  2. Announcements
  3. 💬 Water Meter Pulse Sensor
109 Posts 37 Posters 67.0k Views 35 Watching
  • B bereska
    Is it possible to get any help on this page or not?
    rejoe2R
    rejoe2R
    rejoe2
    @bereska said in 💬 Water Meter Pulse Sensor:
    Crying out loud most likely will not help...
    Seems your setup is a little special, so just some assumptions from one using a serial GW and not MyS-MQTT:
    Your controller is asked for sending an initial value, but has none yet. So no answer is sent out. Triggering the counter on Node side could help to send one (after waiting time has passed). Then have a look at your controller, if there's a value available. If, you might set the correct value, restart your node afterwards and see, if everything now works as expected?
    B 1 Reply Last reply
    • rejoe2R rejoe2
      B
      B
      bereska
      @rejoe2 thank you. How do i trigger "the counter on Node side"?
      • rejoe2R
        rejoe2R
        rejoe2
        ...just let the node count some pulses (your code states: FALLING). So just pull the counter PIN (here: D3) to ground several times.
        • rejoe2R rejoe2
          B
          B
          bereska
          @rejoe2 i did like you said, still no show in HA
          here is the serial log:
           __  __       ____
          16 MCO:BGN:INIT NODE,CP=RNNNA---,VER=2.3.0
          26 TSM:INIT
          28 TSF:WUR:MS=0
          34 !TSM:INIT:TSP FAIL
          36 TSM:FAIL:CNT=1
          38 TSM:FAIL:DIS
          40 TSF:TDI:TSL
           __  __       ____
          26 TSM:INIT
          28 TSF:WUR:MS=0
          34 TSM:INIT:TSP OK
          36 TSM:INIT:STATID=6
          38 TSF:SID:OK,ID=6
          40 TSM:FPAR
          77 TSF:MSG:SEND,6-6-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
          532 TSF:MSG:READ,0-0-6,s=255,c=3,t=8,pt=1,l=1,sg=0:0
          538 TSF:MSG:FPAR OK,ID=0,D=1
          624 TSF:MSG:READ,31-31-6,s=255,c=3,t=8,pt=1,l=1,sg=0:1
          1267 TSF:MSG:READ,21-21-6,s=255,c=3,t=8,pt=1,l=1,sg=0:1
          1546 TSF:MSG:READ,41-41-6,s=255,c=3,t=8,pt=1,l=1,sg=0:1
          2088 TSM:FPAR:OK
          2088 TSM:ID
          2091 TSM:ID:OK
          2093 TSM:UPL
          2097 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=OK:1
          2103 TSF:MSG:READ,0-0-6,s=255,c=3,t=25,pt=1,l=1,sg=0:1
          2109 TSF:MSG:PONG RECV,HP=1
          2113 TSM:UPL:OK
          2115 TSM:READY:ID=6,PAR=0,DIS=1
          2119 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=OK:0100
          2127 TSF:MSG:READ,0-0-6,s=255,c=3,t=15,pt=6,l=2,sg=0:0100
          2138 TSF:MSG:SEND,6-6-0-0,s=255,c=0,t=17,pt=0,l=5,sg=0,ft=0,st=OK:2.3.0
          2148 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=6,pt=1,l=1,sg=0,ft=0,st=OK:0
          2242 TSF:MSG:READ,0-0-6,s=255,c=3,t=6,pt=0,l=1,sg=0:M
          2250 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=11,pt=0,l=11,sg=0,ft=0,st=OK:Water Meter
          2260 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=12,pt=0,l=3,sg=0,ft=0,st=OK:1.1
          2273 TSF:MSG:SEND,6-6-0-0,s=1,c=0,t=21,pt=0,l=0,sg=0,ft=0,st=OK:
          2281 MCO:REG:REQ
          2289 TSF:MSG:SEND,6-6-0-0,s=255,c=3,t=26,pt=1,l=1,sg=0,ft=0,st=OK:2
          2297 TSF:MSG:READ,0-0-6,s=255,c=3,t=27,pt=1,l=1,sg=0:1
          2304 MCO:PIM:NODE REG=1
          2306 MCO:BGN:STP
          2310 TSF:MSG:SEND,6-6-0-0,s=1,c=2,t=24,pt=0,l=0,sg=0,ft=0,st=OK:
          2318 MCO:BGN:INIT OK,TSP=1
          32319 TSF:MSG:SEND,6-6-0-0,s=1,c=2,t=24,pt=0,l=0,sg=0,ft=0,st=OK:
          • rejoe2R
            rejoe2R
            rejoe2
            wrote on last edited by rejoe2
            #99
            Logparser states: there was nothing counted (empty payload). So make sure, there really was counted anything.
            (I didn't check your sketch, just assuming, it's the default one and everything is wired correctly; if that's the case, you should be able to see a different payload than nothing or "0", that your controller might treat as non existent).
              Great work @bart59 !
              Do you have any indication on how long battery life you will get with this setup?
              stevefury
              @mfalkvidd how looks the sensor now with the modifications? and how to wire this?
              • S stevefury
                #101
                @stevefury sorry, I don't understand. Which modifications are you referring to?
                • I
                  I
                  ibibiuooui
                  I'm just getting this....
                  16:57:15.660 -> 10091 TSM:FAIL:RE-INIT
                  16:57:15.660 -> 10093 TSM:INIT
                  16:57:15.660 -> 10101 !TSM:INIT:TSP FAIL
                  16:57:15.660 -> 10103 TSM:FAIL:CNT=2
                  16:57:15.660 -> 10107 TSM:FAIL:DIS
                  16:57:15.713 -> 10111 TSF:TDI:TSL
                  • rejoe2R
                    rejoe2R
                    rejoe2
                    @ibibiuooui said in 💬 Water Meter Pulse Sensor:
                    !TSM:INIT:TSP FAIL
                    See https://www.mysensors.org/build/parser: There's a problem in the initialisation of your transceiver (whatever it may be). So first check wiring, see https://forum.mysensors.org/topic/666/read-this-first-it-could-save-you-a-lot-of-time for further details. If that doesn't help, imo you should open up a seperate thread.
                    • CrankyCoderC
                      CrankyCoderC
                      CrankyCoder
                      wrote on last edited by CrankyCoder
                      #104
                      I am finally getting around to trying this out. I was playing with just trying to see if i can get the pulses. First thing i did was take an old compass and put it beside the meter and had someone turn on the water. I could definitely see the compass needle pull a little as the water was flowing. So I assumed that pull was enough to be detectable with my hall effect sensor. I have tried a couple, and just can't seem to get it to pick up.
                      If i use a magnet, simple code will detect the pulse and the green led on the sensor lights up.
                      But no matter where I put that sensor near the meter it just doesn't seem to detect it. Not quite sure what's happening.
                      The meter i have is this one.
                      https://www.badgermeter.com/resources/add29b88-1ffb-49c9-80ab-bb8697bd6d1a/absolute digital encoder product data sheet ade-ds-00183-en.pdf/
                      Not sure if anyone has any recommendation on which hall effect sensor would be the best for this but ill take suggestions lol
                      My sensor I am testing with is
                      3144E Hall Effect Sensor
                      Doesn't have a sensitivity dial but the recommended one on this build page didn't either.
                      Home Automation Tinkerer
                      www.CrankyCoder.net
                      Gateway: MQTTClientGateway
                      MySensors: 2.3
                      • bart59B bart59
                        I wanted to operate my water pulse meter on batteries and also get the water flow. The original design had the following issues with that:
                        • Incorrect flow calc: micros() was used to calculate the flow, however micros() wraps every 70 minutes which looks like a huge flow (which is then discarded in code)
                        • Volume calc: millis() wraps every 50 days which is not handled correctly either
                        • Too much current for battery use: The IR LED of the TCRT5000 is always on and the LM393 comparator is also taking a few mA's
                        • Could not report flow in sleep mode because millis() does not increment on sleep - need to do this based on calculation of total sleep time. We now simply calculate the number of pulses per minute and deduct the flow
                        • I also had issued with the data transport reliability, so I added error counters (which show up on the Gateway as distance sensors)
                        • I also wanted to provide a measurement counter to the gateway (that counts up each time a message is sent)
                        • The sensor will reboot itself when too many errors occur
                        So I modified the circuit of the IR sensor:
                        • Assumption that the wheel of the water meter turns slowly (takes at least a few seconds to turn around)
                        • We will wake up every 500 millisecond to turn on the IR LED connected to PIN 8. Pin 8 also powers the photo transistor that measures the reflection
                        • I removed the power from the opamp circuit that is linked to the photo transistor
                        • The voltage from the photo transistor is then read using an analog read on A1. Based on a threshold value we will deduct if the mirror on the water meter is in view
                        • Pin 7 is connected to a learning switch which will turn the device in a specific mode and the min/max values on A1 are used to calculate the value of the threshold (which is then stored in the EEPROM)
                        • After 30 seconds in learning mode, the new threshold is established and the LED on Pin 6 will show the actual on/off mirror signals, so you can see the pulses are correctly counted
                        • switch back the DIP switch on Pin 7 to bring back normal mode
                        • The circuit also contains the battery voltage sensor circuit (I am using a 1.5V battery and step up circuit). So the resistors used are 470k from + pole of battery to the A0 input and 1 M ohm from A0 to ground
                         * Version 1.0 - Henrik Ekblad
                         * Version 1.1 - GizMoCuz
                         * Version 1.2 - changed BM: using low power separate circuit for infra red on pin 8 + analog A1
                         * ISSUES WITH ORIGINAL CODE
                         * Incorrect flow calc: micros() was used to calculate the flow, however micros() is wraps every 70 minutes which looks like a huge flow (which is discarded)
                         * Volume calc: millis() wraps every 50 days which is not handled correctly
                         * Too much current for battery use: The IR LED of the TCRT5000 is always on and the LM393 comparator is also taking a few mA's
                         * Could not report flow in sleep mode because millis() does not increment on sleep - need to do this based on calculation of total sleep time
                         * MODIFIED CIRCUIT IR SENSOR
                         * Assumption that the wheel of the water meter turns slowly (takes at least a few seconds to turn around)
                         * We will wake up every second to turn on the IR LED (connected to PIN 8). Pin 8 also powers the photo transistor that measures the reflection
                         * The voltage from the photo transistor is then read using an analog read on A1. Based on a treshold value we will deduct if the mirror is in view
                         * Pin 7 is connected to a learning switch which will turn the device in continous mode and the min/max values on A1 are used to recalc the treshold
                         * during a 30 second period. After this period the new treshold is established and the LED on Pin 6 will show the actual on/off mirror signals
                         * http://www.mysensors.org/build/pulse_water
                        // BOARD: PRO MINI 3.3V/ 8Mhz ATMEGA328 8Mhz
                        #define MY_NODE_ID 10                 // hard code the node number
                        #define SENSOR_POWER 8                // pin that will provide power to IR LED + sense circuit
                        #define IR_SENSE_PIN  A1              // input for IR voltage
                        #define BATTERY_SENSE_PIN  A0         // select the input pin for the battery sense point
                        #define LEARN_SWITCH_PIN 7            // switch (SW1 on battery module) to turn on learning mode (low==on)
                        #define LEARN_LED_PIN 6               // LED feedback during learning mode (LED on battery module)
                        #define LEARN_TIME 30                 // number of seconds we will keep learn loop
                        #define PULSE_FACTOR 1000             // Nummber of blinks per m3 of your meter (One rotation/1 liter)
                        #define MAX_FLOW 80                   // Max flow (l/min) value to report. This filters outliers.
                        #define CHILD_ID 1                    // Id of the sensor child (contains 3 subs: V_FLOW, V_VOLUME, VAR1)
                        #define CHILD_PINGID 2                // ID of ping counter
                        #define CHILD_ERRID 3                 // ID of error counter
                        #define CHECK_FREQUENCY 500           // time in milliseconds between loop (where we check the sensor) - 500ms
                        #define MIN_SEND_FREQ 60              // Minimum time between send (in multiplies of CHECK_FREQUENCY). We don't want to spam the gateway (30 seconds)
                        #define MAX_SEND_FREQ 1200            // Maximum time between send (in multiplies of CHECK_FREQUENCY). We need to show we are alive (600 sec/10 min)
                        #define IR_ON_SETTLE 2                // number of milliseconds after we turned on the IR LED and we assume the receive signal is stable (in ms)
                        #define EE_TRESHOLD 10                // config addresses 0 + 1 used for treshold from learning (loadState() returns only uint8 value)
                        #define TRESHOLD_MARGIN 3             // additional margin before we actually see a one or zero
                        #define RESETMIN 5                    // number of cycle times (either 30 sec of 10 min) we consistently need to have transmission errors before we perform hard reset
                        MyMessage volumeMsg(CHILD_ID,V_VOLUME); // display volume and flow on the same CHILD_ID
                        MyMessage flowMsg(CHILD_ID,V_FLOW); // flow
                        MyMessage lastCounterMsg(CHILD_ID,V_VAR1);
                        MyMessage pingMsg(CHILD_PINGID,V_DISTANCE); // use distance to keep track of changing value
                        MyMessage errMsg(CHILD_ERRID,V_DISTANCE); // use distance to keep track of changing value
                        double ppl = ((double)PULSE_FACTOR / 1000.0);    // Pulses per liter
                        unsigned int oldBatteryPcnt = 0;          // check if changed
                        unsigned int minsendcnt = MIN_SEND_FREQ;  // counter for keeping minimum intervals between sending
                        unsigned int maxsendcnt = MAX_SEND_FREQ;  // counter for keeping maximum intervals between sending
                        unsigned int treshold = 512;              // threshold value when to swap on/off for pulse
                        unsigned long pulseCount = 0;             // total volume of this pulse meter (value stored/received on gateway on pcReceived)
                        unsigned long oldPulseCount = 0;          // to see if we have received something
                        boolean pcReceived = false;               // received volume from prior reboot
                        boolean onoff = false;                    // sensor value above/below treshold
                        unsigned int intervalcnt = 0;             // number of cycles between last period (for flow calculation)
                        double flow = 0;                          // maintain flow
                        double oldflow = 0;                       // keep prior flow (only send on change)
                        unsigned int learntime=LEARN_TIME*2;      // timer for learning period
                        unsigned int learnlow = 1023;             // lowest value found during learning
                        unsigned int learnhigh = 0;               // highest value found during learning
                        boolean learnsaved = false;               // have saved learned value
                        unsigned long pingcnt = 0;
                        unsigned long errcnt = 0;                 // error count
                        unsigned int errcnt2 = 0;                 // error counter set to 0 when sending is ok
                        void(* resetFunc) (void) = 0;//declare reset function at address 0 (for rebooting the Arduino)
                          // make sure a few vars have the right init value after software reboot
                          pingcnt = 0;
                          pcReceived = false;
                          pulseCount = oldPulseCount = 0;
                          // setup hardware
                          pinMode(SENSOR_POWER, OUTPUT);
                          digitalWrite(SENSOR_POWER, LOW);
                          pinMode(LEARN_SWITCH_PIN, INPUT_PULLUP);
                          pinMode(LEARN_LED_PIN, INPUT);      // default is input because this pin also has SW2 of battery block
                          // Fetch last known pulse count value from gateway
                          request(CHILD_ID, V_VAR1);
                          // Fetch threshold value from EE prom
                          treshold = readEeprom(EE_TRESHOLD);
                          if (treshold<30 || treshold>1000) treshold = 512;   // wrong value in EEprom, take default
                          Serial.print("Treshold: ");
                          Serial.println(treshold);
                          // use the 1.1 V internal reference for the battery and IR sensor
                           analogReference(INTERNAL1V1);
                           analogReference(INTERNAL);
                          analogRead(IR_SENSE_PIN); // settle analogreference value
                          wait(CHECK_FREQUENCY); // wait a bit
                        void presentation()  {
                          sendSketchInfo("Water Meter", "1.2");
                          // Register this device as Waterflow sensor
                          present(CHILD_ID, S_WATER);
                          present(CHILD_PINGID, S_DISTANCE);
                          present(CHILD_ERRID, S_DISTANCE);
                          if (digitalRead(LEARN_SWITCH_PIN)==LOW) {
                            pinMode(LEARN_LED_PIN, OUTPUT);
                            digitalWrite(SENSOR_POWER, HIGH);
                            intervalcnt = 0;
                            learn_loop();
                            learnlow = 1023;
                            learnhigh = 0;
                            normal_loop();
                        void learn_loop() {
                          // will run into this loop as long as we are learning
                          wait(500);
                          unsigned int sensorValue = analogRead(IR_SENSE_PIN);
                          Serial.print("IR: ");
                          Serial.print(sensorValue);
                          if (learntime>0) {
                            // still learning
                            learntime--;
                            learnsaved = false;
                            digitalWrite(LEARN_LED_PIN, !digitalRead(LEARN_LED_PIN));  // blink led
                            if (sensorValue < learnlow) {
                              learnlow = sensorValue;
                              Serial.println(" Lowest");
                            } else if (sensorValue > learnhigh) {
                              learnhigh = sensorValue;
                              Serial.println(" Highest");
                            } else Serial.println();
                            if (!learnsaved) {
                              treshold = (learnhigh + learnlow)/2;
                              storeEeprom(EE_TRESHOLD, treshold);
                            learnsaved = true;
                            // just display using LED
                            digitalWrite(LEARN_LED_PIN, sensorValue>treshold);
                            Serial.println((sensorValue>treshold ? " on" : " off"));
                        void normal_loop() {
                          unsigned long start_loop = millis();    // to allow adjusting wait time
                          intervalcnt++;
                          // we start doing a measurement
                          wait(IR_ON_SETTLE);
                          #ifdef MY_DEBUG_DETAIL
                          Serial.println(sensorValue);
                          boolean nowvalue = onoff;
                          if (onoff && (sensorValue<treshold-TRESHOLD_MARGIN)) nowvalue = false;
                          if (!onoff && (sensorValue>treshold+TRESHOLD_MARGIN)) nowvalue = true;
                          if (nowvalue != onoff) {
                            // we have a pulse, only count on upwards pulse
                            onoff = nowvalue;
                            if (onoff) {
                              pulseCount++;
                              #ifdef MY_DEBUG
                              Serial.print("p: ");
                              Serial.println(pulseCount);
                          if (minsendcnt>0) minsendcnt--;
                          if (maxsendcnt>0) maxsendcnt--;
                          // send minimum interval when we have pulse changes or if we had some flow the prior time or send on timeout
                          if ((minsendcnt==0 && (pulseCount != oldPulseCount)) || (minsendcnt==0 && oldflow != 0) || maxsendcnt==0) {
                            if (!pcReceived) {   //Last Pulsecount not yet received from controller, request it again
                              Serial.print("Re-request var1 ..");
                        // Prevent flooding the gateway with re-requests,,, wait at least 1000 ms for gateway (cannot be sleep or smartSleep
                              wait(2*CHECK_FREQUENCY);
                              return;
                            pingcnt++;
                            sensorValue = analogRead(BATTERY_SENSE_PIN);
                            // ((1e6+470e3)/1e6)*1.1 = Vmax = 1.67 Volts
                            // 1.67/1023 = Volts per bit = 0.00158065
                            Serial.print("Battery %: ");
                            Serial.println(batteryPcnt);
                              oldBatteryPcnt = batteryPcnt;
                            double volume = ((double)pulseCount/((double)PULSE_FACTOR));
                            flow = ((double) (pulseCount-oldPulseCount)) * (60000.0 / ((double) intervalcnt*(double) CHECK_FREQUENCY)) / ppl;  // flow in liter/min
                            #ifdef MY_DEBUG
                            Serial.print("pulsecount:");
                            Serial.print("volume:");
                            Serial.println(volume, 3);
                            Serial.print("l/min:");
                            Serial.println(flow);
                            bool b = send(lastCounterMsg.set(pulseCount));  // Send  pulsecount value to gw in VAR1
                            if (b) errcnt2=0; else { errcnt++; errcnt2++; }
                            b = send(volumeMsg.set(volume, 3));               // Send volume (set function 2nd argument is resolution)
                            b = send(flowMsg.set(flow, 2));                   // Send flow value to gw
                            b = send(pingMsg.set(pingcnt));                   // ensure at least this var has a different value
                            b = send(errMsg.set(errcnt2+((float) errcnt2/100),2));    // ensure we always send error count
                            oldPulseCount = pulseCount;
                            intervalcnt = 0;
                            oldflow = flow;
                            if (errcnt2>= (5*RESETMIN)) {
                              Serial.println("Reset");
                              wait(300);
                              resetFunc(); //call reset to reboot the Arduino
                        // calculate how long it took to process all of this. then go to sleep for the remaining period
                          unsigned long end_loop = millis();
                          if (end_loop - start_loop < CHECK_FREQUENCY)
                            sleep(CHECK_FREQUENCY - (end_loop > start_loop ? end_loop - start_loop : 0));
                          if (message.type==V_VAR1) {
                            unsigned long gwPulseCount=message.getULong();
                            pulseCount += gwPulseCount;
                            oldPulseCount += gwPulseCount;
                            flow=oldflow=0;
                            Serial.print("Received last pulse count from gw:");
                            pcReceived = true;
                        void storeEeprom(int pos, int value) {
                            // function for saving the values to the internal EEPROM
                            // value = the value to be stored (as int)
                            // pos = the first byte position to store the value in
                            // only two bytes can be stored with this function (max 32.767)
                            saveState(pos, ((unsigned int)value >> 8 ));
                            pos++;
                            saveState(pos, (value & 0xff));
                        int readEeprom(int pos) {
                            // function for reading the values from the internal EEPROM
                            // pos = the first byte position to read the value from
                            int hiByte;
                            int loByte;
                            hiByte = loadState(pos) << 8;
                            pos++;
                            loByte = loadState(pos);
                            return (hiByte | loByte);
                        Emmanuel AbrahamE
                        Emmanuel AbrahamE
                        Emmanuel Abraham
                        @bart59 Can you post full circuit diagram for the modified code you made?
                        • Paolo RendanoP
                          Paolo RendanoP
                          Paolo Rendano
                          I made some improvements on this sketch. Please review them here: https://github.com/mysensors/MySensors/pull/1540
                          with these changes you will have:
                          1 - factory reset
                          2 - automatic home assistant entities creation
                          3 - counter correction from home assistant using service notify.mysensors
                          4 - fixed counter automatically incremented by 1 at each device restart (due to arduino library interrupt bug)
                          5- other tiny improvements
                          • J
                            J
                            JeeLet
                            wrote on last edited by JeeLet
                            #107
                            Thanks for the feedback
                            For those who think MySensors is finished, the proof is in the pudding, thousands of systems are functional :earth_asia:
                              StephanXL
                              I really like the update you did for Home Assistant integration.
                              But: I do not really understand, how to correctly send the VALUE_TO_ADD.
                              This is what I tried to add 967.067 m³:
                              service: notify.mysensors
                              data:
                                message: VALUE_TO_ADD
                                target: text.water_meter_100_2
                                data: 967067
                              But I just get this error message:
                              Fehler beim Aufrufen des Diensts notify.mysensors. expected dict for dictionary value @ data['data']. Got None
                              These are my newly found entities:
                              What is wrong here?
                              S 1 Reply Last reply
                              • S StephanXL
                                data:
                                  data: 967067
                                What is wrong here?
                                StephanXL
                                I finally got this to work. Unlike what the description here says, this is how to update the value:
                                In Home Assistant, go to Developer->Service->YAML mode:
                                service: text.set_value
                                data:
                                  value: "967067"
                                target:
                                  entity_id: text.water_meter_100_2
                                (change 967067 with the value you want to add to the current counter)
                                The service "notify.mysensors" seems to be deprecated by Home Assistant.