  3. Communication problem (maybe)
30 Posts 5 Posters 13.0k Views 3 Watching
  • H Offline
    H Offline
    Hausner
    I have a UNO R3 as a MQTT GW and some temp sensors (mini pro 5v) and 1 actuator relay sensor (a nano).
    The problem is that the comm to the actuator node keeps "partly" dropping out. Yes, I know it sound wierd, but this is what happens.
    On relay actuator powerup, everything works as planned. I can see the relay on the GW console. The temp sensors then use the relay actuator sensor as a repeater to report temp. It all works. So far so good.
    Now, if I send some commands to the relay actuator (switch on a relay) it works, but no more than 5-10 times, then the GW reports
       <<30 16 00 13 4D 79 4D 51 54 54 2F 32 32 2F 32 2F 56 5F 4C 49 47 48 54 30
      0;0;3;0;9;send: 0-0-22-22 s=2,c=1,t=2,pt=0,l=1,st=fail:0
    The relay node however keeps functioning as a repeater node, even though, it has stopped to respond on actuator "SET" commands.
    This is the relay actuator booting seen from the GW
       0;0;3;0;9;read: 22-22-0 s=255,c=0,t=18,pt=0,l=3:1.4
       0;0;3;0;9;read: 22-22-0 s=255,c=3,t=6,pt=1,l=1:0
       0;0;3;0;9;send: 0-0-22-22 s=255,c=3,t=6,pt=0,l=1,st=ok:M
       0;0;3;0;9;read: 22-1-0 s=255,c=3,t=6,pt=1,l=1:0
       0;0;3;0;9;send: 0-0-1-22 s=255,c=3,t=6,pt=0,l=1,st=fail:M
       0;0;3;0;9;read: 22-22-0 s=255,c=3,t=11,pt=0,l=5:Relay
       0;0;3;0;9;read: 22-22-0 s=255,c=3,t=12,pt=0,l=3:1.0
       0;0;3;0;9;read: 22-22-0 s=1,c=0,t=3,pt=0,l=3:1.4
       0;0;3;0;9;read: 22-22-0 s=2,c=0,t=3,pt=0,l=3:1.4
       0;0;3;0;9;read: 22-22-0 s=3,c=0,t=3,pt=0,l=3:1.4
       0;0;3;0;9;read: 22-22-0 s=4,c=0,t=3,pt=0,l=3:1.4
       0;0;3;0;9;read: 22-22-0 s=5,c=0,t=3,pt=0,l=3:1.4
    and seen from the node:
     repeater started, id 22
     send: 22-22-0-0 s=255,c=0,t=18,pt=0,l=3,st=ok:1.4
     send: 22-22-0-0 s=255,c=3,t=6,pt=1,l=1,st=ok:0
     read: 0-0-22 s=255,c=3,t=6,pt=0,l=1:M
     send: 22-22-0-0 s=255,c=3,t=11,pt=0,l=5,st=ok:Relay
     send: 22-22-0-0 s=255,c=3,t=12,pt=0,l=3,st=ok:1.0
     send: 22-22-0-0 s=1,c=0,t=3,pt=0,l=3,st=ok:1.4
     send: 22-22-0-0 s=2,c=0,t=3,pt=0,l=3,st=ok:1.4
     send: 22-22-0-0 s=3,c=0,t=3,pt=0,l=3,st=ok:1.4
     send: 22-22-0-0 s=4,c=0,t=3,pt=0,l=3,st=ok:1.4
     send: 22-22-0-0 s=5,c=0,t=3,pt=0,l=3,st=ok:1.4
    The GW and relay node are now only 20cm apart because I thought it could be a bad signal problem, but then again, it works fine in it's original place when it's only repeating temp sensors. As soon as I send the actuator "switch on" commands, the relay actuator part starts to fail.
    Any advise would be highly appreciated :)
    • H Offline
      H Offline
      You must upgrade to 1.4.1
      • H Offline
        H Offline
        Hausner
        I only see version 1.4 on the download page. :(
        • H Offline
          H Offline
          You will get 1.4.1 when downloading.
          • H Offline
            H Offline
            Hausner
            wrote on last edited by Hausner
            Yes, I figured that out, but the problem is still there...
            Only 5-10 relay on/off, then it fails.
            It actually looks like the GW never sends the new status. I see faild on GW, but nothing on the node?
            • N Offline
              N Offline
              niccodemi
              @Hausner I've got same issues with relay nodes. Other sensor nodes work ok.
              See this post for my serial output. At first I thought this is because of ethernet gw but now I am having similar issues with serial gw. I can switch relay on/off few times but after that node stops responding.
              • H Offline
                H Offline
                How do you power you relays?
                • H Offline
                  H Offline
                  Hausner
                  I first tried with the nano, but (ofcause) that was insuffient.
                  So now the 8-channel relay is powered externally, via JD-VCC and GND. The nano has a 5v to the 5v on the relay pin which is next to the INx pins. Nothing on the GND.
                  • N Offline
                    N Offline
                    niccodemi
                    Same here, relay is powered separately.
                    H 1 Reply Last reply
                    • N niccodemi
                      H Offline
                      H Offline
                      Hausner
                      Do you have the arduino and relay on shared GND?
                      • P Offline
                        P Offline
                        pgo
                        wrote on last edited by pgo
                        Do you use sleep in some of the nodes? I found with sleep(xxx) the messages get dropped across the mesh... I found that by making multiple sensors in one node - http://forum.mysensors.org/topic/115/implementing-multiple-sensors/59 and it gets worse with going through repeaters. For example the lux sensor could be very active and then the Relay ON/OFF messages get dropped... Interesting I did never see a temp or lux node message got dropped through the mesh.
                        EDIT I am using MQTT broker gateway and open HAB, but will probably switch to MQTT client gateway<->mosquitto<->openHAB to check whether the message delivery gets more stable.
                        • H Offline
                          H Offline
                          Hausner
                          @pgo
                          Yes, I have 3 temp nodes running on battery which uses the sleepmode.
                          But it doesn't matter if they are runnig or not, the result with the relay node is the same. With the battery nodes offline it does however seem more stable. At least I can get 3-4 times as many relay on/off before it fails.
                          I'm running the default MQTT GW, DallasTemperature Nodes and Relaynode sketches. OpenHAB as controller.
                          Something tells me, that I might have to go back to the serial GW on a Raspberry and then use the GPIO pins to control the relay. When that was running, I never had a single problem with messages getting dropped.
                          • N Offline
                            N Offline
                            niccodemi
                            @Hausner yes, arduino and relay share ground. I use this node solely as relay (not repeater) and still have issues.
                            • H Offline
                              H Offline
                              Hausner
                              I have now converted the 3 temp sensors to mains power and removed the sleep function, but the problem is still the same :(
                              I even let the temp nodes be repeaters! I looks like the GW can't SEND to the nodes, receiving is just fine. I'm getting "spammed" with temp readings atm.
                              I have already tried with a CAP on the GW radio, but still out of luck :(
                              Somehow this tells me, that mysensors is not for me :(
                              • H Offline
                                H Offline
                                Hausner
                                UPDATE:
                                I was getting a bit frustrated with the relay node not working, so as a last resort, i decided to reset all the nodes. Starting with the temp nodes and the relay at the end.
                                And I'll be damned! The system has now been running 3-4 hours with only a single hickup! (a relay failed on first request)
                                So this tells me, that if you only have "1-way send" battery nodes in the mesh eg. temp sensors, then the "intelligent" mesh works fine, but as soon as you introduce main powered "recieve" nodes to the setup, it starts to fail (big time!). So pgo, you were right! I have just seen the same as you.
                                At the temp sensors, I have removed the sleep command. The only problem now is that i'm getting flooded with temp readings! Anyone know of a simple solution to only have reading every 1 min without killing the radio?
                                • D Offline
                                  daulagari
                                  Good observation but what is the difference between the "1-way send" battery nodes and the main powered "receive" nodes? Is it that the main powered nodes do send more often messages and therefore the network gets flooded?
                                  I am not sure how this is related to "i decided to reset all the nodes. Starting with the temp nodes and the relay at the end."
                                  On:
                                  In there sketch there is:
                                  float temperature = static_cast<float>(static_cast<int>((gw.getConfig().isMetric?sensors.getTempCByIndex(i):sensors.getTempFByIndex(i)) * 10.)) / 10.;
                                  if (lastTemperature[i] != temperature && temperature != -127.00) {
                                    gw.send(msg.setSensor(i).set(temperature,1));
                                  Right?
                                  Is the temperature changing every minute??
                                  • H Offline
                                    H Offline
                                    Hausner
                                    @daulagari
                                    By 1-way node I mean a reporting node. It only reports a temperature, nothing else. So therefore 1 way traffic TO the GW/controller.
                                    A relay node on the other hand has to receive also, else you can't flip on/off the relays.
                                    This is roughly 1 minute worth of controller log:
                                     2014-11-13 04:49:27 - Helena_temp_LastUpdate state updated to 2014-11-13T04:49:27
                                     2014-11-13 04:49:28 - Temperature_GF_Helena state updated to 26.7
                                     2014-11-13 04:49:28 - Helena_temp_LastUpdate state updated to 2014-11-13T04:49:28
                                     2014-11-13 04:49:29 - Temperature_GF_Helena state updated to 26.6
                                     2014-11-13 04:49:29 - Helena_temp_LastUpdate state updated to 2014-11-13T04:49:29
                                     2014-11-13 04:49:30 - Temperature_GF_Helena state updated to 26.7
                                     2014-11-13 04:49:30 - Helena_temp_LastUpdate state updated to 2014-11-13T04:49:30
                                     2014-11-13 04:49:39 - Temperature_GF_Helena state updated to 26.6
                                     2014-11-13 04:49:39 - Helena_temp_LastUpdate state updated to 2014-11-13T04:49:39
                                     2014-11-13 04:50:07 - Temperature_GF_Living state updated to 24.3
                                     2014-11-13 04:50:07 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:07
                                     2014-11-13 04:50:08 - Temperature_GF_Living state updated to 24.2
                                     2014-11-13 04:50:08 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:08
                                     2014-11-13 04:50:12 - Temperature_GF_Living state updated to 24.3
                                     2014-11-13 04:50:12 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:12
                                     2014-11-13 04:50:14 - Temperature_GF_Living state updated to 24.2
                                     2014-11-13 04:50:14 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:14
                                     2014-11-13 04:50:15 - Temperature_GF_Helena state updated to 26.7
                                     2014-11-13 04:50:15 - Helena_temp_LastUpdate state updated to 2014-11-13T04:50:15
                                     2014-11-13 04:50:16 - Temperature_GF_Helena state updated to 26.6
                                     2014-11-13 04:50:16 - Helena_temp_LastUpdate state updated to 2014-11-13T04:50:16
                                     2014-11-13 04:50:16 - Temperature_GF_Living state updated to 24.3
                                     2014-11-13 04:50:16 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:16
                                     2014-11-13 04:50:16 - Temperature_GF_Living state updated to 24.2
                                     2014-11-13 04:50:18 - Temperature_GF_Living state updated to 24.3
                                     2014-11-13 04:50:18 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:18
                                     2014-11-13 04:50:19 - Temperature_GF_Helena state updated to 26.7
                                     2014-11-13 04:50:19 - Helena_temp_LastUpdate state updated to 2014-11-13T04:50:19
                                     2014-11-13 04:50:20 - Temperature_GF_Helena state updated to 26.6
                                     2014-11-13 04:50:20 - Helena_temp_LastUpdate state updated to 2014-11-13T04:50:20
                                     2014-11-13 04:50:20 - Temperature_GF_Living state updated to 24.2
                                     2014-11-13 04:50:20 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:20
                                     2014-11-13 04:50:20 - Temperature_GF_Helena state updated to 26.7
                                     2014-11-13 04:50:20 - Temperature_GF_Living state updated to 24.3
                                     2014-11-13 04:50:22 - Temperature_GF_Helena state updated to 26.6
                                     2014-11-13 04:50:22 - Helena_temp_LastUpdate state updated to 2014-11-13T04:50:22
                                     2014-11-13 04:50:23 - Temperature_GF_Living state updated to 24.2
                                     2014-11-13 04:50:23 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:23
                                     2014-11-13 04:50:24 - Temperature_GF_Living state updated to 24.3
                                     2014-11-13 04:50:24 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:24
                                     2014-11-13 04:50:26 - Temperature_GF_Helena state updated to 26.7
                                     2014-11-13 04:50:26 - Helena_temp_LastUpdate state updated to 2014-11-13T04:50:26
                                     2014-11-13 04:50:26 - Temperature_GF_Living state updated to 24.2
                                     2014-11-13 04:50:26 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:26
                                     2014-11-13 04:50:27 - Temperature_GF_Living state updated to 24.3
                                     2014-11-13 04:50:27 - Living_temp_LastUpdate state updated to 2014-11-13T04:50:27
                                     2014-11-13 04:50:29 - Temperature_GF_Helena state updated to 26.6
                                     2014-11-13 04:50:29 - Helena_temp_LastUpdate state updated to 2014-11-13T04:50:29
                                    As you can see i'm getting way more than 1 reading a second. I think this is happening because of the rounding up/down of the temperature readings.
                                    P 1 Reply Last reply
                                    • H Offline
                                      H Offline
                                      wrote on last edited by hek
                                      Please post your sketch code. And to which pins you have connected sensors.
                                      • H Offline
                                        H Offline
                                        Hausner
                                        Temperatur sensor
                                         // Example sketch showing how to send in OneWire temperature readings
                                         #include <OneWire.h>
                                         int numSensors=0;
                                         boolean receivedConfig = false;
                                         boolean metric = true;
                                         MyMessage msg(0,V_TEMP);
                                         //int BATTERY_SENSE_PIN = A0; // select the input pin for the battery sense point
                                         //int oldBatteryPcnt = 0;
                                           // Startup OneWire
                                           sensors.begin();
                                           // Startup and initialize MySensors library. Set callback for incoming messages.
                                           gw.begin();
                                           gw.sendSketchInfo("Temperature Sensor", "1.0");
                                              gw.present(i, S_TEMP);
                                           //analogReference(INTERNAL);
                                           // Process incoming messages (like config from server)
                                           float temperature = static_cast<float>(static_cast<int>  ((gw.getConfig().isMetric?sensors.getTempCByIndex(i):sensors.getTempFByIndex(i)) * 10.)) / 10.;
                                        // get the battery Voltage
                                        //int sensorValue = analogRead(BATTERY_SENSE_PIN);
                                        //Serial.println(sensorValue);
                                        //float batteryV = sensorValue * 0.004106;
                                        //int batteryPcnt = sensorValue / 10;
                                         //Serial.print("Battery Voltage: ");
                                           //Serial.print(batteryV);
                                           //Serial.println(" V");
                                           //Serial.print("Battery percent: ");
                                           //Serial.print(batteryPcnt);
                                           //Serial.println(" %");
                                           //if (oldBatteryPcnt != batteryPcnt) {
                                           // Power up radio after sleep
                                           //gw.sendBatteryLevel(batteryPcnt);
                                           //oldBatteryPcnt = batteryPcnt;
                                           //gw.sleep(SLEEP_TIME);
                                        The temp sensor has been build according to this: http://mysensors.org/build/temp
                                        1 small exception though. I have used 5v->3.3v aparters for the radios, but that shouldn't matter.
                                        10Pcs-lot-Socket-Adapter-Plate-Board-For-8Pin-NRF24L01-Wireless-Transceive-Module-51-Free-Shipping.jpg
                                        • H Hausner
                                          Temperatur sensor
                                           int numSensors=0;
                                             // Startup OneWire
                                             sensors.begin();
                                             gw.begin();
                                          H Offline
                                          H Offline
                                          Why did you comment away this line?
                                          12.2k