  2. Announcements
  3. 💬 Power Meter Pulse Sensor
183 Posts 40 Posters 92.4k Views 37 Watching
    wrote on last edited by gohan
    #140
    Yes, could be that a simple debounce could do the trick but I'll have to look deeper into it. @Yveaux what do you think?
      @xydix Could you try to increase the 10000L to 100000L interval in the OnPulse function and see if it works without the capacitor?
      • U
        U
        user2684
        I tried to build something similar and it is working nicely, thanks for sharing the idea! However, I've noticed the light sensor (alone) consumes 1mA constantly which is quite a lot when used for a battery powered project. Even if I report to the controller once per hour (summing up the power consumption along the way), still the light sensor needs to be always on, meaning I'd probably need to replace batteries after a month or so. Is there any workaround or alternative sensor which I can use or am I doing something completely wrong? Thanks
        C 1 Reply Last reply
        • U user2684
          C
          C
          cstewy
          @user2684 I had the same issue when I built this with a standalone atmega328p running on 2x AA's. I set it up with wake on interrupt from the It was constantly drawing 1.6mA to power the tsl257 to detect the flashes. My target was 1+ years on 2 x AA's. My solution to achieve this was to sleep for 125ms, wake up, send power to tsl257 to check light state (on/off), if it changed from previous reading then there was a pulse (well half pulse). By measuring every 125ms I can guarantee to capture fast pulses up to 14.4kW. (3600000/125)/2. It is 20kW max draw for residential in my country. Now:
          Average mA Consumption Sleep 0.1
          Average mA Consumption Wake 0.064516129
          Average mA Consumption Transmit 0.002916667
          Battery Life (2xAAs) = 1.7 years
          U 1 Reply Last reply
          • C cstewy
            U
            U
            user2684
            @cstewy many thanks and very interesting. You basically saying it consumes less by waking up every 125ms rather than being asleep but with the sensor eating up current continuously. Definitely worth trying thanks! Meanwhile I've reduced the number of radio transmission and the batteries lasted for a couple of months but still is not ideal. Thanks! I'll try and report back
            • A
              artipi
              Hello, i'm stuck with this sensor, because no Interrupt is really working. I've cut down the code to this:
               * Version 1.0 - Henrik Ekblad
               * This sketch provides an example how to implement a LM393 PCB
               * Use this sensor to measure kWh and Watt of your house meter
               * You need to set the correct pulsefactor of your meter (blinks per kWh).
               * The sensor starts by fetching current kWh value from gateway.
               * Reports both kWh and Watt back to gateway.
               * Unfortunately millis() won't increment when the Arduino is in
               * sleepmode. So we cannot make this sensor sleep if we also want
               * to calculate/report watt value.
               * http://www.mysensors.org/build/pulse_power
              // Enable debug prints
              //#define MY_RADIO_NRF24
              //#define MY_RADIO_NRF5_ESB
              //#define MY_RADIO_RFM95
              //#include <MySensors.h>
              #define DIGITAL_INPUT_SENSOR 2  // The digital input you attached your light sensor.  (Only 2 and 3 generates interrupt!)
              #define PULSE_FACTOR 500       // Number of blinks per of your meter
              #define SLEEP_MODE false        // Watt value can only be reported when sleep mode is false.
              #define MAX_WATT 1000000          // Max watt value to report. This filters outliers.
              #define CHILD_ID 10             // Id of the sensor child
              uint32_t SEND_FREQUENCY =
                  15000; // Minimum time between send (in milliseconds). We don't want to spam the gateway.
              double ppwh = ((double)PULSE_FACTOR)/1000; // Pulses per watt hour
              bool pcReceived = true;
              volatile uint32_t pulseCount = 0;
              volatile uint32_t lastBlink = 0;
              volatile uint32_t watt = 0;
              uint32_t oldPulseCount = 0;
              uint32_t oldWatt = 0;
              double oldkWh;
              uint32_t lastSend;
              //MyMessage wattMsg(CHILD_ID,V_WATT);
              //MyMessage kWhMsg(CHILD_ID,V_KWH);
              //MyMessage pcMsg(CHILD_ID,V_VAR1);
                Serial.begin(9600);
                Serial.println("Start setup");
                //request(CHILD_ID, V_VAR1);
                pinMode(DIGITAL_INPUT_SENSOR,INPUT_PULLUP);
                attachInterrupt(digitalPinToInterrupt(DIGITAL_INPUT_SENSOR), onPulse, RISING);
                lastSend=millis();
                Serial.println("Start setup: last sent: ");
                pinMode(LED_BUILTIN, OUTPUT);
                digitalWrite(LED_BUILTIN, LOW);
                //sendSketchInfo("Energy Meter", "1.3");
                //present(CHILD_ID, S_POWER);
              void onPulse()
                Serial.println("onPulse:");
                digitalWrite(LED_BUILTIN, HIGH);   // turn the LED on (HIGH is the voltage level)
                delay(1000);                       // wait for a second
                digitalWrite(LED_BUILTIN, LOW);    // turn the LED off by making the voltage LOW
                delay(1000);
                pulseCount++;
                Serial.println("pulseCount:");
              The Problem ist, that only on Start the interrupt ist working once, but no LED blinks.
              Can someone help?
              • A artipi
                double oldkWh;
                uint32_t lastSend;
                  Serial.begin(9600);
                  lastSend=millis();
                void onPulse()
                  delay(1000);
                  pulseCount++;
                Can someone help?
                #146
                @artipi using Serial.print and delay from within an interrupt service routine will mess things up. Interrupt service routines must be executed quickly.
                From https://www.arduino.cc/reference/en/language/functions/external-interrupts/attachinterrupt/:
                Since delay() requires interrupts to work, it will not work if called inside an ISR.
                You need to do the blinking inside loop().
                • A
                  artipi
                  Ah, this explains many things. Thank you, now its working:)!
                  • alowhumA
                    alowhumA
                    alowhum
                    @artipi can you share your code?
                    • A
                      artipi
                      @alowhum: Its the original code. Nothing changed. I've only made some tests with my version...
                      • P
                        P
                        patrikr76
                        wrote on last edited by patrikr76
                        #150
                        Hey guys
                        So i am trying to use this sketch with the sleep mode set to true 'cause i need to run it on battery.
                        It works fine running with usb power on it and sleep mode on false.
                        But with sleep mode true i am getting nothing in myscontroller after the initial startup.
                        All i changed is the sleep mode from false to true.
                        Running it on a clone nano with some chinese "flame detector" sensor.
                        Been trying to figure out if it has something to do with how it reports when in sleep mode but it should still report whatever the send frequency is set to right?
                        I was using a tv remote to fake impulses, with seems to work on usb power, but not on battery.
                        Any suggestions?
                        Best regards
                        Patrik
                        • P patrikr76
                          Hey guys
                          Any suggestions?
                          Best regards
                          Patrik
                          #151
                          @patrikr76 just to make sure we are on the same page, could you clarify which sketch you are using? This thread has discussed lots of sketches and it would be a pity if we’re looking at different code :)
                          In any case, the debug log from the node will give the best information on what is happening.
                          It could also be useful to only change one thing. Right now you change sleep mode and switch to battery, right? How does the node behave with sleep mode on, but still running on usb power? How does the node behave with sleep mode off, but running on battery?
                          • P
                            P
                            patrikr76
                            #152
                            @mfalkvidd , you are absolutely right. Let me clarify.
                            I am using the example code that is under build and power meter pulse sensor, updated may 1st, 2018.
                            Running it with "sleep mode = false" it works fine with both usb and battery power, just drains the battery quite fast.
                            Setting it to "sleep mode = true" it doesn't work either on usb or battery power.
                            Here's how the serial monitor looks for the startup phase with sleep mode as true.
                            23:21:24.219 ->  __  __       ____
                            23:21:24.219 -> |  \/  |_   _/ ___|  ___ _ __  ___  ___  _ __ ___
                            23:21:24.219 -> | |\/| | | | \___ \ / _ \ `_ \/ __|/ _ \| `__/ __|
                            23:21:24.219 -> | |  | | |_| |___| |  __/ | | \__ \  _  | |  \__ \
                            23:21:24.219 -> |_|  |_|\__, |____/ \___|_| |_|___/\___/|_|  |___/
                            23:21:24.219 ->         |___/                      2.3.0
                            23:21:24.219 ->
                            23:21:24.219 -> 16 MCO:BGN:INIT NODE,CP=RNNNA---,VER=2.3.0
                            23:21:24.254 -> 25 TSM:INIT
                            23:21:24.254 -> 26 TSF:WUR:MS=0
                            23:21:24.254 -> 33 TSM:INIT:TSP OK
                            23:21:24.254 -> 35 TSF:SID:OK,ID=2
                            23:21:24.254 -> 37 TSM:FPAR
                            73 TSF:MSG:SEND,2-2-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                            201 TSF:MSG:READ,0-0-2,s=255,c=3,t=8,pt=1,l=1,sg=0:0
                            23:21:24.428 -> 205 TSF:MSG:FPAR OK,ID=0,D=1
                            2080 TSM:FPAR:OK
                            23:21:26.306 -> 2081 TSM:ID
                            23:21:26.306 -> 2082 TSM:ID:OK
                            23:21:26.306 -> 2084 TSM:UPL
                            23:21:26.306 -> 2087 TSF:MSG:SEND,2-2-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=OK:1
                            23:21:26.306 -> 2095 TSF:MSG:READ,0-0-2,s=255,c=3,t=25,pt=1,l=1,sg=0:1
                            23:21:26.306 -> 2100 TSF:MSG:PONG RECV,HP=1
                            23:21:26.306 -> 2103 TSM:UPL:OK
                            23:21:26.306 -> 2104 TSM:READY:ID=2,PAR=0,DIS=1
                            23:21:26.306 -> 2109 TSF:MSG:SEND,2-2-0-0,s=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=OK:0100
                            23:21:26.341 -> 2118 TSF:MSG:READ,0-0-2,s=255,c=3,t=15,pt=6,l=2,sg=0:0100
                            23:21:26.341 -> 2125 TSF:MSG:SEND,2-2-0-0,s=255,c=0,t=17,pt=0,l=5,sg=0,ft=0,st=OK:2.3.0
                            23:21:26.341 -> 2134 TSF:MSG:SEND,2-2-0-0,s=255,c=3,t=6,pt=1,l=1,sg=0,ft=0,st=OK:0
                            2203 TSF:MSG:READ,0-0-2,s=255,c=3,t=6,pt=0,l=1,sg=0:M
                            23:21:26.410 -> 2210 TSF:MSG:SEND,2-2-0-0,s=255,c=3,t=11,pt=0,l=12,sg=0,ft=0,st=OK:Energy Meter
                            23:21:26.445 -> 2220 TSF:MSG:SEND,2-2-0-0,s=255,c=3,t=12,pt=0,l=3,sg=0,ft=0,st=OK:1.0
                            23:21:26.445 -> 2228 TSF:MSG:SEND,2-2-0-0,s=1,c=0,t=13,pt=0,l=0,sg=0,ft=0,st=OK:
                            23:21:26.445 -> 2234 MCO:REG:REQ
                            23:21:26.445 -> 2237 TSF:MSG:SEND,2-2-0-0,s=255,c=3,t=26,pt=1,l=1,sg=0,ft=0,st=OK:2
                            2252 TSF:MSG:READ,0-0-2,s=255,c=3,t=27,pt=1,l=1,sg=0:1
                            23:21:26.480 -> 2257 MCO:PIM:NODE REG=1
                            23:21:26.480 -> 2259 MCO:BGN:STP
                            23:21:26.480 -> 2263 TSF:MSG:SEND,2-2-0-0,s=1,c=2,t=24,pt=0,l=0,sg=0,ft=0,st=OK:
                            23:21:26.480 -> 2269 MCO:BGN:INIT OK,TSP=1
                            23:21:26.480 -> 2272 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                            23:21:26.480 -> 2277 TSF:TDI:TSL
                            As far as i can see it seems fine and also shows up in myscontroller.
                            And here is an example how it looks after 20 seconds sleep.
                            2414 MCO:SLP:WUP=-1
                            23:26:36.346 -> 2416 TSF:TRI:TSB
                            23:26:36.346 -> 2418 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                            23:26:36.346 -> 2423 TSF:TDI:TSL
                            I don't see any connection attempts with my gateway, or shouldn't there by any if the sensor is not triggered?
                            Here i can show how it looks when tricking the sensor with the ir on the mouse.
                            2456 MCO:SLP:WUP=-1
                            23:27:48.785 -> 2458 TSF:TRI:TSB
                            23:27:48.785 -> 2460 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                            23:27:48.785 -> 2465 TSF:TDI:TSL
                            2467 MCO:SLP:WUP=-1
                            23:27:48.924 -> 2468 TSF:TRI:TSB
                            23:27:48.959 -> 2470 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                            23:27:48.959 -> 2476 TSF:TDI:TSL
                            2478 MCO:SLP:WUP=-1
                            23:27:49.098 -> 2480 TSF:TRI:TSB
                            23:27:49.098 -> 2481 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                            23:27:49.098 -> 2486 TSF:TDI:TSL
                            2488 MCO:SLP:WUP=-1
                            23:27:49.235 -> 2490 TSF:TRI:TSB
                            23:27:49.235 -> 2492 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                            23:27:49.270 -> 2497 TSF:TDI:TSL
                            2498 MCO:SLP:WUP=-1
                            23:27:49.408 -> 2500 TSF:TRI:TSB
                            23:27:49.408 -> 2502 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                            23:27:49.408 -> 2507 TSF:TDI:TSL
                            2509 MCO:SLP:WUP=-1
                            23:27:49.546 -> 2510 TSF:TRI:TSB
                            23:27:49.546 -> 2512 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                            23:27:49.546 -> 2518 TSF:TDI:TSL
                            Interrupt is triggered and it wakes up, but nothing is sent to the gateway.
                            Have i missed something?
                            • P patrikr76
                              23:21:24.219 ->
                              2080 TSM:FPAR:OK
                              2414 MCO:SLP:WUP=-1
                              2456 MCO:SLP:WUP=-1
                              2467 MCO:SLP:WUP=-1
                              2478 MCO:SLP:WUP=-1
                              2488 MCO:SLP:WUP=-1
                              2498 MCO:SLP:WUP=-1
                              2509 MCO:SLP:WUP=-1
                              @patrikr76 great info, thanks!
                              The -1 in Wup=-1 indicates that the node was waken up by timer and not by interrupt. That’s very strange, since the time stamps clearly show that 20 seconds has not passed.
                              Could you add
                              Serial.println(pulseCount);
                              after
                              sleep(SEND_FREQUENCY);
                              to see if pulseCount is increased?
                              • P
                                P
                                patrikr76
                                #154
                                @mfalkvidd , Here's the serial monitor after adding the serial print.
                                2269 MCO:SLP:WUP=-1
                                14:15:15.125 -> 2270 TSF:TRI:TSB
                                14:15:15.125 -> 0
                                14:15:15.125 -> 2272 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                                14:15:15.125 -> 2277 TSF:TDI:TSL
                                2279 MCO:SLP:WUP=-1
                                14:15:37.264 -> 2281 TSF:TRI:TSB
                                14:15:37.264 -> 0
                                14:15:37.264 -> 2282 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                                14:15:37.264 -> 2287 TSF:TDI:TSL
                                2289 MCO:SLP:WUP=-1
                                14:15:59.354 -> 2291 TSF:TRI:TSB
                                14:15:59.354 -> 0
                                14:15:59.354 -> 2293 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                                14:15:59.389 -> 2298 TSF:TDI:TSL
                                As you see, it sleeps about 22 secs with no pulse on it.
                                Moving the mouse over it gives this.
                                2353 MCO:SLP:WUP=-1
                                14:18:09.982 -> 2355 TSF:TRI:TSB
                                14:18:09.982 -> 4
                                14:18:09.982 -> 2357 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                                14:18:09.982 -> 2362 TSF:TDI:TSL
                                2363 MCO:SLP:WUP=-1
                                14:18:23.059 -> 2365 TSF:TRI:TSB
                                14:18:23.059 -> 5
                                14:18:23.059 -> 2367 MCO:SLP:MS=20000,SMS=0,I1=255,M1=255,I2=255,M2=255
                                14:18:23.059 -> 2372 TSF:TDI:TSL
                                Looking through the code, this one raises a flag.
                                if (pcReceived && (SLEEP_MODE || sendTime))
                                The pulseCount send is within that if statement which is not fullfilled because it doesn't receive pcReceived.
                                Or am i wrong?
                                • P
                                  P
                                  patrikr76
                                  Found a solution, which is not ideal.
                                  I was having similar problem with a motion sensor not being able to send, adding a delay after sleep helped on that one, but it was just a 5ms delay needed.
                                  On this one i had to add a 1 sec delay in the begining of the loop. I tried smaller but then it didn't work.
                                  I am starting to think it is the nano clone that has crappy components.
                                  • P patrikr76
                                    @patrikr76 nice work.
                                    Sounds very similar to https://forum.mysensors.org/topic/9655/delay-after-tsf-tri-tsb/14
                                      StKilda
                                      I have two meters I would like to measure: One that the LED is off most of the time and briefly pulses on per increment (at 3200 pulses per Kwh - so I adjusted the pulse factor accordingly). This works fine. The second meter, the LED pulses off (meaning the led it lit most of the time, and pulses off briefly). Do I need to adjust the code in any way to deal with this meter? Thanks. Really impressed it works virtually out of the box.
                                      • S StKilda
                                        Great work @stkilda
                                        I think the sketch will work without modification. The easiest way to find out is probably to try it.
                                          you may need to change the interrupt behavior, but try it first