    Hi Yveaux. To my opinion it is not necesarry for the library to do the buffering.
    I'm looking for an option where the node enters void loop() even if there is no gateway when the node boots, so it can do things locally.
    Because there is no gateway, it is not possible to send or receive messages. It is no problem if they get lost.
    For the node a user can create a buffer for messages that should be reported when the nodes detects a gateway is available.
    The function isTransportOK() can for instance be use to discover if a gateway is available.
    So I think it is only necesarry to implement an option to enter void(loop) when no gateway is detected and periodically try to register to the gateway.
    I think what @eric_smid suggests can be an important feature. The manual control must work, even if the gateway is temporarily out of order. Otherwise the rest of the family will complain a lot.
    TheoLT 1 Reply Last reply
      TheoLT
      TheoLT
      TheoL
      wrote on last edited by TheoL
      @mfalkvidd @Yveaux There was a similar discussion a couple of weeks ago. The gateway should always be reachable. Unless there's a power cut. But to be honest I don't know what happens then. Might take a couple of hours before my network is completely healed. Because the nodes might come up earlier than the gateway once the power is back on. Also the gateway might not be able to handle all the node registrations. But in those cases nodes need to register themselves with a random delay. Just to give the gateway the time to handle the load. Because I'm not convinced it can.
      My personal statement is: Devices should work independently from your home automation if they are a vital part of your life. Like light and so. Home Automation and IoT should enhance your life, and not take over your life.
      And to be honest. I don't see the need of buffering messages. Because the messages you'll be buffering might already be outdated when the gateway and your controller come up again. Meaning you could have switched the lights on and then off. So what would be the value of buffering the outdated data? We should just simply accept the fact that we've lost some sensor values. The data can be interpolated in the long run anyway. Which Domoticz already does, when it shows you the graphs.
      I can't remember the last power cut we had over here. So to me losing some sensor values in a situation like that is acceptable. Certainly if all of my MySensors devices will keep working in a situation like this. Then loosing data isn't that bad.
      This is also the reason why you should send the current state of sensors and actors on a regular basis to you controller. That way the controller and the nodes will be in synch again at some time, after a power cut.
      This feature would indeed help us in creating a solution which enhances our lives instead of the opposite. But that's just my 50 cents. Curious how Z-waves handles this?
      • eric_smidE
        eric_smidE
        eric_smid
        I have Z-wave modules (Fibaro) installed. The switches can be used without gateway.
        When the gateway boots (I use Razzberry) it start detecting the nodes. I assume it it is up to the nodes to send the current state.
        I agree that buffering messages is useless in most cases. A periodic update (initiated by the user program) is in my opinion the correct solution.
        • sundberg84S
          sundberg84S
          I would love to see an start on this - maybe a relay example that works without the gateway. As @TheoL said, lights - and i think thats one end to start. The best would offcourse be to make some generic thing that works for all nodes.
          • Bogdan BrezuicaB
            Bogdan BrezuicaB
            Bogdan Brezuica
            I have the same issue with a gas sensor. I would really like the buzzer to sound even if the gateway is unreachable. Letting the home automation know there is a gas leak in order to take other measures wold be optimal but sounding the alarm is mandatory.
              It's only during startup the node does a handshake with the parent node (which can be disabled using MY_TRANSPORT_DONT_CARE_MODE in dev branch). During normal operation the library never block even if communication link is down.
              tekkaT TheoLT 2 Replies Last reply
                tekkaT
                tekkaT
                tekka
                Important: enabling MY_TRANSPORT_DONT_CARE_MODE requires setting MY_PARENT_NODE_ID
                • eric_smidE
                  eric_smidE
                  eric_smid
                  Great this option is available!
                  Is it possible to let the node use the last used parent, instead of configuring the parent?
                  tekkaT 1 Reply Last reply
                    tekkaT
                    tekkaT
                    tekka
                    @eric_smid No, not in the current implementation
                      TheoLT
                      TheoLT
                      TheoL
                      @hek Just curious. How important is the handshake? Because if it's important I think it would be a good option, to let node's do a delayed hand shake when the initial one fails. So that they can continue, but just won't use the my sensors part until a delayed handshake is done.
                      A delayed hand shake would only be needed when there's a power cut.
                      H 1 Reply Last reply
                      • TheoLT TheoL
                        H
                        H
                        Heizelmann
                        Coming from this thread, where I learned that an implementation of this feature is in progress.
                        In my opinion it is an essential architectural feature. Reasons for this you can see above.
                        Here I summarize what I think is necessary:
                        General requirements
                        • Devices should work independently from the gateway
                        • Enter loop() even if gateway is not reachable
                        • Buffering of messages not necessary. Its up to the user to implement this.
                        Needed functionality
                        • retrieve available gateways (gets a list of available gateways)
                        • request to register ( gets success or failure with reason)
                        • de-register ( gets success or failure with reason)
                        D 1 Reply Last reply
                        • H Heizelmann
                          DavidZH
                          @Heizelmann
                          I've been thinking about his as well. Probably for different reasons though.
                          I find myself with time to spare and my laptop at hand quite often, but I'm not home at those moments. I'd love to be able to write code and test sensors at those times, but that's impossible because there's no gateway.
                          For that I'd like to propose a "Test Mode".
                          • test port to Transport.
                          • NO connection to gateway.
                          • simulate the Transport calls in the sketch with just a line in the debug with ACK.
                          • when possible: send "messages" to node with the Arduino serial monitor.
                          I am aware that this might pose some biiiiiiig changes in the lib. So this might be something for the 2.5 or 3.0 release.
                          Thoughts?
                          • D DavidZH
                            @Heizelmann
                            Thoughts?
                            H
                            H
                            Heizelmann
                            I am now ready with my node and I need the non-blocking feature urgently. Is there an estimation when this feature will be come or can anyone provide a workaround?
                              If you use the development branch and want to prohibit the registration wait. Add
                              #define MY_TRANSPORT_WAIT_READY_MS 1
                              @tekka, correct me if I'm wrong please ;)
                                tekkaT
                                tekkaT
                                tekka
                                @hek correct :+1:
                                @Heizelmann Would be good to get some feedback on this feature, please let us know how it works in your hands.
                                H eric_smidE 2 Replies Last reply
                                • tekkaT tekka
                                  @hek correct :+1:
                                  H
                                  H
                                  Heizelmann
                                  Here my report after a quick test.
                                  To say it short: Generally I am happy with it, it works very well. Only one small problem.
                                  In detail:
                                  When connection is initially off, the sketch entered after the defined wait the loop.
                                  before()
                                  5 TSM:INIT
                                  7 TSF:WUR:MS=1000
                                  13 !TSM:INIT:TSP FAIL
                                  15 TSM:FAIL:CNT=1
                                  17 TSM:FAIL:PDT
                                  1008 MCO:BGN:STP
                                  Setup()
                                  1510 MCO:BGN:INIT OK,TSP=0
                                  If the sketch tries to send within the loop a message is logged.
                                  145312 !MCO:SND:NODE NOT REG
                                  If connection comes back the sketch connects to the gateway on the fly within the defined wait time.
                                  244251 TSM:FPAR:OK
                                  244252 TSM:ID
                                  244254 TSM:ID:OK
                                  244255 TSM:UPL
                                  244259 TSF:MSG:SEND,42-42-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=OK:1
                                  244265 TSF:MSG:READ,0-0-42,s=255,c=3,t=25,pt=1,l=1,sg=0:1
                                  244271 TSF:MSG:PONG RECV,HP=1
                                  244274 TSM:UPL:OK
                                  244276 TSM:READY:ID=42,PAR=0,DIS=1
                                  244281 TSF:MSG:SEND,42-42-0-0,s=255,c=3,t=15,pt=6,l=2,sg=0,ft=0,st=OK:0100
                                  244288 TSF:MSG:READ,0-0-42,s=255,c=3,t=15,pt=6,l=2,sg=0:0100
                                  244295 TSF:MSG:SEND,42-42-0-0,s=255,c=0,t=17,pt=0,l=10,sg=0,ft=0,st=OK:2.1.0-beta
                                  244304 TSF:MSG:SEND,42-42-0-0,s=255,c=3,t=6,pt=1,l=1,sg=0,ft=0,st=OK:0
                                  244321 TSF:MSG:READ,0-0-42,s=255,c=3,t=6,pt=0,l=1,sg=0:M
                                  Presentation()
                                  244329 TSF:MSG:SEND,42-42-0-0,s=255,c=3,t=11,pt=0,l=22,sg=0,ft=0,st=OK:My Node
                                  244339 TSF:MSG:SEND,42-42-0-0,s=255,c=3,t=12,pt=0,l=3,sg=0,ft=0,st=OK:1.2
                                  244347 TSF:MSG:SEND,42-42-0-0,s=1,c=0,t=1,pt=0,l=0,sg=0,ft=0,st=OK:
                                  244356 TSF:MSG:SEND,42-42-0-0,s=2,c=0,t=1,pt=0,l=0,sg=0,ft=0,st=OK:
                                  244364 TSF:MSG:SEND,42-42-0-0,s=3,c=0,t=3,pt=0,l=0,sg=0,ft=0,st=OK:
                                  244370 MCO:REG:REQ
                                  244373 TSF:MSG:SEND,42-42-0-0,s=255,c=3,t=26,pt=1,l=1,sg=0,ft=0,st=OK:2
                                  244380 TSF:MSG:READ,0-0-42,s=255,c=3,t=27,pt=1,l=1,sg=0:1
                                  244385 MCO:PIM:NODE REG=1
                                  Only problem is that you get high logging traffic in the case when you are in loop and network connection gets lost again as long as the connection is lost.
                                  605458 TSF:MSG:READ,1-1-1,s=1,c=1,t=1,pt=0,l=0,sg=0:
                                  605463 !TSF:MSG:LEN,0!=7
                                  605465 TSF:MSG:READ,1-1-1,s=1,c=1,t=1,pt=0,l=0,sg=0:
                                  605470 !TSF:MSG:LEN,0!=7
                                  605472 TSF:MSG:READ,1-1-1,s=1,c=1,t=1,pt=0,l=0,sg=0:
                                  605477 !TSF:MSG:LEN,0!=7
                                  • H Heizelmann
                                    In detail:
                                    before()
                                    5 TSM:INIT
                                    7 TSF:WUR:MS=1000
                                    15 TSM:FAIL:CNT=1
                                    17 TSM:FAIL:PDT
                                    1008 MCO:BGN:STP
                                    Setup()
                                    244251 TSM:FPAR:OK
                                    244252 TSM:ID
                                    244254 TSM:ID:OK
                                    244255 TSM:UPL
                                    244274 TSM:UPL:OK
                                    Presentation()
                                    244370 MCO:REG:REQ
                                    tekkaT
                                    tekkaT
                                    tekka
                                    wrote on last edited by tekka
                                    @Heizelmann Thanks for your testing. I couldn't reproduce this behavior, can you post your sketch for further analysis?
                                    • tekkaT tekka
                                      H
                                      H
                                      Heizelmann
                                      wrote on last edited by Heizelmann
                                      #21
                                      @tekka May be it is the kind of my testing. For getting quick results I simply plug and un-plug the radio module (NRF24L01+) from the socket in my sensor node. I know, this is not a real use case but it was easy and I didn't thought there is adifference in behaviour. How do you you switch off and on the network connection in your test?
                                      • H Heizelmann
                                        tekkaT
                                        tekkaT
                                        tekka
                                        @Heizelmann yes, unplugging the radio results in what you observed. Simply unplug the GW (and repeaters)...
                                        • tekkaT tekka
                                          H
                                          H
                                          Heizelmann
                                          #23
                                          @tekka OK unplugging the GW leads to a different behaviour.
                                          First the node didn't detect the failure as long it is not trying to send.
                                          When it tries to send it fails
                                          131268 !TSF:MSG:SEND,42-42-0-0,s=1,c=1,t=16,pt=0,l=1,sg=0,ft=0,st=NACK:1
                                          and after some more failure this
                                          238494 !TSM:READY:UPL FAIL,SNP
                                          238497 TSM:FPAR
                                          238534 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=6,st=OK:
                                          238995 !TSF:SND:TNR
                                          240002 !TSF:SND:TNR
                                          240542 !TSM:FPAR:NO REPLY
                                          240544 TSM:FPAR
                                          240581 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                                          246683 !TSM:FPAR:FAIL
                                          246685 TSM:FAIL:CNT=1
                                          246687 TSM:FAIL:PDT
                                          and after a while mostly only
                                          609748 !TSF:SND:TNR
                                          When gateway comes back a proper reinitialization takes place:
                                          620572 TSM:FAIL:RE-INIT
                                          620574 TSM:INIT
                                          620581 TSM:INIT:TSP OK
                                          620583 TSM:INIT:STATID=42
                                          620587 TSF:SID:OK,ID=42
                                          620589 TSM:FPAR
                                          620625 TSF:MSG:SEND,42-42-255-255,s=255,c=3,t=7,pt=0,l=0,sg=0,ft=0,st=OK:
                                          Current: 0.00
                                          0:0:0
                                          Current: 0.00
                                          0:0:0
                                          621443 TSF:MSG:READ,0-0-42,s=255,c=3,t=8,pt=1,l=1,sg=0:0
                                          621448 TSF:MSG:FPAR OK,ID=0,D=1
                                          Current: 0.00
                                          0:0:0
                                          Current: 0.00
                                          0:0:0
                                          622633 TSM:FPAR:OK
                                          622635 TSM:ID
                                          622637 TSM:ID:OK
                                          622638 TSM:UPL
                                          622642 TSF:MSG:SEND,42-42-0-0,s=255,c=3,t=24,pt=1,l=1,sg=0,ft=0,st=OK:1
                                          622652 TSF:MSG:READ,0-0-42,s=255,c=3,t=25,pt=1,l=1,sg=0:1
                                          622657 TSF:MSG:PONG RECV,HP=1
                                          622660 TSM:UPL:OK
                                          622662 TSM:READY:ID=42,PAR=0,DIS=1
                                          From now the sensor can send again without errors. :smiley:
                                          So far my tests.
                                          Except the case where the radio of the sensor went off and causes a lot of logging all test cases where satisfactorily.
                                          I think this is really an edge case and not so serious.
                                          From this point of view I would welcome that this beta development version will be published.