
                        4 TSF:WUR:MS=0
                        12 TSM:INIT:TSP OK
                        16 TSF:SID:OK,ID=80
                        18 TSM:FPAR
                        2062 TSM:FPAR:OK
                        2062 TSM:ID
                        2064 TSM:ID:OK
                        2066 TSM:UPL
                        2086 TSM:UPL:OK
                        6187 MCO:REG:REQ
                        6207 MCO:BGN:STP
                        294391 TSF:MSG:ACK
                        GW
                        IP: 10.200.62.10
                        pm open,type:2 0
                             if (state == true){
                        Node
                        4 TSM:INIT
                        4 TSF:WUR:MS=0
                        12 TSM:INIT:TSP OK
                        16 TSF:SID:OK,ID=80
                        18 TSM:FPAR
                        2062 TSM:FPAR:OK
                        2062 TSM:ID
                        2064 TSM:ID:OK
                        2066 TSM:UPL
                        2093 TSM:UPL:OK
                        4169 MCO:REG:REQ
                        4247 MCO:BGN:STP
                        54800 TSF:MSG:ACK
                        99366 TSF:MSG:ACK
                        101451 TSF:MSG:ACK
                        GW
                        IP: 10.200.62.10
                        pm open,type:2 0
                        Whole code
                        #include <Ticker.h>
                        #define RELAY_ON 1
                        #define RELAY_OFF 0
                        #define NUMPIXELS 1
                        #define PIXELPIN 4
                        int oldValue=0;
                        bool state;
                          // Setup the button
                          strip.begin();
                          startupSequence();
                          debouncer.update();
                              if (value == true){
                          oldValue = value;
                             if (state == true){
                          delay(350);
                          delay(350);
                          delay(350);
                          delay(350);
                          delay(350);
                          delay(350);
                          delay(350);
                            strip.show();
                        martinhjelmareM Offline
                        martinhjelmare
                        @Brian-Morris
                        Don't invert the state before you send it back to the controller . Ie this part:
                        state?false:true
                        should be:
                        state?true:false