  3. Sensor for Vallox DigitSE RS485 ventilation system with integration into FHEM.
rs485valloxfhem
36 Posts 12 Posters 27.7k Views 12 Watching
  • HeinzH Heinz
    After some months of testing a little update:
    I received some e-mails questioning the so called "heat recovery cell bypass" mode. There is a damper inside the device that can
    is switched automatically by the vallox-controller to bypass the heat recovery cell (HRC) to avoid heating up the house during the
    summer months. Well, when you open the device on a hot summer day you will probably see the damper in an obvious wrong position:
    the air does not bypass the HRC! Huh! whats wrong here?
    Explanation:
    The device tries to cool down the incoming air by leading it through the HRC which is still colder than the temperature outside. If the temperature outside is colder than the air inside the house the damper is switched to the expected position. There are two things to you have to do to make all that work correctly:
    • turn off heating mode (the LED of the left most button on your control device must be off)
    • the HRC bypass temperature must be set to a value below the outside temperature (e.g. 14 degrees)
    To illustrate that effect I logged the temperatures in FHEM:
    Sorry for the german labels.
    The first plot shows the damper position: blue background: HRC bypass is active.
    The second plot shows the temperature outside the house (blue) and the temperature inside the house (red)
    As soon as the temperature outside is greater than the temperature inside the HRC bypass is deactivated to cool the incoming air by leading the air through the "colder" HRC.
    The fourth diagram shows the temperature of the air that is entering the rooms (purple) and the temperature outside the house (blue).
    You can see that the fresh air entering the rooms is lower than the temperature outside: the cooling effect works (even if it is only few degrees)
    To all guys thinking about how to control the damper on their own logic from a raspi or arduino. This is not neccessary as the vallox logic works very well.
    m26872M
    m26872M
    m26872
    @Heinz What Fhem plot style and font are you using?
    • HeinzH
      HeinzH
      Heinz
      @m26872
      I modified the dark style. If you need the files I will upload em with a description how to integrate those.
      m26872M 1 Reply Last reply
      • HeinzH Heinz
        @m26872
        m26872M
        m26872M
        m26872
        @Heinz Yes please! I really liked those plots.
        I wouldn't mind it in german (as usual with Fhem stuff), but it's a lot easier for me with english.
        • HeinzH
          HeinzH
          Heinz
          wrote on last edited by Heinz
          @m26872
          I simply copied the dark style of FHEM and named it dark2:
          copy the following files to your FHEM subfolder www/pgm2
          dark2style.css
          dark2svg_defs.svg
          dark2svg_style.css
          In your FHEM.cfg select this style for your WEB Frontend e.g.:
          define WEB FHEMWEB 8083 global
          attr WEB stylesheetPrefix dark2
          That's it.
          If you want to have other plot colours edit the files starting with dark2svg... I think it is self explaining.
          • HeinzH
            HeinzH
            Heinz
            For those who want to have the FHEM files here they are:
            _MYSENSOR_Vallox.cfg
            simply place the file in FHEM's subfolder FHEM and include it your fhem.cfg:
            include ./FHEM/_MYSENSOR_Vallox.cfg
            And here are the plot files which have to be placed in the subfolder www\gplot
            SVG_FileLog_Vallox_6.gplot
            SVG_FileLog_Vallox_5.gplot
            SVG_FileLog_Vallox_4.gplot
            SVG_FileLog_Vallox_3.gplot
            SVG_FileLog_Vallox_2.gplot
            SVG_FileLog_Vallox_1.gplot
            You will likely have to adapt the room and group names, and of course the german names, sorry for that.
            m26872M ausbremenA 3 Replies Last reply
            • HeinzH Heinz
              m26872M
              m26872M
              m26872
              @Heinz
              Nice! Now I really want to buy a Vallox ... (and a house...)
              • SkjallS
                SkjallS
                Skjall
                Moin @Heinz,
                is it possible to use a RS485 USB-Stick (http://shop.in-circuit.de/product_info.php?cPath=38&products_id=81) instead of this construction? I've tried it with your .net Sniffer on my Windows PC and it worked well.
                Skjall
                • HeinzH
                  HeinzH
                  Heinz
                  You can use this rs485 to usb adapter to control the vallox device, no problem there. But do you intend to use your windows pc as controller then? Or do you want to use the stick directly with fhem? this would require some software which takes the serial telegrams and imports the values into fhem... or any other homeautomation controller.
                  • SkjallS
                    SkjallS
                    Skjall
                    wrote on last edited by Skjall
                    #21
                    No, the Windows PC was only for testing and verifying that the RS485 Connection workes well.
                    My preferred solution would be this stick at the Raspberry Pi which is running the FHEM. Therefor I'd need a module to read the stream and interpret it in the FHEM format. Problem: I've never written a module. It would be possible somehow.. in some month. ;)
                    The alternate solution would be your mysensor system. Especially because its running and tested. Problem: The Hardware. I have no experience in arduino and absolutly no idea how to build such a board. Thats why I thought I could plug the stick to an arduino and make it magicly work. ;)
                    EDIT: Ok. It is easier than I thought to write this module. I'm working on it and the main functions should be finished this week. I'll publish it, if it is ready for testing.
                    HeinzH 1 Reply Last reply
                    • SkjallS Skjall
                      HeinzH
                      HeinzH
                      Heinz
                      Ah ok I see. Probably you can get some help in the fhem forum. I also thought about doing this using a raspi... you could use the library to write a standalone exe which reads the serial stuff from usb and sets the values in fhem using the webinterface.
                      • B
                        B
                        boehrian
                        Hello, Thank you for this Tool. I have rebuild it but I get no Data in Fhem and the serial Monitor from Arduino. Can every one help me?
                        0_1488198457149_upload-35f8091f-da2a-4c43-ab73-7574f41a77b4
                        This is the output from serial Monitor.
                        • HeinzH
                          HeinzH
                          Heinz
                          here is my output:
                          Opening port
                          Port open
                          Starting repeater (RNNRA-, 2.0.0)
                          TSM:INIT
                          TSM:RADIO:OK
                          TSP:ASSIGNID:OK (ID=100)
                          TSM:FPAR
                          TSP:MSG:SEND 100-100-255-255 s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=bc:
                          TSP:MSG:READ 1-1-100 s=255,c=3,t=8,pt=1,l=1,sg=0:1
                          TSP:MSG:FPAR RES (ID=1, dist=1)
                          TSP:MSG:PAR OK (ID=1, dist=2)
                          TSP:MSG:READ 0-0-100 s=255,c=3,t=8,pt=1,l=1,sg=0:0
                          TSP:MSG:PAR OK (ID=0, dist=1)
                          TSP:MSG:READ 104-104-100 s=255,c=3,t=8,pt=1,l=1,sg=0:1
                          TSP:MSG:FPAR RES (ID=104, dist=1)
                          TSM:FPAR:OK
                          TSM:ID
                          TSM:CHKID:OK (ID=100)
                          TSM:UPL
                          TSP:PING:SEND (dest=0)
                          TSP:MSG:SEND 100-100-0-0 s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=ok:1
                          TSP:MSG:READ 0-0-100 s=255,c=3,t=25,pt=1,l=1,sg=0:1
                          TSP:MSG:PONG RECV (hops=1)
                          TSP:CHKUPL:OK
                          TSM:UPL:OK
                          TSM:READY
                          TSP:MSG:SEND 100-100-0-0 s=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=ok:0100
                          !TSP:MSG:SEND 100-100-0-0 s=255,c=0,t=18,pt=0,l=5,sg=0,ft=0,st=fail:2.0.0
                          TSP:MSG:SEND 100-100-0-0 s=255,c=3,t=6,pt=1,l=1,sg=0,ft=1,st=ok:0
                          TSP:MSG:READ 0-0-100 s=255,c=3,t=6,pt=0,l=1,sg=0:M
                          TSP:MSG:SEND 100-100-0-0 s=255,c=3,t=11,pt=0,l=15,sg=0,ft=0,st=ok:Vallox Digit SE
                          TSP:MSG:SEND 100-100-0-0 s=255,c=3,t=12,pt=0,l=3,sg=0,ft=0,st=ok:2.5
                          TSP:MSG:SEND 100-100-0-0 s=0,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=1,c=0,t=6,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=2,c=0,t=6,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=3,c=0,t=6,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=4,c=0,t=6,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=5,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=6,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=7,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=8,c=0,t=3,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=9,c=0,t=3,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=10,c=0,t=3,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=11,c=0,t=3,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=12,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=13,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=14,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=15,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=24,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=25,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=26,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=27,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=28,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=29,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=30,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=31,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=32,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=33,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=34,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=35,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=36,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=37,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=38,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=39,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=40,c=0,t=4,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=41,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=42,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=43,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=44,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=45,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=46,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=47,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=48,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          TSP:MSG:SEND 100-100-0-0 s=49,c=0,t=23,pt=0,l=0,sg=0,ft=0,st=ok:
                          Started cyclic update timer.
                          Request registration...
                          TSP:MSG:SEND 100-100-0-0 s=255,c=3,t=26,pt=1,l=1,sg=0,ft=0,st=ok:2
                          TSP:MSG:READ 0-0-100 s=255,c=3,t=27,pt=1,l=1,sg=0:1
                          Node registration=1
                          Init complete, id=100, parent=0, distance=1, registration=1
                          Dropped 0
                          Received telegram from 21->11 command=0 arg=A3
                          Received telegram from 11->21 command=A3 arg=29
                          Property 200 changed 41
                          Power state 1
                          TSP:MSG:SEND 100-100-0-0 s=8,c=1,t=2,pt=2,l=2,sg=0,ft=0,st=ok:1
                          CO2 adjust state 0
                          TSP:MSG:SEND 100-100-0-0 s=9,c=1,t=2,pt=2,l=2,sg=0,ft=0,st=ok:0
                          Humidity adjust state 0
                          TSP:MSG:SEND 100-100-0-0 s=10,c=1,t=2,pt=2,l=2,sg=0,ft=0,st=ok:0
                          Heating state 1
                          TSP:MSG:SEND 100-100-0-0 s=11,c=1,t=2,pt=2,l=2,sg=0,ft=0,st=ok:1
                          Filter guard indicator 0
                          TSP:MSG:SEND 100-100-0-0 s=12,c=1,t=24,pt=2,l=2,sg=0,ft=0,st=ok:0
                          Heating indicator 1
                          TSP:MSG:SEND 100-100-0-0 s=13,c=1,t=24,pt=2,l=2,sg=0,ft=0,st=ok:1
                          Fault indicator 0
                          TSP:MSG:SEND 100-100-0-0 s=14,c=1,t=24,pt=2,l=2,sg=0,ft=0,st=ok:0
                          Serivce reminder indicator 0
                          TSP:MSG:SEND 100-100-0-0 s=15,c=1,t=24,pt=2,l=2,sg=0,ft=0,st=ok:0
                          Received telegram from 21->11 command=0 arg=29
                          Received telegram from 11->21 command=29 arg=1
                          Received telegram from 21->11 command=0 arg=35
                          Received telegram from 11->21 command=35 arg=9D
                          Temp incomming 19
                          TSP:MSG:SEND 100-100-0-0 s=4,c=1,t=0,pt=2,l=2,sg=0,ft=0,st=ok:19
                          Received telegram from 21->11 command=0 arg=71
                          Received telegram from 11->21 command=71 arg=0
                          This is the output of the mysensors 2.0 version which can be downloaded from
                          https://github.com/windkh/mysensors/tree/master/ValloxSensor
                          I wonder why your node has id=0.
                          • B
                            B
                            boehrian
                            Hi, my output ist now:
                            0 MCO:BGN:INIT REPEATER,CP=RNNRA--,VER=2.1.1
                            3 TSM:INIT
                            4 TSF:WUR:MS=0
                            12 TSM:INIT:TSP OK
                            13 TSF:SID:OK,ID=42
                            15 TSM:FPAR
                            52 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                            2059 !TSM:FPAR:NO REPLY
                            2061 TSM:FPAR
                            2098 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                            4105 !TSM:FPAR:NO REPLY
                            4107 TSM:FPAR
                            4143 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                            6151 !TSM:FPAR:NO REPLY
                            6153 TSM:FPAR
                            6189 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                            8197 !TSM:FPAR:FAIL
                            8198 TSM:FAIL:CNT=1
                            8200 TSM:FAIL:PDT
                            18203 TSM:FAIL:RE-INIT
                            18205 TSM:INIT
                            18212 TSM:INIT:TSP OK
                            18214 TSF:SID:OK,ID=42
                            18216 TSM:FPAR
                            18253 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                            20261 !TSM:FPAR:NO REPLY
                            20263 TSM:FPAR
                            20300 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                            22307 !TSM:FPAR:NO REPLY
                            22309 TSM:FPAR
                            22346 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                            24353 !TSM:FPAR:NO REPLY
                            24355 TSM:FPAR
                            24392 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                            I get no reply from the Vallox.
                            Is your original Vallox controller online
                            • HeinzH
                              HeinzH
                              Heinz
                              #26
                              The "no reply" message is from the mysensors library, but I don't know what it means.
                              The line "started cyclic update timer" indicates that the sensor initialized successfully, but it is missing in your output.
                              My latest code is online at
                              https://github.com/windkh/valloxserial/blob/master/examples/mysensors/ValloxSensor.ino
                                Use the log parser to help you interpret the log.
                                • HeinzH Heinz
                                  ausbremenA
                                  ausbremenA
                                  ausbremen
                                  @heinz
                                  Hi Heinz, the SVG_FileLog_Vallox_#.gplot files are empty ...probably the link is dead...could you reup them? Or could you send them tio me?
                                  Thanks, Holger
                                  • HeinzH Heinz
                                    ausbremenA
                                    ausbremenA
                                    ausbremen
                                    @heinz
                                    Sorry...everything is fine with the gplot files...it was my fault trying to look at them with the crimpson editor...instead of FHEM gplot
                                    • C
                                      C
                                      captaindork
                                      Hello Heinz, all,
                                      first of all thank you for sharing your work in this thread!
                                      I have not to much skills around programming and arduino, but was however able to build this and integrate my Vallox 90 SE into ioBroker. Absolutely Great!
                                      You mentioned the bypass damper above and I see you have visualized it in fhem. I found the Value to set the Threshold temp for this (31), however I wonder where you got the actual bypass position from. Which Value shows if its open or closed?
                                      I do not want to control it, i just would like to log the Position Status to see when it happens.
                                      Thanks a lot i feel blind :)
                                      • C captaindork
                                        Hello Heinz, all,
                                        HeinzH
                                        HeinzH
                                        Heinz
                                        Hi @captaindork
                                        sorry for delay,.... the position of the damper (which is the bypass) is indicated through a single bit of the multi purpose IO-Port 2. The library defines that as property 38 DamperMotorPositionProperty.
                                        In the mysensors example it is published as
                                        const uint8_t DAMPER_MOTOR_POSITION = 42;
                                        The value is either 1 or 0.
                                        I mapped it in FHEM as follows
                                        attr MYSENSOR_Vallox mapReading_DamperMotorPosition 42 value1
                                        define MYSENSOR_Vallox_DamperMotorPosition dummy
                                        attr MYSENSOR_Vallox_DamperMotorPosition alias WRG-Bypass
                                        attr MYSENSOR_Vallox_DamperMotorPosition devStateIcon 1:rc_GREEN 0:rc_BLANK
                                        attr MYSENSOR_Vallox_DamperMotorPosition event-on-update-reading state
                                        attr MYSENSOR_Vallox_DamperMotorPosition group Status
                                        attr MYSENSOR_Vallox_DamperMotorPosition icon vent_bypass
                                        attr MYSENSOR_Vallox_DamperMotorPosition room Lüftung
                                        attr MYSENSOR_Vallox_DamperMotorPosition sortby 3
                                        define MYSENSOR_Vallox_DamperMotorPosition_Notify notify MYSENSOR_Vallox:DamperMotorPosition:.* { my $d = sprintf ("%.0f", ReadingsVal("MYSENSOR_Vallox","DamperMotorPosition", 0));; fhem("set MYSENSOR_Vallox_DamperMotorPosition $d");;}
                                        define MYSENSOR_Vallox_DamperMotorPosition_Notify2 at +*00:01:00 { my $d = sprintf "%.0f", ReadingsVal("MYSENSOR_Vallox","DamperMotorPosition", 0);; fhem("set MYSENSOR_Vallox_DamperMotorPosition $d");;}
                                        • R
                                          R
                                          RHead
                                          Hi.
                                          Can you make exact parts list for this setup.