  3. Problem with Wind Speed sensor
53 Posts 6 Posters 19.4k Views 7 Watching
  • rnollenR
    rnollenR
    rnollen
    @AWI Thanks, I will give it a try. Today I also received some additional info. The device is a NPN model. Type 12CM, according to the supplier it is 12 pulses for 1m/s per second. But the manual says that this model is 10 pulses for 1m/s.
    So basically I could now connect the device as NPN, only I need to find out how :)
    AWIA 1 Reply Last reply
    • rnollenR rnollen
      AWIA
      AWIA
      AWI
      @rnollen good news. Npn needs a pull-up so the sketch above should be able to do it. It uses the internal pull-up of the Arduino. I am curious to the outcome.
      rnollenR 1 Reply Last reply
      • AWIA AWI
        rnollenR
        rnollenR
        rnollen
        wrote on last edited by rnollen
        #22
        It does not work entirely correct I think. In the serial Monitor I see "Inf" as outcome of the sketch :( Don't see exactly where that is coming from :)
        Maybe something wrong with the wiring? I Attached the 12V DC to red and blue. The Yellow, connected it to the breadboard and a cable from the D7 also to this connection. I took a 4.7K resistor, connected also to this group and the other side of this resistor I connected to the 5V of the Arduino? Is that correct?
        When I remove the resistor: then this is my outcome of the sketch:
        12.82
        inf
        inf
        3.36
        1.88
        55.06
        inf
        37037.03
        inf
        333333.34
        30.95
        17.43
        inf
        142857.14
        inf
        125000.00
        500000.00
        500000.00
        90909.10
        500000.00
        39.47
        inf
        250000.00
        500000.00
        inf
        20.54
        45.67
        58823.53
        inf
        9.88
        inf
        inf
        9.17
        inf
        Then I got some numbers, but what they mean :) The very high numbers are when rotating..
        • rnollenR rnollen
          12.82
          inf
          inf
          3.36
          1.88
          55.06
          inf
          37037.03
          inf
          333333.34
          30.95
          17.43
          inf
          142857.14
          inf
          125000.00
          500000.00
          500000.00
          90909.10
          500000.00
          39.47
          inf
          250000.00
          500000.00
          inf
          20.54
          45.67
          58823.53
          inf
          9.88
          inf
          inf
          9.17
          inf
          AWIA
          AWIA
          AWI
          wrote on last edited by AWI
          #23
          @rnollen the "inf" means infinite and is caused by a 0 division. You can try to remove the line starting with 'float' and print the time values.
          I assume you changed the anemometer pin in the sketch to d7...?
          And connected the gnd of 12v and 5v together?
          • AWIA AWI
            rnollenR
            rnollenR
            rnollen
            I have did some additional testing. The DC12 is wrong I think, when I use that then the whole sketch does not give any values back. Now used the 5V of the arduino, then I got something readings using this sketch. I have added some additional serial print lines for logging. But when times are zero, then the frequency is INF and that happens when I don't rotate, so that looks OK I think
            Timeon: 0
            Timeoff: 0
            TimePeriod: 0
            Frequency: inf
            Timeon: 0
            Timeoff: 87951
            TimePeriod: 87951
            Frequency: 11.37
            Timeon: 24222
            Timeoff: 22899
            TimePeriod: 47121
            Frequency: 21.22
            Timeon: 24960
            Timeoff: 27680
            TimePeriod: 52640
            Frequency: 19.00
            Timeon: 27545
            Timeoff: 28273
            TimePeriod: 55818
            Frequency: 17.92
            Timeon: 63310
            Timeoff: 0
            TimePeriod: 63310
            Frequency: 15.80
            The serial.print lines:
            Serial.print("Timeon: ");
            Serial.println(timeon);
            Serial.print("Timeoff: ");
            Serial.println(timeoff);
            Serial.print("TimePeriod: ");
            Serial.println(timePeriod);
            Serial.print("Frequency: ");
            Serial.println(frequency);
            But any idea, because I am still lost don't know exactly what the conclusion of this is :)
            AWIA 2 Replies Last reply
            • rnollenR rnollen
              Timeon: 0
              Timeoff: 0
              TimePeriod: 0
              Frequency: inf
              Timeon: 0
              Timeoff: 87951
              TimePeriod: 87951
              Frequency: 11.37
              Timeon: 24222
              Timeoff: 22899
              TimePeriod: 47121
              Frequency: 21.22
              Timeon: 24960
              Timeoff: 27680
              TimePeriod: 52640
              Frequency: 19.00
              Timeon: 27545
              Timeoff: 28273
              TimePeriod: 55818
              Frequency: 17.92
              Timeon: 63310
              Timeoff: 0
              TimePeriod: 63310
              Frequency: 15.80
              AWIA
              AWIA
              AWI
              @rnollen this looks much better. You get frequencies in the 10 to 20 range when rotating. The inf when you're not rotating are caused by timer overflow so nothing wrong there.
              Now it is time for a more dedicated measurement. Basically replace the standard arduino routines with your own version. It is middle of the night here so I have to leave it for tomorrow...
              • rnollenR rnollen
                Timeon: 0
                Timeoff: 0
                TimePeriod: 0
                Frequency: inf
                Timeon: 0
                Timeoff: 87951
                TimePeriod: 87951
                Frequency: 11.37
                Timeon: 24222
                Timeoff: 22899
                TimePeriod: 47121
                Frequency: 21.22
                Timeon: 24960
                Timeoff: 27680
                TimePeriod: 52640
                Frequency: 19.00
                Timeon: 27545
                Timeoff: 28273
                TimePeriod: 55818
                Frequency: 17.92
                Timeon: 63310
                Timeoff: 0
                TimePeriod: 63310
                Frequency: 15.80
                AWIA
                AWIA
                AWI
                @rnollen time for "Take 2" I created it in Codebender to make sure it compiles. Could not test functionality yet.
                The "take 2" code implements a non-blocking measurement of the frequency of the anemometer (pulses per second). It should be safe for overflow.
                Take 3 could be to translate it to m/s windspeed according to your type of anemometer and finally:
                Take 4 MySensors' ise it!!
                https://codebender.cc/sketch:347690
                • rnollenR
                  rnollenR
                  rnollen
                  #27
                  @AWI Hmm.. I see this:
                  1000.00
                  1000.00
                  1000.00
                  1000.00
                  1000.00
                  1000.00
                  1000.00
                  1000.00
                  1000.00
                  500.00
                  1000.00
                  0.00
                  inf
                  1000.00
                  0.00
                  0.00
                  Don't think that this is correct right? Am I doing something wrong, or does these numbers say anything to you :)
                  • rnollenR rnollen
                    1000.00
                    1000.00
                    1000.00
                    1000.00
                    1000.00
                    1000.00
                    1000.00
                    1000.00
                    1000.00
                    500.00
                    1000.00
                    0.00
                    inf
                    1000.00
                    0.00
                    0.00
                    AWIA
                    AWIA
                    AWI
                    #28
                    @rnollen was a short night... :sweat:
                    Forgot the return lastFrequencyI changed the sketch in last post. No guarantee that it works, don't have the hardware.
                    • rnollenR
                      rnollenR
                      rnollen
                      @AWI Sorry for the late reply, I got the flu :( But did test the sketch, but I got the same results basically.. Mostly 1000, inf and sometimes a 500? So what can be wrong here?
                      Thanks for all you're efforts so far!! Really appreciate it :)
                      • rnollenR rnollen
                        AWIA
                        AWIA
                        AWI
                        #30
                        @rnollen No problem, I hope you recovered well. Haven't looked at the sketch until now and discovered that I must have been suffering from something too... I added a missing line but still can't test it. Please give it a try..
                        • rnollenR
                          rnollenR
                          rnollen
                          @AWI I am still ill, while doing this :) Hopefully tomorrow will be better, Hahaha.. :)
                          But, the results looks promising and OK I guess :)
                          8.13
                          10.87
                          14.08
                          20.00
                          27.78
                          23.81
                          25.64
                          10.75
                          0.00
                          1.81
                          12.66
                          11.49
                          10.75
                          10.00
                          9.35
                          8.85
                          8.33
                          7.87
                          It's 0 when I am not turning it around, so that is OK. Low number, when rotating it slowly. High number when rotating it fast :)
                          • rnollenR rnollen
                            8.13
                            10.87
                            14.08
                            20.00
                            27.78
                            23.81
                            25.64
                            10.75
                            0.00
                            1.81
                            12.66
                            11.49
                            10.75
                            10.00
                            9.35
                            8.85
                            8.33
                            7.87
                            AWIA
                            AWIA
                            AWI
                            @rnollen take care.. This is how it should be (with the anemometer) I will post the MySensors version tomorrow (need some sleep now)
                            • AWIA AWI
                              rnollenR
                              rnollenR
                              rnollen
                              #33
                              @AWI ..Awesome ☺ Thanks so far ☺
                              • rnollenR rnollen
                                AWIA
                                AWIA
                                AWI
                                #34
                                @rnollen I made the sketch but forgot to post it... Have a look here
                                https://codebender.cc/sketch:347770
                                I does not compile in codebender.cc yet because of v2 MySensor but it should in the IDE.
                                Have fun and let me know the results
                                TheoLT 1 Reply Last reply
                                • AWIA AWI
                                  TheoLT
                                  TheoLT
                                  TheoL
                                  @AWI Great job. I'm planning to make my own anemometer, just because it's fun to do. And was already thinking about the problems that might occur. Hardware wise it's easy. Just use a hall sensor to detect pulses and a rotating magnet.
                                  When the diameter of the magnet will be around 9cm, the magnet will reach the Hall sensor within 3ms or less if there's a Hurricane. That can be a problem because the sensor might think that the magnet isn't moving.
                                  Because of that I was thinking about counting the pulses in a interrupt handler (pin 2 or 3) . And just let the loop periodically read the values and send them to the gateway if necessary.
                                  Now comes my question for you. I was thinking of using some kind of decade counter IC. And let the IC handle the pulse counting. That way I only have to read and reset the counter IC. Do you happen to know a good counter IC that I can connect to the Arduino? It would make the project much easier.
                                  • TheoLT TheoL
                                    AWIA
                                    AWIA
                                    AWI
                                    @TheoL I have to dig in my ancient history to find hardware for that purpose. An interrupt routine would be much easier and fast enough. (would be take 4 of this thread :smile:)
                                    • AWIA AWI
                                      TheoLT
                                      TheoLT
                                      TheoL
                                      @AWI I know it's ancient stuff ;-) But very reliable. Maybe something like this? THE 4017B DECADE COUNTER But I don't know I it could handle the speed?
                                      I'm also thinking about replacing the hall sensor with an infrared pulse sensor. It has a shorter on time than a magnet with a hall sensor. At least that's what I'm thinking ;-)
                                      • rnollenR
                                        rnollenR
                                        rnollen
                                        #38
                                        @AWI Thanks for the sketch, but I still run in some issues. When i download the sketch, I got an error with the line "#include <MySensor.h> ". The strange thing is, everything seems to be OK, but it say it cannot be found. When I copy/paste the lines from a different sketch, it does work correct?? The strange thing is, I don't see difference. Maybe something wrong with a font or some sort?
                                        But, then the issues really start. All the Mysensors stuff, is not recognized (e.g.send). I was able to fix that, copying from other sketches and add gw. before everything. In the serial monitor it then looks OK. That seems for me to solve the issues on that side.
                                        But finally, in domoticz, it does not work then :( Everything is looking perfect, I see the sensors appear, but no new device is added). I saw a topic on the domoticz forum where the same thing happened :) and where you also replyed in: https://www.domoticz.com/forum/viewtopic.php?f=42&t=11490&p=82522&hilit=wind#p82522
                                        Tried some various stuff, but no result sofar
                                        Any idea?
                                        • rnollenR rnollen
                                          Any idea?
                                          AWIA
                                          AWIA
                                          AWI
                                          @rnollen it seems you are running into the changes related to the new development syntax. I wrote the sketch with the development version.. There are many threads on the forum discussing that so I won't repeat it here.
                                          The sensor not appearing I remember from another wind sensor discussion. Domoticz builds it when a few wind types are present. You can add a wind direction dummy (presentation is already in the sketch, commented) and send a "0" degrees value.