    hi,
    Awesome that you want to implement the support for the AUTO assigning of unique ID's!
    yes, as far as i got it now it starts out with the sensor presenting itself by shouting 255;255;3;0;3; across the network.
    Decoded this means the following:
    node-id: "255;" this means the node has no ID
    child-sensor-id: "255;" this means the node has no child sensor ID's assigned to any sensors attached ( i do not know if this would also be automatically assigned aswell.. but i hope @hek could give us some clarification on this? )
    message-type: "3;" the message type defines the type of message and basicaly why the message is send. the number 3 means that it is an internal message (propably for configuration)
    ack: "0;" no ack needed
    sub-type: "3;" this is where the magic happens. since in the message type it was defined this is an internal message we can state what type of internal message it is in this parameter. the 3 means "I_ID_REQUEST" wich means internal ID request. The node is requesting an ID.
    payload: "(NULL, nothing, empty)" there is no payload, the request is simply enough.
    the controller recieves this request and defines what ID's are already in use. the controller picks a unique number between 1 and 254 and assignes it to the node using the same message-type but a different sub-message-type ( sub-message-type 4 means "Id response back to sensor. Payload contains sensor id" .
    The assigned ID will be transmitted in the payload section.
    example:
    The node boots and looks in his EEPROM memory if it already has a node-ID. if it doesnt it wil broadcast a request for the ID with: 255;255;3;0;3;
    The controller then looks in his table of vended ID's and sends back the first number available (in this example i have only one sensor so number 1 would be vended) and transmits the assigned ID to the node with: 255;255;3;0;4;1
    The node then owns the number 1.
    when something would be transmitted to the node it will listen to this number.
    i dont yet know how the child-sensor-id's work.. sorry for that :-|
    thanks for the help !
    i hope i made it a bit more clear what is needed to vend a node ID.
    vincent,
    tbowmoT
    tbowmoT
    tbowmo
    #26
    The child sensor Id is defined in the arduino sketch by yourself.
    for example the following code:
    Setup() {
    gw.begin();
    gw.present(0,S_TEMP); // Present child sensor ID 0 as temperature sensor
    Loop() {
    / Thomas
    • D
      diamantmatch
      Thanks @tbowmo !
      I uploaded two standard sketches to the node and the gateway so i never noticed before.
      It seems quite logical to define the child-sensor-ID in the sketches on the sensor node itself.
      will do that next time i upload a new sketch!
      • freedomoticF
        freedomoticF
        freedomotic
        Hi all,
        thanks for your explanations. I have some questions:
        1. when the controller assigned an ID, this is stored on the node. If the controller restarts, is this address maintained in the node? or does the node detect this restarting and ask again a new address?
        2. is the address changed only after a specific request by the node?
          Hope my questions are clear. Every freedomotic object must have a fixed address, so if it assign an ID, this shouldn't change at any restarting of software or node.
          Thanks for your support.
        Freedomotic Iot & Smart Spaces framework
        http://www.freedomotic.com
          1. yes node remembers id and won't ask again.
          2. Normally the node wont ask again (unless you clear the eeprom).
          • NuubiN
            NuubiN
            Nuubi
            (might be a silly question..) How do you clean the eeprom? Is it not enought to write another sketch to the chip?
              I've created a ClearEpromConfig in examples.
              • D
                diamantmatch
                hey,
                i really feel like i'm just nagging about things here.. sorry about that.
                i can not seem to get the sensor to listen to the serial output from the plugin..
                i suspect the plugin from not transmitting a newline, every string transmitted should end with \n
                • freedomoticF
                  freedomoticF
                  freedomotic
                  wrote on last edited by freedomotic
                  #33
                  Hi @diamantmatch,
                  I implemented a first draft of Auto-ID feature.
                  If you want you can test it using the attached file (you must extract thejar in it), substituting the old in the plugin folder. Starting Freedomotic from command line you can see all plugin activity.
                  I'm reviewing the entire plugin, to improve it and support an increasing number of devices.
                  Let me know and thanks for support mysensors-3.0.zip
                  • A
                    Aloha
                    Hi Mauro,
                    I read somewhere there's currently no web frontend. Is this still the case? And if so, how do you access freedomotic remotely?
                    / Thomas
                    • freedomoticF
                      freedomoticF
                      freedomotic
                      Hi Thomas,
                      the web client is under development. We hope to realease soon a first demo. If you are interested you can take a look at our repository https://github.com/freedomotic (Polymer). Now is it possible to interact remotely using our REST API (under development). It's the base to create customized clients in every programming languages. More info at http://freedomotic.com/content/plugins/restapi-v3
                      Remember that Freedomotic is a "framework" to create custom iot/home/building automations solutions.
                      Thanks for your interest
                      Mauro
                      • freedomoticF freedomotic
                        Hi Vincent,
                        please can you give me more details? What's the expected reply from the controller (freedomotic)?
                        And your sensor request? I developed the plugin by simulating devices communications. Maaybe something is not complete.
                        asterisco
                        @freedomotic
                        Hi freedomotic, I'm traying to test you plug-in in freedomotic, but dont make it works. Could you please give me a mini setup advise, for example for a** RelayActuator** using Lights General Switch. I set
                        protocolo: mysensors
                        dirección: 7;1 //static ip because i don`t use AUTO mode (or should I use AUTO mode? to make it works)
                        actions: turn on/of MySensors light
                            <property name="serial.port" value="COM5"/>
                            <property name="serial.baudrate" value="115200"/>
                            <property name="serial.databits" value="8"/>
                            <property name="serial.parity" value="0"/>
                            <property name="serial.stopbits" value="1"/>
                        There is allways the same message:
                        my sensors is reciving a command while is not running. Turn on the plugin first.
                        but the plugin is turned on, what im doing wrong???
                        thanks
                        • freedomoticF
                          freedomoticF
                          freedomotic
                          Hi @asterisco
                          can you post a complete console log? If you double click on plugin icon (to stop it) and do the same to restart it do you receive the same error? Thanks for support
                          A 1 Reply Last reply
                          • D
                            dzairo
                            Hi.
                            I download and try your freedomotic .. Install MySensor Plugin ..
                            But show : Plugin started failed , see log for detail.
                            Is possible make tutorial for WIndows 7 user ?
                            What all need install , download and set..
                            regards.
                            • freedomoticF
                              freedomoticF
                              freedomotic
                              Hi @dzairo
                              I need more info, for example your configuration data. Probably your serial port is not set correctly.
                              Start Freedomotic, go to Plugins->Configure (in Main menu), select MySensors and set your gateway port.
                              If you can start freedomotic from command line as "java -jar freedomotic.jar" so you can see all error messages.
                              I'm improving documentation and log messages.
                              Thanks for support
                                Hi @asterisco
                                asterisco
                                quite similar errors with the plugin started or stoped
                                plugin stoped: my sensors is reciving a command while is not running. Turn on the plugin first.
                                ** plugin started:** Succesfull test receives a command while is not ruuning. Turn on the plugin firsr
                                the logs appear and disappear as quikly thar they are almost imposible to read and i de log file is empty
                                bye
                                • freedomoticF
                                  freedomoticF
                                  freedomotic
                                  Hi @asterisco
                                  I uploaded a new version with improved log messages. Can you remove the old plugin folder and reinstall it?
                                  Are you using the last dailybuild?
                                    Martin Guttesen
                                    I get an exception when i try to use mysensor plugin
                                    Windows 8.1
                                    INFO <AWT-EventQueue-0> [Plugin] Starting plugin MySensors
                                    Exception in thread "AWT-EventQueue-0" java.lang.NoClassDefFoundError: com/freed
                                    omotic/objects/EnvObjectPersistence
                                    at com.freedomotic.plugins.devices.mysensors.MySensors.loadConfiguredObj
                                    ects(MySensors.java:227)
                                    at com.freedomotic.plugins.devices.mysensors.MySensors.onStart(MySensors
                                    .java:65)
                                    at com.freedomotic.api.Protocol$1.run(Protocol.java:133)
                                    at org.apache.shiro.subject.support.SubjectRunnable.doRun(SubjectRunnabl
                                    e.java:120)
                                    at org.apache.shiro.subject.support.SubjectRunnable.run(SubjectRunnable.
                                    java:108)
                                    at org.apache.shiro.subject.support.DelegatingSubject.execute(Delegating
                                    Subject.java:391)
                                    at com.freedomotic.security.AuthImpl2.executePrivileged(AuthImpl2.java:1
                                    86)
                                    at com.freedomotic.security.AuthImpl2.pluginExecutePrivileged(AuthImpl2.
                                    java:177)
                                    at com.freedomotic.api.Protocol.start(Protocol.java:151)
                                    at com.freedomotic.jfrontend.PluginJList$1$1.actionPerformed(PluginJList
                                    .java:116)
                                    at javax.swing.AbstractButton.fireActionPerformed(Unknown Source)
                                    at javax.swing.AbstractButton$Handler.actionPerformed(Unknown Source)
                                    at javax.swing.DefaultButtonModel.fireActionPerformed(Unknown Source)
                                    at javax.swing.DefaultButtonModel.setPressed(Unknown Source)
                                    at javax.swing.AbstractButton.doClick(Unknown Source)
                                    at javax.swing.plaf.basic.BasicMenuItemUI.doClick(Unknown Source)
                                    at javax.swing.plaf.basic.BasicMenuItemUI$Handler.mouseReleased(Unknown
                                    Source)
                                    at java.awt.Component.processMouseEvent(Unknown Source)
                                    at javax.swing.JComponent.processMouseEvent(Unknown Source)
                                    at java.awt.Component.processEvent(Unknown Source)
                                    at java.awt.Container.processEvent(Unknown Source)
                                    at java.awt.Component.dispatchEventImpl(Unknown Source)
                                    at java.awt.Container.dispatchEventImpl(Unknown Source)
                                    at java.awt.Component.dispatchEvent(Unknown Source)
                                    at java.awt.LightweightDispatcher.retargetMouseEvent(Unknown Source)
                                    at java.awt.LightweightDispatcher.processMouseEvent(Unknown Source)
                                    at java.awt.LightweightDispatcher.dispatchEvent(Unknown Source)
                                    at java.awt.Window.dispatchEventImpl(Unknown Source)
                                    at java.awt.EventQueue.dispatchEventImpl(Unknown Source)
                                    at java.awt.EventQueue.access$200(Unknown Source)
                                    at java.awt.EventQueue$3.run(Unknown Source)
                                    at java.security.AccessController.doPrivileged(Native Method)
                                    at java.security.ProtectionDomain$1.doIntersectionPrivilege(Unknown Sour
                                    ce)
                                    ce)
                                    at java.awt.EventQueue$4.run(Unknown Source)
                                    ce)
                                    at java.awt.EventQueue.dispatchEvent(Unknown Source)
                                    at java.awt.EventDispatchThread.pumpOneEventForFilters(Unknown Source)
                                    at java.awt.EventDispatchThread.pumpEventsForFilter(Unknown Source)
                                    at java.awt.EventDispatchThread.pumpEventsForHierarchy(Unknown Source)
                                    at java.awt.EventDispatchThread.pumpEvents(Unknown Source)
                                    at java.awt.EventDispatchThread.run(Unknown Source)
                                    Caused by: java.lang.ClassNotFoundException: com.freedomotic.objects.EnvObjectPe
                                    rsistence
                                    at java.net.URLClassLoader$1.run(Unknown Source)
                                    at java.net.URLClassLoader.findClass(Unknown Source)
                                    at java.lang.ClassLoader.loadClass(Unknown Source)
                                    at sun.misc.Launcher$AppClassLoader.loadClass(Unknown Source)
                                    ... 48 more
                                    • freedomoticF
                                      freedomoticF
                                      freedomotic
                                      Thanks for your report.
                                      I'll take a look ASAP.
                                        sdndba
                                        Hi @freedomotic
                                        I've read over all the posts and would like to get an update on the status of the plugin, also would like to know where to get the latest version. If I can get this installed I can help you test in on a very large system with over 50 nodes with various sensors on a ranch. Thanks,
                                        • freedomoticF
                                          freedomoticF
                                          freedomotic
                                          Hi @sdndba
                                          thanks for your offer. We are working on a new version. When it is available I'll post here.
                                          Happy new year!!!