  4. Energy meter not updating watts.

Energy meter not updating watts.

Scheduled Pinned Locked Moved Vera
17 Posts 4 Posters 6.5k Views 1 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • I Offline
    I Offline
    integlikewhoa
    wrote on last edited by
    #5

    I think when I was using the tv remote it would flash like 4-5 times per each button I pressed so I'm sure the IR was just blinking like crazy.

    Here is my actual usage for yesterday.
    Energy.JPG

    1 Reply Last reply
    0
    • I Offline
      I Offline
      integlikewhoa
      wrote on last edited by
      #6

      Well it's defiantly my flash counts that's way off. I brought the laptop out to the meter and plugged in and got some valid info off the meter.
      my flashes are more then 1 every second with a/c running. I counted around 30 in 25 seconds using a stopwatch.

      During this time with sketch stock at 1000 it was reading.
      Watt:285,623

      Ofcourse I changed 1000 to 10,000 as suggested for a trial and it went to
      Watt:29,373

      and for kicks I wanted to get it into something more accurate so I changed it to 100,000
      Which is now reading and updating right in VERA (ofcourse since it's not over the max)
      Watt:2972

      So I guess the trick now is trying to figure out what each blink real value is on my meter.
      3,000 watts with 220v a/c running puts me around 13.6 amps.
      I'm thinking for a few lights on,TV, fridge, ceilings fans and 3.5 ton a/c this is reading low now.

      I don't have an amp clamp and havent figured out how to read this digital Itron OPENWAY Centron meter. It only has one button.

      1 Reply Last reply
      0
      • I Offline
        I Offline
        integlikewhoa
        wrote on last edited by
        #7

        Well I found out meter will read the kW in 2 decimal points. It was reading around 4.3kW with the ac running. Reading the serial seeing what it was outputting vs what the meter was reading I started adjusting the sketch then uploading then reseting the sensor and re reading the serial. I got it reading about spot on with 105000 flash per KWH.

        The. I shut off the AC kW reading on Meter went down to around 1.3 ish but the serial was showing 3,011 watts or something. So it didn't change in perportion. I do know the flashes slowed down but didn't recount yet to see just how much. Maybe 1 flash ever 2 seconds now. It definitely didn't cut it into quarters from 4kw to 1kw.

        1 Reply Last reply
        0
        • korttomaK Offline
          korttomaK Offline
          korttoma
          Hero Member
          wrote on last edited by
          #8

          nice to see you have worked out some of your issues.
          Seems to be tricky to get a pulse from the ITRON usually it says like 1000 imp/kwh or something similar beside the led on the meter and this should be pretty accurate.

          • Tomas
          I 1 Reply Last reply
          0
          • korttomaK korttoma

            nice to see you have worked out some of your issues.
            Seems to be tricky to get a pulse from the ITRON usually it says like 1000 imp/kwh or something similar beside the led on the meter and this should be pretty accurate.

            I Offline
            I Offline
            integlikewhoa
            wrote on last edited by
            #9

            @korttoma it sure doesn't seem like if fixed much.

            I'll include some pictures but I don't see anything anywhere on the meter that might give an indication of the pulses. And def. nothing around the IR. I'm also confused now how even when I got it reading right at higher usage. It didn't drop down much after I cut the usage and was still given a high reading.

            20141009_222916.jpg
            20141009_222937.jpg
            20141009_222930.jpg

            1 Reply Last reply
            0
            • JohnJ Offline
              JohnJ Offline
              John
              Plugin Developer
              wrote on last edited by John
              #10

              It looks like the calculation is off in the example sketch:

              Your meter is providing Kh, which renders the below calculation wrong (I think)

              watt = (3600000000.0 /interval) / ppwh;
              

              Your calculation should be

              watt = (3600000000.0 * ppwh) / interval;
              

              3600 (one hour) times the unit (1.0 Kh) devided by the time between two blinks.

              I could be wrong though because it is quick plain from the head.

              My Domotica project: http://www.pidome.org

              I 1 Reply Last reply
              0
              • JohnJ John

                It looks like the calculation is off in the example sketch:

                Your meter is providing Kh, which renders the below calculation wrong (I think)

                watt = (3600000000.0 /interval) / ppwh;
                

                Your calculation should be

                watt = (3600000000.0 * ppwh) / interval;
                

                3600 (one hour) times the unit (1.0 Kh) devided by the time between two blinks.

                I could be wrong though because it is quick plain from the head.

                I Offline
                I Offline
                integlikewhoa
                wrote on last edited by
                #11

                @John so I'm a bit lost (not surprised) at your formula. Can you throw some numbers in your new formula based on my information above (or fictitious numbers for an example) and give me an idea of what it should look like.

                1 Reply Last reply
                0
                • JohnJ Offline
                  JohnJ Offline
                  John
                  Plugin Developer
                  wrote on last edited by
                  #12

                  @integlikewhoa

                  Ok, let's say there are 4 seconds between each pulse, you would then have a formula like:

                  (3600 * 1.0) / 4 = 900 WATT
                  

                  An example if a blink takes 0.91 seconds

                  (3600 * 1.0) / 0.91 = 3956 WATT
                  

                  But like i said, i could be wrong ;)

                  My Domotica project: http://www.pidome.org

                  I 1 Reply Last reply
                  0
                  • JohnJ John

                    @integlikewhoa

                    Ok, let's say there are 4 seconds between each pulse, you would then have a formula like:

                    (3600 * 1.0) / 4 = 900 WATT
                    

                    An example if a blink takes 0.91 seconds

                    (3600 * 1.0) / 0.91 = 3956 WATT
                    

                    But like i said, i could be wrong ;)

                    I Offline
                    I Offline
                    integlikewhoa
                    wrote on last edited by
                    #13

                    @John said:

                    watt = (3600000000.0 * ppwh) / interval;

                    Well i put the Pulse count back to 1000 then I changed the formula above and now I'm getting some wierd up and down readings even tho the meter was fairly stable during this time.

                    sensor started, id 2
                    send: 2-2-0-0 s=255,c=0,t=17,pt=0,l=3,st=ok:1.4
                    send: 2-2-0-0 s=255,c=3,t=6,pt=1,l=1,st=ok:0
                    read: 0-0-2 s=255,c=3,t=6,pt=0,l=2:I
                    send: 2-2-0-0 s=255,c=3,t=11,pt=0,l=12,st=ok:Energy Meter
                    send: 2-2-0-0 s=255,c=3,t=12,pt=0,l=3,st=ok:1.0
                    send: 2-2-0-0 s=1,c=0,t=13,pt=0,l=3,st=ok:1.4
                    send: 2-2-0-0 s=1,c=2,t=24,pt=0,l=3,st=ok:1.4
                    read: 0-0-2 s=1,c=1,t=24,pt=0,l=6:81287
                    Received last pulse count from gw:81287
                    Watt:3609
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81316
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.3160
                    Watt:268656
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81351
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.3510
                    Watt:264861
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81389
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.3890
                    Watt:272975
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81415
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.4150
                    Watt:141464
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81421
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.4210
                    Watt:10582
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81448
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.4480
                    Watt:12944
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81471
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.4710
                    Watt:7069
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81473
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.4740
                    Watt:1215
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81479
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.4790
                    Watt:21161
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81510
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.5100
                    Watt:5983
                    send: 2-2-0-0 s=1,c=1,t=24,pt=5,l=4,st=ok:81529
                    send: 2-2-0-0 s=1,c=1,t=18,pt=7,l=5,st=ok:81.5290

                    1 Reply Last reply
                    0
                    • I Offline
                      I Offline
                      integlikewhoa
                      wrote on last edited by
                      #14

                      i'm so lost on this. I can read the screen on the meter. I got my meter holding down to around 1.31kW according to the meter read out. I set the timer for a minute and counted the flashes on the LM393 LED. It flashed around 26 times in that min. So 60 min in an hour that's 1,560 flashes per around 1.31kWh..

                      Next I kicked on the AC and let the Kw reading on the meter level out around 3.10kW and then I set the timer and counted 54 pulses per min. x 60 for 3,240 per hour.

                      Everything looks per proportional and right along with what I found on the internet for this meter.

                      1,000 blinks per kWh.

                      Using the factory settings should put me right there is what I keep thinking. But that gets me showing 300,000 watts

                      using your above formula and pulses still at 1000 it still gets me in the 300,000 range.

                      If i change my pluse per KWh to 100,000 then it gets me into the right area at 3000 watts when my ac is on which is in the ball park but if I turn the AC off and kW drop to 1.3 ish

                      The serial is still showing 3,000 range in watts it wont drop to the 1,000 so watts it should be.

                      1 Reply Last reply
                      0
                      • I Offline
                        I Offline
                        integlikewhoa
                        wrote on last edited by
                        #15

                        Hoping can jump in and shed some new light on this. BUMP!

                        1 Reply Last reply
                        0
                        • hekH Offline
                          hekH Offline
                          hek
                          Admin
                          wrote on last edited by
                          #16

                          http://efundies.com/electricity/how_to_read_power_meter.htm

                          I 1 Reply Last reply
                          0
                          • hekH hek

                            http://efundies.com/electricity/how_to_read_power_meter.htm

                            I Offline
                            I Offline
                            integlikewhoa
                            wrote on last edited by
                            #17

                            Thanks for that info, it seems to only confirms that the meter is working right and that my problem is in the sktech. LOL

                            I really need help finding out why the example sketch with the "1000 blinks per kWh" set doesn't work anywhere close to where it should be.

                            I'm using the example sketch and my meter has 1.0kH tag on the front.

                            @hek said:

                            http://efundies.com/electricity/how_to_read_power_meter.htm

                            @integlikewhoa said:

                            i'm so lost on this. I can read the screen on the meter. I got my meter holding down to around 1.31kW according to the meter read out. I set the timer for a minute and counted the flashes on the LM393 LED. It flashed around 26 times in that min. So 60 min in an hour that's 1,560 flashes per around 1.31kWh..

                            Next I kicked on the AC and let the Kw reading on the meter level out around 3.10kW and then I set the timer and counted 54 pulses per min. x 60 for 3,240 per hour.

                            Everything looks per proportional and right along with what I found on the internet for this meter.

                            1,000 blinks per kWh.

                            Using the factory settings should put me right there is what I keep thinking. But that gets me showing 300,000 watts

                            using your above formula and pulses still at 1000 it still gets me in the 300,000 range.

                            If i change my pluse per KWh to 100,000 then it gets me into the right area at 3000 watts when my ac is on which is in the ball park but if I turn the AC off and kW drop to 1.3 ish

                            The serial is still showing 3,000 range in watts it wont drop to the 1,000 so watts it should be.

                            1 Reply Last reply
                            0
                            Reply
                            • Reply as topic
                            Log in to reply
                            • Oldest to Newest
                            • Newest to Oldest
                            • Most Votes


                            15

                            Online

                            11.7k