  • YveauxY Yveaux
    @hek said:
    a thing-that-can-be-turned-on-or-of
    Hmmmm.... Let me think.... a switch ? ;-)
    Haha.. yeah.. :+1:
      @a-lurker said:
      Electrical impedance and resistance are not the same thing- suspect resistance is intended here?
      V_IMPEDANCE --> V_RESISTANCE
      I think the impedance-variable comes from the RFXTRX plugin. And it is related to body fat measurements for body scales.
      http://code.mios.com/trac/mios_rfxtrx/browser/trunk/L_RFXtrx.lua
      If I understand it correctly Impedace is used for AC and resistance for DC. Not sure what would be most useful in this setup.
      DammeD
      DammeD
      Damme
      Code Contributor
      @hek Moisture or Water detecded... Might be 2 different ?
      Thinking different applications: Moisture in ground. (I.e. Water needed? Ground dry?) And Water level, hmm, if you have a fluid level meter to detect overfill. or leakage. Fluid flow
      hekH 1 Reply Last reply
        @Yveaux said:
        When transfered as ASCII you're right, but that isn't required with 1.4 anymore.
        Most users still use the serial protocol. Which means strings like "0.000003423" must be generated and transferred to the controller from gateway.
        YveauxY
        YveauxY
        Ok, but is this a problem? You could even pass it as 3.423e-6....
        You don't want this string on air if you can transfer the same thing in 4 bytes, that's true.
        I only want to state that if you transfer it purely in SI units, without scaling, you always know what the actual value is.
        • YveauxY
          YveauxY
          I'm still in doubt if we really need all these different value types...
          In principle a (light) switch, water level sensor, burglar alarm, heater status <fill in your own binary switch> all just return or take 0 or 1. V_BINARY should suffice for all of them.
          For other values you see the struggle between defining them as bare units (V_AMPS, V_VOLTS, V_CUBIC_MEASURE) and function (V_FLOW, V_WEIGHT, V_HUMIDITY).
          Can't we just live with transfering values by specifying their units only and leave the interpretation of it to the controller (e.g. V_AMPS, V_BINARY, V_PERCENTAGE) ?
          I'm not familiar with Vera, but e.g. the OpenHAB/MQTT combination doesn't care at all what type of value is exchanged. It's up to the configuration of OpenHAB how a value is interpreted.
          • DammeD Damme
            For water detected I would probably use V_TRIPPED.
            Hmm.. Soil Moisture.. I have no idea how to represent this. Help me! The ebay sensors we're using isn't super accurate and comes uncalibrated.
            DammeD 1 Reply Last reply
              DammeD
              DammeD
              Damme
              Code Contributor
              @hek I know, ist more 'need moisture' or not :) Hmm... V_Moisture, (relative) 0-255 / 0-100% / True | False
              • YveauxY
                YveauxY
                @hek Can we also pass battery level as just a sensor value? There's no real need to pass this as an internal message, is it?
                  Z
                  Z
                  Zeph
                  First off, this is a very positive step forward!
                  Now some details
                  I think that we need to be clear about the core concept of what we intend to measure.
                  Resistance or impedance generally don't make much sense, as they are usually not the conceptual thing being measured but an intermediate value used in calculating it.
                  This is also true of Volts and Amps, except that sometimes we really do want volts and amps (for power monitoring).
                  But consider a Light Dependent Resistor in a bridge circuit.
                  We could report the value as ADC readings 0..1023.
                  Or we could convert that to volts 0..3.3 or 0..5.0 or whatever.
                  Or we could convert that to LDR resistance (knowing the other resistor value) in ohms.
                  Or we could do some calcs and try to report the result in Lux.
                  Since the conceptual thing we are trying to measure is light intensity, the best option would be to report it in Lux if possible. Not as ohms, volts, or ADC readings.
                  So any time we see something reporting as resistance or impedance, we should ask if that's the core concept we need to report, or an incompletely processed proxy that will be hard for the server to understand.
                  Likewise with volts or amps - are we really trying to report temperature or humidty or what? If we are monitoring a battery or the AC mains, then maybe volts it exactly right, but we need to think it out first.
                  So who in a home automation context cares about resistance or impedance as the core thing being measured?
                    To simplify sketches even further we've discussed and decided to let sensors send in standard SI units and let controller convert them to the appropriate format.
                    This will also remove the need for a unit-config exchange with controller at sensor startup.
                    The new over-the-air messages has changed quite much with a more logical structure that can handle extension and even a completely different network layer if needed.
                    The ongoing work can be found here:
                    https://github.com/henrikekblad/Arduino/blob/development/libraries/MySensors/MyMessage.h
                    Will not bring this into development until it actually compiles.
                    Feel free to give feedback and report any missed sensor-types.
                    In parallell we should probably discuss the serial-protocol for 2.0. Is it time for json perhaps?
                    Z
                    Z
                    Zeph
                    wrote on last edited by Zeph
                    #29
                    @hek said:
                    V_TEMPERATURE - Degrees celsius <int or float>
                    V_HUMIDITY - Humidity percentage 0-100% <int or float>
                    Can any of the values be int or float? Or just these two?
                    V_DIMMER - Percentage 0-100% (used for lights, blinds and curtains)
                    The core concept here is V_PERCENT. In one home automation system there might be only one included concept, the Dimmer, and you'd have to use that for blinds as well as dimmers. In another home automation system there might be separate UI widgets for blinds and light dimmers. The sensactuator node's code should not need to change either way. Mapping a given V_PERCENT variable to UI concepts of blinds or dimmers is conceptually part of the configuration for a given (version of a) home automation system.
                    V_FORECAST Whether forecast. One of "stable", "sunny", "cloudy", "unstable", "thunderstorm" or "unknown"
                    Difficult one. That is very definitely not the controlled vocabulary used by all forecasting sources, and mapping into this list is going to be difficult. "Scattered showers" and "partly cloudy" and "light rain" and "foggy" are not going to be easily represented. What about stable/sunny versus stable/rainy? Are stable/unstable mutually exclusive choices with the others, or optional additional attributes for any of the other choices?
                    Maybe this has to be an open vocabulary with a text string? What text they will get depends on their source.
                    V_RAIN - mm
                    V_WIND - m/s (average wind speed during last report period)
                    V_GUST - m/s (highest wind speed during since last report)
                    V_WATT - Watt <int>
                    V_KWH - kWh <int or float>
                    What is the report period and what resets it? Last minute, last hour, last 24 hours, since midnight, since the reset button was pushed, or using automatic episode detection (I was just looking at a rain sensor which uses 8 hours of no rain to separate rain accumulation events). Without some knowledge of the reporting period these values cannot be meaningfully interpreted.
                    V_RAIN could be a forever incrementing total if the host wants to do its own deltas and define it's own report periods (maybe several of them).
                    V_WIND is a bit more difficult. If we had guaranteed delivery, we could just average since the last report from the node. Of course, some weather stations may do their own averaging, or the node could average many readings. But how does the host know?
                    From my perspective these "time period sum or average" values would ideally involve:
                    • an OTA format which loses no useful information available from the sensors or peripherals
                    • a flexible gateway (or adapter) which reformulates into time units meaningful to the HA controller software
                      Let me make up an example. Suppose the sensor reported wind speed averages over 5 minute periods and the HA controller wanted to report it over one hour periods. The gateway could average 12 reports - for either the last 60 minutes, or for on-the-hour, as needed. Or "new rainfall" could be reported in 10 minute increments, but accumulated since midnight by the gateway, if that's what the controller prefers. Different controllers might use different accumulation periods; and what is sent to a controller could vary from what was uploaded to a cloud service. The node should not be adapting to the controller, it should send all available and useful info and the gateway or adapter should adjust - sort of like degrees F but more complicated because it might involve keeping running totals for averaging.
                    V_ANGLE - radians <float or int>
                    Here's one of those "generic vs specific" ones. Like V_PERCENT suggested above, V_ANGLE has no implications for what is being measured, only the units. It could be wind direction, it could be the plantation shutter position, it could be the solar panel tilt. How does the host know?
                    (This is the kind of thing that prompted my suggestions on another thread to separate the concept of units from what is being measured.)
                    An int for radians doesn't make much sense (unless we have a scaling factor).
                    I think degrees is a reasonable compromise - it's more precise than any sensor we're going to afford (or than the noise in the data itself would make moot), so it loses no meaningful accuracy. And virtually no sensor is going to report in radians. Some report in degrees. If it reports in 16 compass points or such, that can be easily converted to degrees, without even using floating point.
                    V_WEIGHT - kg <int, float>
                    V_DISTANCE - Cm <int, float>
                    V_IMPEDANCE - Ohm
                    See other message about intermediate calculations and the true conceptual thing being measured, (with impedance as an example). What does a distance of 240cm mean?
                    V_ARMED - Armed status of a security sensor. 1=Armed, 0=Bypassed
                    V_TRIPPED - Tripped status of a security sensor. 1=Tripped, 0=Untripped
                    Here the underlying concept is "V_BINARY", with a variety of associated labels for 1 and 0 based on what is being reported or controlled. On/Off, Open/Closed, Armed/Unarmed, Tripped/Untripped, Locked/Unlocked, Enabled/Disabled, etc. Do we create an ever expanding set of binary options as different variable types? Or is it functionally one variable type (or a small number with definably different dynamics from each other) with additional attributes (like the labels used for 1 and 0)?
                    V_SCENE_ON - Scene number <int>
                    V_SCENE_OFF - Scene number <int>
                    Now we are conflating events or commands with statuses or values. We turn on a light by setting it to 1 (or 100%) and we turn it off by setting it to 0 (or 0%). This leverages the same "set value to" underlaying functionality, and allows a simple and consistent query concept (what is the current value of the light?) What is the advantage of treating a Scene differently?
                    Scenes are a bit confusing, because they may or may not be mutually exclusive. They are neither obviously "checkboxes" or "radio buttons".
                    V_HEATER_MODE - Heater mode. One of "Off", "HeatOn", "CoolOn", or "AutoChangeOver"
                    How do we set the themostat? What about Fan?
                    V_HEATER_STATUS - 1=On, 0=Off. Heater power switch
                    What about CoolOn mode? If it's cooling, is V_HEATER_STATUS on or off?
                    V_LIGHT_LEVEL - 0-100% <int>
                    Is this a sensor (alternative to V_Lux) or an actuator (different than V_DIMMER/V_PERCENT above)?
                    V_UP - command which modes blinds ful up. Use DIMMER to specify percentage
                    V_DOWN - command which moved blinds to full down. Use DIMMER to specify percentage
                    Use V_DIMMER (or V_PERCENT) instead of or in addition to this? Why not just set to 100% instead of having a "V_UP" command?
                    V_STOP - stop blinds in the middle of motion.
                    This is a bit tricky too - it's time dependent and latency becomes important, if you want to set a given position manually. So maybe it's just about canceling any previous command whereever the blinds are, eg: for safety. I'm not really sure how this is used in a script.
                    V_LOCK_STATUS - 1=Locker, 0 = Unlocked
                    Again, is this different than other binary set/query dynamics, or just different labels?
                    V_DUST_LEVEL - ug/m3
                    One of the issues I mentioned in the other thread is uncalibrated values. That comes up with some sensors. For example, the sensor's values may not be convertable to ug/m3, it might measure particle count without mass, or size without density to compute mass, or only particles within a given range. (Light is like this too, by the way, as a sensor's true output is not lux, but lux-within-a-given-wavelength-range-with_weighting, but we skip past that).
                    V_VOLTS - Volt <int or float>
                    V_AMPS - Ampere <int or float>
                    Discussed in another message. OK if the thing we are really measuring IS voltage or current.
                    Anyway, this is moving forward despite my questions, and it's meeting my desire to have each of these defined more meaningfully. Thanks!
                    • Z
                      Z
                      Zeph
                      #30
                      I see four concepts involved in describing variables types here.
                      1. Simplest is format, like int or float (or what size of int, signed or not). OK, that's getting separated out and is pretty well understood.
                      2. Another is what I'm going to call dimension - what kind of physical or abstract thing is being measured, like temperature or position or speed or particle density.
                      3. A related one is units.
                      The units usually imply the dimension, so it becomes very tempting to conflate dimension and units into just the latter. However sometimes we don't know or need to know standard units. For example, we might have an uncalibrated light dependent resistor, for which we know only two things: we get readings from 0 to 1023, and higher is brighter (or lower is brighter) - but we don't know the lux and don't have the info to compute it. In this case we DO know the dimension (brightness) and the direction. We could record values over time and graph them, we could know when it's getting brighter or dimmer and when it peaks, we could empirically set meanngful thresholds ("when value > 350 at night the lights are still on") - all without knowing the value in Lux. If we cannot report brightness in lux, should we ignore the readings,, lie about the lux, or have a concept of uncalibrated values whose demension and direction are known but whose units are not?
                      Also, the same units may be used for conceptually different things - like temperature, dew point, and wind chill. So units don't always imply the dimension.
                      1. Meaning or semantics. Take angle - is it a wind direction or a servo position or what? Even something like temperature gets a bit confused - we are all familiar with air temp, but concepts like temp at 3 meters and at grould level come up. Or input and output temperature for a heating system. Or measured temperature versus thermostat setting. Or how about absolute vs relative humidity?
                      Now when we come up with a defined list of variable types, it's all too easy to mix and match among these concepts when deciding where to lump and where to split )(and how to name and describe). Avoiding a hodgepodge of concepts is the challenge.
                      Let me give a small example. Here's one way to slice things:with just dimension and units:
                       V_SPEED m/s
                       V_ANGLE degrees
                      And here's a different one, mixing in semantics:
                      V_WIND m/s
                      V_WIND_DIRECTION "from direction" in degrees cw from true north
                      We currently don't have either, we have V_ANGLE and V_WIND, some from conceptual framework. Not criticising, just observing. I'm very sympathetic to how this happens.
                      Also notice that angle for wind also has an implicit or explicit orientation (where is 0 degrees/radians and which way increases), which is missing from the abstraction of angle.
                      The problem with combining semantics is that your controlled vocabulary of types can get so large.
                      My best solution so far is to handle dimension as a mutually exclusive type choice (choose one), and semantics as a tag or attribute (choose zero or more of many). If the semantics are not understood by a given system ("what's manifold water temperature mean, I've not been programmed to understand that?" then at least it understands the temperature dimension and the units. This doesn't make it all easy, but it seems to make it more tractable than just having one mutually exclusive list for to represent all aspects (except format #1 above)
                      YveauxY 1 Reply Last reply
                      • Z Zeph
                         V_SPEED m/s
                         V_ANGLE degrees
                        V_WIND m/s
                        YveauxY
                        YveauxY
                        @Zeph Most of the concepts and ideas you touch have already been mentioned in the posts above... Did you read them?
                          wrote on last edited by hek
                          #32
                          Ok, I've had a solutions bubbling in my head over night. It will add one byte in the MySensors Req/Set Header but solves a lot of the discussions we've had earlier in other threads as well. Its also replaces both INTERNAL and PRESENTATION command.
                          --- Moved to the first post ---
                          DammeD Z 2 Replies Last reply
                          • YveauxY
                            YveauxY
                            @hek said:
                            Where does this fit?
                            V_DEW_POINT - Degrees Celsius <int or float>
                            Either it doesn't fit in (let the controller calculate it) or place under S_HUMIDITY.
                            I'm not completely convinced we need to store it this way and use another byte for each req/set message (which are most common...). I'll let it rest for a while so I might diss your solution later ;-)
                              DammeD
                              DammeD
                              Damme
                              Code Contributor
                              wrote on last edited by Damme
                              #34
                              Could someone please explain to me why we have S_ types at all? I really dont get it.. I Only think it makes things more complicated. (my conclusion - I dont like it)
                              • DammeD Damme
                                #35
                                Read my post again and explain how you would distinguish a thermometer from a uv sensor on the controller side without it?
                                YveauxY DammeD 2 Replies Last reply
                                  YveauxY
                                  YveauxY
                                  IMHO this all depends on the controller used, as I already explained. I'm not familiar with Vera, but e.g. for OpenHAB/MQTT the actual type of a sensor is defined by the OpenHAB configuration. It just receives a value and you need to tell it that node x sensor y is a temperature sensor.
                                  Possibly Vera and other systems are more of a plug-and-play kind and are able to add a sensor depending on its type automatically.
                                  I (for a long time) agree with @Damme but I can imagine there are systems that do require this information.
                                  [dissing start] Did you think about sending the sensor type only once, durig presentation? There really is no need to send it with each set/req message as it is static for the duration of the connection. For Vera and the like this probably means you should buffer these values in the gateway... [dissing end]
                                  DammeD hekH 2 Replies Last reply
                                    DammeD
                                    DammeD
                                    Damme
                                    Code Contributor
                                    @hek I've been thinking and thinking and even might have an other solution.. but I'll wait with that.
                                    so every piece of data has a S_type and V_type.. V_ must be a fixed unique table (not starting from 0 on every S_type)
                                    I'm more acceptable now than 10 minutes ago.. :)
                                    • YveauxY Yveaux
                                      DammeD
                                      DammeD
                                      Damme
                                      Code Contributor
                                      I think for the controllers view it would be best for the node to send every message with sensor id, sensor type, value type and payload. Noone needs to remember anything :) The way back to the node the rest can be omitted, as long as sensor id is there.
                                      • YveauxY Yveaux
                                        Yes, it would save a byte. But it could be very useful for a simpler controller (which can determine sensor type from each and every message) and when displaying sniffing data ;).
                                        This would only leave 3 COMMAND types left. REQ, SET and STREAM. Where STREAM-data probably could be handled by S_NODE (internal). This means just 1 bit is needed for a SET/REQ flag. But @ToSa would have to feedback on this.
                                        DammeD YveauxY T 3 Replies Last reply
                                          DammeD
                                          DammeD
                                          Damme
                                          Code Contributor
                                          @hek S_node could include stuff as
                                          Reboot
                                          ClearEEprom
                                          Read EEprom byte
                                          Set EEprom byte
                                          besides stream data types.
                                          (to be discussed if any of them are useful or not and if they should be hardcoded or not)